Gas boiler KSV 100. Modular boiler KSV for outdoor installation
Steel hot water heating boilers for outdoor use
Working for natural gas and light liquid fuel.
Heating capacity 0.036 MW, 0.07 MW, 0.095 MW, 0.19 MW, 0.29 MW, 0.5 MW.
Installation and operation manual
KSV-00.12.-30 RE
The guide includes the following sections:
Introduction 3
1 Description and operation of the product 4
1.1 Purpose 4
1.2 General information 4
1.3 General requirements 4
1.4 Specifications 5
1.5 Composition 7
1.6 Device 7
1.7 Operating principle 7
1.8 Measuring instruments 12
1.9 Marking 12
2 Operation 12
2.1 Operating restrictions 12
2.2 Preparation for operation 13
2.3 Operation 14
3 Maintenance 15
3.1 Safety precautions 15
3.2 Maintenance 15
4 Maintenance. 15
5 Storage 15
6 Transportation 16
7 Disposal 16
8 Warranty 16
Introduction
This manual is an important and integral part of the delivery and is handed over to the consumer along with the product. Please read the entire manual containing important information about the design of the boiler and its correct operation in order to ensure complete and correct use his technical capabilities. Steel hot water heating boilers for external use of the KSV type (hereinafter referred to as boilers) with a heating capacity from 0.036 to 0.5 MW are designed in four standard sizes and can be operated on light liquid or gaseous fuels. The boiler must be serviced by an operator who has a certificate for the right to service boilers. Persons under 18 years of age are not allowed to work. Workers authorized to work with the boiler must be familiar with the device and the principle of its operation. Persons servicing the boiler must know and follow general rules safety precautions when working with electrically driven mechanisms. When operating the boiler, in addition to this manual, the following regulatory and technical documents must be additionally used:
Device rules and safe operation steam boilers with a steam pressure of no more than 0.07 MPa, hot water boilers and water heaters with a water heating temperature of no higher than 115 °C.
Safety rules for gas distribution and gas consumption systems. PB.
Passport and operating instructions for the burner device (burner)
1. Description and operation of the product.
1.1 Purpose
KSV (steel hot water boiler) heating for external use is intended for heating administrative and industrial buildings and facilities, residential buildings, structures for various purposes and hot water supply when using flow-type and high-speed boilers.
1.2. General information about the product
Boilers are equipped with an atmospheric or blown natural gas burner low pressure or liquid fuel, with an atmospheric burner they are non-volatile gas boilers and are intended for outdoor installation;
Boilers are used in heating systems with natural and forced circulation of coolant;
The boiler operates in automatic mode without constant presence service personnel;
Climatic design of boilers Category 1. GOST;
1.3 General technical requirements
1.3.1. Boilers must use gaseous and liquid fuels of the type recommended by the Manufacturer. Depending on the configuration additional equipment The boiler can operate on the following main types of fuel:
– gaseous fuel– natural gas GOST 5542-87;
– light liquid fuel – diesel fuel, (solar oil) GOST 305-88, TPB TU, viscosity at 20º C, 4 – 6x1– 6); m2/S (cSt);
Attention!
1. The possibility of using other types of fuel must be agreed with the Manufacturers of the boiler and burner devices.
2. The fuel used must correspond in its characteristics to the fuel specified in the documentation for the burner.
1.3.2. The quality indicators of feed water must comply with the requirements of the “Rules for the design and safe operation of steam and hot water boilers, PB 10-574–03”; GOST.
Attention!
Burners used with the boiler must have a valid certificate of conformity of the State Standard of the Russian Federation, permission for use from Rostechnadzor of the Russian Federation
(Gosgortekhnadzor of the Russian Federation) and approval of the Boiler Manufacturer for use as part of the boiler unit.
1.4. Technical characteristics, operational parameters and functional features outdoor boilers of the KSV series
Table 1
Technical characteristics of external-use boilers of the KSV series, operated with blast-type burners.
Model | KSV-40 | KSV-100 | KSV-150 | KSV-500 |
Power (heating capacity), kW | ||||
Rated power (heating capacity) at 80% of max power, kW | ||||
Coefficient useful action,% not less | ||||
Max gas consumption, m³/hour | ||||
Max gas pressure in the network, kPa | ||||
Maximum pressure in the heating system – atm | ||||
Max coolant temperature, °С | ||||
Coolant volume in the boiler, liter | ||||
Nozzle diameter heating systems, mm | ||||
Conductive gas pipeline diameter, inch/mm (not less) | ||||
The chemical water treatment method is selected by a specialized organization designing the facility, taking into account the quality of the source water and the requirements for network water and make-up water. Before putting the boiler into operation, it is necessary to inspect the heating networks. Eliminate leaks and flush the heating system. Washing methods and methods are established by a specialized design organization, depending on local conditions. Attention. It is strictly prohibited to put the boiler into operation without prepared (washed) heating networks and without ensuring the required quality indicators of the network and make-up water, in order to avoid subsequent contamination of the boiler with sludge and scale. 2.2 Preparation for operation. Before putting the boiler into operation, you should make sure that the power supply system and all assembly units are in good working order, as well as that they are securely fastened. Boilers received for operation must be checked for absence mechanical damage related to transportation and storage. Before installing and connecting boilers to external mains, it is necessary to check its completeness in accordance with the boiler passport. During operation, boilers must be kept in good working order and clean, and periodically check the reliability of fastening of all its elements. The boiler is placed outdoors, outside on a specially prepared foundation. The boiler installation project must be carried out by a specialized design organization, in accordance with the technical specifications and installation requirements and comply current SNiP P-35-75 “Boiler installations” and “Safety rules in gas industry" Before starting installation work, it is necessary to remove all plugs and open the boiler for an internal inspection of the firebox. Installation, adjustment and commissioning of the boiler should be carried out in accordance with the Installation and Operation Manual. Installation and trim of the burner device must be carried out in accordance with the documentation supplied with the burner. Installation and adjustment of the burner safety shutdown device should be carried out in accordance with the instructions in the documentation for the device. Check the correct installation of all equipment, pipelines and fittings. Mount pressure gauges on the water pipeline pipes and install thermometers in the sleeves. Pour oil into the thermometer sleeves. Connect the boiler to all communications in accordance with the boiler installation project. Fill the boiler with water that has undergone chemical water treatment. Make adjustments safety valves to open them when the water pressure in the boiler rises above the operating pressure. Before putting the boiler into operation, commissioning work must be carried out by a specialized organization, in which it is necessary: − check the correct installation and all equipment, pipelines, fuel lines, shut-off and safety valves, instrumentation and automation devices; − carry out verification tests for density. Eliminate any identified leaks. Before final commissioning, the following points must be completed: 8. Warranty If these instructions are not followed, the requirements for the manufacturer to fulfill warranty obligations are not valid. This product has passed hydraulic testing in accordance with the “Rules for the design and safe operation of steam boilers with a steam pressure of no more than 0.07 MPa, hot water boilers and water heaters with a water heating temperature not exceeding 115 ° C”, meets the requirements of GOST and is certified equipment. No changes should be made to the boiler design without agreement with the manufacturer. If such changes are made, the manufacturer is not responsible for the performance and safety of the boiler. The boiler's warranty period is 2 years from the date of commissioning. But no more than 36 months from the date of sale. The average service life before decommissioning is 10 years. In case of failure or breakdown of the boiler and/or its constituent elements, excluding components from third-party manufacturers (fittings, safety devices, instrumentation devices, etc.), during the warranty period, the consumer must notify the manufacturer. Consideration of all defects that arise during the warranty period is carried out in accordance with the contract for the supply of products and the legislation of the Russian Federation in force at the time the defect occurred. By agreement with the manufacturer, repairs may be carried out by a third-party specialized organization according to the recommendations and instructions of the manufacturer. The warranty does not cover damage and its consequences caused by: Improper use. Improper installation or commissioning by the user or a third party. Natural wear and tear. Improper or negligent handling or poor maintenance. Unsuitable operating media, especially wrong choice or burner settings, unintended fuels or impurities in the combustion air. Chemical, electrical or electronic influences not caused by the manufacturer. Insufficient amount of water. Failure to comply with these installation and operating instructions. Incompetent measurements and repairs carried out by the buyer or a third party. |
SWR 40 – SWR 100 – SWR150 – SWR 500
PASSPORT
STEEL BOILERhot waterOUTDOOR
344009 Teplov LLC, Rostov-on-Don, Sholokhov Ave. 237
1.Purpose
Universal steel boilers for outdoor installation, type KSV, are designed for heating and hot water supply administrative buildings, residential buildings, social and cultural facilities, schools, hospitals, buildings for various purposes.
2.General information about the product
The boilers are equipped with an atmospheric or blown burner using low-pressure natural gas or liquid fuel; with an atmospheric burner, they are non-volatile gas boilers and are intended for outdoor installation;
KSV boilers can be used as backup source heat supply at facilities with an unstable energy supply system;
Boilers are used in heating systems with natural and forced circulation of coolant;
The boiler operates automatically without the constant presence of maintenance personnel;
Climatic design of boilers Category 1. GOST 15150-69;
Boilers automatically provide standby heating when the gas supply decreases;
KSV boilers for outdoor installation automatically comply with safety requirements (clause 4.16 of SP 41-104-2000).
3. Technical data and characteristics of the boiler
Boilers of the KSV type comply with TU 4931-007-10258780-97. The main parameters are given in the table.
Options |
Boiler type |
|||||
Heating capacity, kW |
Atmospheric burner |
|||||
Blast burner |
||||||
Nominal heating output (at 80% load from max) |
Atmospheric burner |
|||||
Blast burner |
||||||
Heated area (H=2.5-3 m) m² |
Atmospheric burner |
|||||
Blast burner |
||||||
Efficiency, % not less than |
||||||
Nominal gas pressure in the network, kPa |
||||||
Type of atmospheric burner / blast / diesel |
Atmospheric burner |
|||||
Blast burner |
According to permission |
|||||
Maximum gas consumption, m³/h of fuel, kg |
Atmospheric burner |
|||||
Blast burner |
||||||
Maximum coolant temperature, ° C |
||||||
Carbon monoxide (CO) emissions in dry undiluted combustion products at rated power, not more than mg/m³ |
Within acceptable standards |
Within acceptable standards |
Within acceptable standards |
|||
Coolant volume in the boiler, l |
||||||
Diameter of heating system supply pipes, mm |
Diameter of supply gas pipeline, inch (DN) for atmospheric burner |
|||||
Overall dimensions, mm |
1080x2250x2220 |
||||
Boiler weight (without chimney), kg |
4.Completeness
The boiler delivery set is shown in the table.
Name |
Quantity |
Note |
|
KSV boiler assembly |
|||
Burner * atmospheric |
|||
Automatic three way valve |
|||
Chimney** with mounting brackets |
|||
* Blast burner available upon request
** Available upon special order.
5. Boiler design.
The boiler is a combustion device with a water jacket. At the top of the boiler there is a bundle of vertical flame tubes. For more efficient heat transfer and increased efficiency, turbulators are placed in the flame tubes. A removable boiler cover is provided for cleaning flame tubes and turbulators. At the rear of the boiler there is an automatic flow regulator 2 (Fig. 1) (only for atmospheric burners) and a cleaning hatch 6. The automatic flow regulator prevents flame separation from occurring due to excess draft, and also increases efficiency and reduces gas consumption. The boiler is thermally insulated with mineral wool mats and sheet steel, which allows the boiler to be operated without the construction of boiler rooms and furnace rooms. On the front panel there is a thermometer 3, showing the temperature of the coolant at the outlet of the boiler 3, temperature sensors 9 and burner 4. The front panel is closed by a thermally insulated metal door with a screw lock.
6. Operating principle
The boiler operates in automatic mode. Heat is transferred to the coolant through the walls of the boiler and the walls of the flame tubes. The thermal output of the boiler and the building heating system must be coordinated. An automatic three-way valve 3 is placed in the boiler piping circuit (Fig. 2.3), which prevents the formation of condensate and tarry deposits in the furnace (even with excess power of the heating system). For use in heating systems with forced circulation of coolant, it is necessary to install circulation pumps corresponding power according to the diagram shown in Fig. 3*. IN closed system In heating, the deaeration process occurs by heating the coolant to 90º and removing air through air exhaust devices. Reheating and removing the released air completes the deaeration cycle heating system and serves to protect it from intense corrosion. The KSV boiler with an UGT burner has automatic adjustment of gas flow depending on the heat removal from the heating system and the outside air temperature. The KSV boiler with the UGT burner, in the absence of draft and excess gas pressure in the furnace, switches to igniter combustion, which indicates a malfunction in the gas duct or gas supply system.
The boiler is started in the following sequence:
Fill the system completely with water;
Open gas tap on the gas pipeline to the boiler;
Start the boiler (according to the burner data sheet);
When the temperature on the boiler reaches 60 o C, turn on the network pump (with forced circulation of the coolant);
7. Boiler installation
Install the boiler on the site intended for installation. The chimney, which is an integral part of the boiler, is installed on the boiler. The height of the chimney must be at least 8 m (for boilers with an atmospheric burner).
Installation to the heating system and gas pipeline must be carried out in accordance with the “Model Rules” fire safety for residential buildings, hotels, dormitories, administrative buildings, individual garages" (PPB01-93).
Install an automatic thermostatic three-way valve in the immediate vicinity of the boiler in the bypass line immediately behind the building wall,
The supply and return pipelines from the boiler to the heated building should be thermally insulated.
After installing the boiler, carry out a hydraulic test by filling the system with water and raising the pressure in it to 4.5 kg/cm2 on the pressure gauge. The boiler is considered to have passed the test if within 15 minutes. no signs of rupture, residual deformations, or pressure drop leaks were found.
8. Indication of safety measures
Installation and operation of the boiler must comply with the requirements of the “Rules for the design and safe operation of steam and hot water boilers.”
Start-up and commissioning of the boiler must be carried out by a specialized organization that has the appropriate license.
When the boiler stops in winter period For more than a day, it is necessary to completely drain the water from the boiler and heating system.
At the end heating season leave the boiler filled with water to avoid corrosion.
Rapid filling of a hot boiler with coolant is not allowed.
At positive air temperatures, the boiler should be operated with a load of no more than 80% of the maximum (for boilers with atmospheric burners).
An increase in gas pressure above 5 kPa leads to failure of the gas burner device.
9. Possible faults and ways to eliminate them
Malfunction |
Cause and solution |
Smell of gas |
Leak from a gas pipeline. Check the gas pipes inside the boiler and outside. |
The smell is not completely burnt gas |
Clogged hot flue gas exhaust channel. Make sure that the chimney height (for atmospheric burners) and its diameter correspond to the type of boiler. Check gas flow. Check combustion stability. |
Condensation formation |
Return line overcooling. Check serviceability automatic three-way valve. |
Boiler fast product is contaminated tami combustion |
Adjust the combustion, check the composition of the exhaust gases. Check the gas flow and efficiency of the chimney. |
10. Manufacturer's warranty
Teplov LLC guarantees the operability of the boiler and the free replacement or repair of failed assembly units and parts of the boiler for 24 months from the date of commissioning but not more than 30 months from the date of shipment, provided that the consumer complies with the conditions of transportation, storage and operation.
The manufacturer is not responsible in the following cases:
Mechanical damage to the boiler;
Incorrect connection to the heating system;
Incorrect operation of the boiler (heating a boiler that is not filled with water, quickly filling a hot boiler cold water, using the boiler as an instantaneous water heater);
Lack of automatic thermostatic three-way valve in the heating system;
Installation of the boiler by an organization that does not have the appropriate license;
Start-up and commissioning of the boiler by an organization that does not have the appropriate license;
Gas pressure exceeding 5 kPa;
Lack of maintenance.
All of the above violations of operating rules can cause cracks in the boiler pipe structures, which is not a manufacturing defect.
11. Certificate of acceptance
1. SWR boiler __________ factory number ____________________
corresponds technical specifications TU 4931-002-79248424-2006, TU 4931-001-79248424-2006 were manufactured in full compliance with GOST 10617-83 and GOST 20548-93 and were found fit for use.
Pipe structures and pipe connections of the boiler were subjected to hydraulic testing with an excess pressure of 6 kg/cm 2 for 15 minutes.
2. Chimney: Diameter _________________ mm,
height _______________________________ m (not less than 8 m for boilers with an atmospheric burner.
Date of manufacture: _____________________________________
Quality Control Department representative _____________________________________
Director of operations __________________________________
12. Warranty card
LLC "Teplov"
Address: Rostov-on-Don, Sholokhov Ave., 237
13. Certificate of external SWR boiler
The boiler is manufactured according to TU 4931-002-79248424-2006, TU 4931-001-79248424-2006
Factory number _______________________
Heating capacity, kW ______________
Operating coolant pressure 4.0 bar
Maximum coolant temperature, 95 º
Boiler tested hydraulic pressure trial 6 bar
Date of manufacture ________________
Quality Control Department representative ________________
Head of Production ______________ M.P.
1. Boiler body |
5. Return line |
2. Air flow regulator |
6. Flue cleaning hatch |
3. Thermometer |
7. Chimney pipe |
4. Atmospheric burner |
8. Pipe hotline |
9. Temperature sensor |
KSV-40 (W70 KW) |
||||||||||
KSV-100 (W190 KW) |
||||||||||
KSV-150 (W290 KW) |
||||||||||
KSV-500 (W500 KW) |
1. Boiler body |
6. Flue cleaning hatch |
2. Natural air flow grille (winter, summer) |
7. Chimney pipe |
3. Thermometer |
8. Hotline connection |
4. Burner |
9. Thermostat |
5. Return line |
10. Condensate drain pipe |
11. Gas pipe |
1. Chimney |
|
8. Boiler circulation line |
|
9. Return line |
|
10. Vertical riser |
|
5. Deaerator |
11. Safety valve |
6. Heating device |
12. Ball valve |
13. Membrane expansion tank |
1. Chimney |
6. Heating device |
7. Boiler circulation line |
|
3. Automatic three-way valve |
8. Return line |
9. Vertical riser - |
|
5. Deaerator |
10. Ball valve |
11. Membrane expansion tank |
1. Chimney |
6. Heating device |
7. Boiler circulation line |
|
3. Automatic three-way valve |
8. Return line |
9. Vertical riser |
|
5. Expansion tank |
10. Water heater | Document
190 kW;
Combustion chamber type:
closed;
Manufacturer country:
Russia;
Location:
floor;
Application:
for buildings;
Contour:
single-circuit;
Brand:
Weishaupt;
The KSV outdoor boiler is intended for heating administrative and industrial buildings, residential buildings and structures for various purposes (schools, kindergartens, medical institutions, dormitories, office buildings, car dealerships, shopping centers, warehouses, workshops, workshops industrial enterprises etc.).
Due to the design features, our outdoor boilers are installed near the building in open areas, without additional construction of specialized premises and do not require the installation of fire extinguishing systems and gas analyzers. Outdoor boilers are equipped with a forced-air gas burner (Weishaupt - Germany, UNIGAS - Italy) or a liquid fuel burner (Weishaupt - Germany, UNIGAS - Italy). Outdoor boilers operate in automatic mode without the constant presence and special training of maintenance personnel and are not subject to Rostekhnadzor control during operation.
High efficiency (92%) in external-use KSV boilers is achieved by placing turbulators in the heat exchanger, which increase the passage time of the exhaust gases, thereby ensuring more efficient heating of the coolant. For the manufacture of the heat exchanger, steel seamless pipes High Quality, which ensures long service life reducing the risk of emergency stops. The boiler body for external use is made of steel sheet with protective coating and insulated with modern thermal insulation foil materials. You can find prices for outdoor boilers produced by our company.
The production of outdoor boilers is carried out at modern equipment. At the request of the customer, they are produced in different versions. If necessary, our outdoor boilers are equipped with a double-walled “sandwich” chimney system, which is a structure consisting of two pipes various diameters(external and internal). The distance between them is filled with non-flammable thermal insulation material made from high quality basalt fiber. This design ensures rapid heating inner pipe, which, in turn, allows short term, after starting work, raise the temperature in the chimney above the dew point and avoid the formation of condensation.
The product is certified.
Advantages:
- do not require a specially equipped room; they are located in an open area near the building.
- do not require the installation of fire extinguishing systems, gas analyzers, etc.
- operate automatically, without the constant presence of maintenance personnel
- high efficiency - 92%.
- run on both natural gas and diesel fuel
SWR 40 – SWR 100 – SWR150 – SWR 500
PASSPORT
OUTDOOR STEEL hot water boiler
344009 Teplov LLC, Rostov-on-Don, Sholokhov Ave. 237
1.Purpose
Universal steel boilers for outdoor installation, type KSV, are intended for heating and hot water supply of administrative buildings, residential buildings, social and cultural facilities, schools, hospitals, and buildings for various purposes.
2.General information about the product
- Boilers are equipped with an atmospheric or blown burner using low-pressure natural gas or liquid fuel; with an atmospheric burner they are non-volatile gas boilers and are intended for outdoor installation;
- KSV boilers can be used as a backup source of heat supply at facilities with an unstable power supply system;
- Boilers are used in heating systems with natural and forced circulation of coolant;
- The boiler operates in automatic mode without the constant presence of maintenance personnel;
- Climatic design of boilers U category 1. GOST 15150-69;
- Boilers automatically provide standby heating when the gas supply decreases;
- KSV boilers for outdoor installation automatically comply with safety requirements (clause 4.16 of SP 41-104-2000).
Boilers of the KSV type comply with TU 4931-007-10258780-97. The main parameters are given in the table.
No. |
Options |
Boiler type |
||||
SWR 40 |
SWR 100 |
SWR 150 |
SWR 500 |
|||
1 |
Heating capacity, kW |
Atmospheric burner |
36 |
95 |
- |
- |
Blast burner |
70 |
190 |
290 |
500 |
||
2 |
Nominal heating output (at 80% load from max) |
Atmospheric burner |
29 |
76 | ||
Blast burner |
56 |
152 |
240 |
400 |
||
3 |
Heated area (H=2.5-3 m) m² |
Atmospheric burner |
360 |
1000 | ||
Blast burner |
700 |
2000 |
3000 |
5000 |
||
4 |
Efficiency, % not less than |
86 |
89 |
89 |
89 |
|
5 |
Nominal gas pressure in the network, kPa |
1,2 |
2,0 |
|||
6 |
Type of atmospheric burner / blast / diesel |
Atmospheric burner |
UGT |
|||
Blast burner |
According to permission |
|||||
7 |
Maximum flow gas, m³/h fuel, kg |
Atmospheric burner |
4,4 |
11,4 |
- |
- |
Blast burner |
8,5 |
22,8 |
32 |
61,1 |
||
8 |
Maximum coolant temperature, ° C |
95 |
||||
9 |
Carbon monoxide (CO) emissions in dry undiluted combustion products at rated power, not more than mg/m³ |
|
Within acceptable standards |
Within acceptable standards |
Within acceptable standards |
|
10 |
Coolant volume in the boiler, l |
62 |
166 |
253 |
370 |
|
11 |
Diameter of heating system supply pipes, mm |
57 |
76 |
89 |
108 |
12 |
Diameter of supply gas pipeline, inch (DN) for atmospheric burner |
1/2" (15) |
1"(25) |
- |
- |
13 |
dimensions, mm |
540x1200x1200 |
740x1460x1880 |
840x1710x2220 |
1080x2250x2220 |
14 |
Boiler weight (without chimney), kg |
170 |
470 |
850 |
1450 |
4.Completeness
The boiler delivery set is shown in the table.
No. |
Name |
Quantity |
Note |
1 |
KSV boiler assembly |
1 | |
2 |
Burner * atmospheric |
1 | |
3 |
Automatic three way valve |
1 | |
4 |
Chimney** with mounting brackets |
1 | |
5 |
Passport |
1 |
* Blast burner available upon request
** Available upon special order.
5. Boiler design.
The boiler is a combustion device with a water jacket. At the top of the boiler there is a bundle of vertical flame tubes. For more efficient heat transfer and increased efficiency, turbulators are placed in the flame tubes. A removable boiler cover is provided for cleaning flame tubes and turbulators. At the rear of the boiler there is an automatic flow regulator 2 (Fig. 1) (only for atmospheric burners) and a cleaning hatch 6. The automatic flow regulator prevents flame separation from occurring due to excess draft, and also increases efficiency and reduces gas consumption. The boiler is thermally insulated with mineral wool mats and sheet steel, which allows the boiler to be operated without the construction of boiler rooms and furnace rooms. On the front panel there is a thermometer 3, showing the temperature of the coolant at the outlet of the boiler 3, temperature sensors 9 and burner 4. The front panel is closed by a thermally insulated metal door with a screw lock.
6. Operating principle
The boiler operates in automatic mode. Heat is transferred to the coolant through the walls of the boiler and the walls of the flame tubes. The thermal output of the boiler and the building heating system must be coordinated. An automatic three-way valve 3 is placed in the boiler piping circuit (Fig. 2.3), which prevents the formation of condensate and tarry deposits in the furnace (even with excess power of the heating system). For use in heating systems with forced circulation of coolant, it is necessary to install circulation pumps of appropriate power according to the diagram shown in Fig. 3*. In a closed heating system, the deaeration process occurs by heating the coolant to 90º and removing air through air exhaust devices. Reheating and removing the released air completes the deaeration cycle of the heating system and serves to protect it from intense corrosion. The KSV boiler with an UGT burner has automatic adjustment of gas flow depending on the heat removal from the heating system and the outside air temperature. The KSV boiler with the UGT burner, in the absence of draft and excess gas pressure in the furnace, switches to igniter combustion, which indicates a malfunction in the gas duct or gas supply system.
The boiler is started in the following sequence:
- fill the system completely with water;
- open the gas valve on the gas pipeline to the boiler;
- start the boiler (according to the burner data sheet);
- when the temperature on the boiler reaches 60 o C, turn on the network pump (with forced circulation of the coolant);
- Install the boiler on the site intended for installation. The chimney, which is an integral part of the boiler, is installed on the boiler. The height of the chimney must be at least 8 m (for boilers with an atmospheric burner).
- Installation to the heating system and gas pipeline should be carried out in accordance with the “Model fire safety rules for residential buildings, hotels, dormitories, administrative buildings, individual garages” (PPB01-93).
- Install an automatic thermostatic three-way valve in the immediate vicinity of the boiler in the bypass line immediately behind the building wall,
- The supply and return pipelines from the boiler to the heated building should be thermally insulated.
8. Indication of safety measures
- Installation and operation of the boiler must comply with the requirements of the “Rules for the design and safe operation of steam and hot water boilers.”
- commissioning and commissioning of the boiler must be carried out by a specialized organization that has the appropriate license.
- when stopping the boiler in winter for more than a day, it is necessary to completely drain the water from the boiler and heating system.
- at the end of the heating season, leave the boiler filled with water to avoid corrosion.
- rapid filling of a hot boiler with coolant is not allowed.
- at positive air temperatures, the boiler should be operated with a load of no more than 80% of the maximum (for boilers with atmospheric burners).
9. Possible malfunctions and ways to eliminate them
Malfunction |
Cause and solution |
Smell of gas |
Leak from a gas pipeline. Check gas pipes inside the boiler and outside. |
The smell is not completely burnt gas |
Clogged hot flue gas exhaust channel. Make sure that the chimney height (for atmospheric burners) and its diameter correspond to the type of boiler. Check gas flow. Check combustion stability. |
Condensation formation |
Return line overcooling. Check serviceability automatic three-way valve. |
Boiler fast product is contaminated tami combustion |
Adjust the combustion, check the composition of the exhaust gases. Check the gas flow and efficiency of the chimney. |
10. Manufacturer's warranty
Teplov LLC guarantees the operability of the boiler and the free replacement or repair of failed assembly units and parts of the boiler for 24 months from the date of commissioning but not more than 30 months from the date of shipment, provided that the consumer complies with the conditions of transportation, storage and operation.
The manufacturer is not responsible in the following cases:
Mechanical damage to the boiler;
Incorrect connection to the heating system;
Incorrect operation of the boiler (heating a boiler that is not filled with water, quickly filling a hot boiler with cold water, using the boiler as a flow-through water heater);
Lack of automatic thermostatic three-way valve in the heating system;
Installation of the boiler by an organization that does not have the appropriate license;
Start-up and commissioning of the boiler by an organization that does not have the appropriate license;
Gas pressure exceeding 5 kPa;
Lack of maintenance.
All of the above violations of operating rules can cause cracks in the boiler pipe structures, which is not a manufacturing defect.
11. Certificate of acceptance
1. SWR boiler __________ factory number ____________________
complies with the technical specifications of TU 4931-002-79248424-2006, TU 4931-001-79248424-2006 is manufactured in full compliance with GOST 10617-83 and GOST 20548-93 and is recognized as fit for use.
Pipe structures and pipe connections of the boiler were subjected to hydraulic testing overpressure 6 kg/cm 2 for 15 minutes.
2. Chimney: Diameter _________________ mm,
height _______________________________ m (not less than 8 m for boilers with an atmospheric burner.
Date of manufacture: _____________________________________
Quality Control Department representative _____________________________________
Director of operations __________________________________
12. Warranty card
LLC "Teplov"
Address: Rostov-on-Don, Sholokhov Ave., 237
13. Certificate of external SWR boiler
The boiler is manufactured according to TU 4931-002-79248424-2006, TU 4931-001-79248424-2006
Factory number _______________________
Heating capacity, kW ______________
Operating coolant pressure 4.0 bar
Maximum coolant temperature, 95 º
The boiler is tested with a test hydraulic pressure of 6 bar
Date of manufacture ________________
Quality Control Department representative ________________
Head of Production ______________ M.P.
A |
IN |
WITH |
D |
d |
TO |
N |
N, |
|
KSV-40 |
540 |
1200 |
1200 |
178 |
57 |
150 |
115 |
1035 |
KSV-40 |
A |
IN |
WITH |
D |
d |
TO |
N |
Hi |
diameter |
supply |
|
KSV-40 (W70 KW) |
540 |
1200 |
1200 |
178 |
57 |
150 |
115 |
1035 |
1/2 |
Left |
KSV-100 (W190 KW) |
740 |
1460 |
1880 |
178 |
76 |
200 |
130 |
1727 |
1 |
Left |
KSV-150 (W290 KW) |
840 |
1710 |
2220 |
219 |
89 |
250 |
160 |
2005 |
1.1/2 |
Left |
KSV-500 (W500 KW) |
1080 |
2250 |
2220 |
325 |
114 |
250 |
160 |
2005 |
2 |
On right |
1. Boiler body |
6. Flue cleaning hatch |
2. Natural air flow grille (winter, summer) |
7. Chimney pipe |
3. Thermometer |
8. Hotline connection |
4. Burner |
9. Thermostat |
5. Return line |
10. Condensate drain pipe |
11. Gas pipe |
1. Chimney |
7. Pump |
2. Clamp |
8. Boiler circulation line |
|
9. Return line |
4. Boiler |
10. Vertical riser |
5. Deaerator |
11. Safety valve |
6. Heating device |
12. Ball valve |
13. Membrane expansion tank |
1. Chimney |
6. Heating device |
2. Clamp |
7. Boiler circulation line |
3. Automatic three-way valve |
8. Return line |
4. Boiler |
9. Vertical riser |
5. Expansion tank |
10. Water heater |
11. Shut-off valve |
How long will you overpay for heat and water supply, while you can save on installation, maintenance and gas consumption by purchasing a modular boiler KSV!
The KSV modular boiler replaces old boilers and has capital costs up to 4 times lower than block and roof boiler houses.
Stop overpaying for heat!
Costs for heat are reduced by 5 times, and hot water 8 times, thanks to the new boiler design.
Reducing equipment maintenance costs. Operating the boiler does not require specially trained personnel.
Reducing losses in the heating network to zero due to the absence of a pipeline outside the heated facility.
Economical blower burner own production many times cheaper than foreign analogues.
Low cost of KSV boilers compared to a stationary or block boiler house.
Block boiler houses require more than 20 permits, and KSV boilers can be launched with just one document.
Why will the KSV modular boiler solve your heating problems?
- All elements of the block boiler room are mounted in one external boiler body.
- Saving energy through the use of energy-saving devices.
- Gas savings due to high efficiency.
- The burner automation operates at extreme temperatures down to -45 °C
- Quick installation
- Easy to start (burner is already set up at the factory)
- Long service life (15 years)
- NPO VR KS LLC produces spare parts for warranty and post-warranty service
- Capital costs are reduced by 2-4 times (compared to block and roof boiler houses)
- Possibility of complete electrical independence
ECONOMIC EFFECT in just one heating season!
Technical specifications
modular boilers KSUV
Complete set of modular boiler KSV
The modular outdoor boiler of the KSV series is a 3-pass fire-tube boiler with a blow burner of the GDK series, located in a thermally insulated casing made of galvanized steel. An energy-automatic thermostatic three-way valve is mounted inside the boiler, connected to a circulation pump of appropriate capacity.
- Blast burner
- three-way valve
- DEAERATION EXPANSION TANK
- Water-water heater
Blast burner GDK - diffusion-kinetic burner
The use of diffusion-kinetic burners (DK) makes it possible to obtain the same characteristics as when using imported blown burners of the same power, while the energy consumption for the burner fan drive is reduced by 3 times, which allows the boiler to operate in a non-volatile mode, up to 72 hours, the noise level is reduced by 2 times. GDK burners can operate at outside air temperatures down to – 45°C, which is unattainable for imported forced-air burners. The last circumstance is decisive when using these burners in boilers with external SWR placement.
AUTOMATIC THERMOSTATIC 3 WAY VALVE
The formation of condensate inside the fire tube part of the boiler leads to an increase in soot, a decrease in efficiency and failure of the boiler.
The use of a volatile automatic three-way valve with low hydraulic resistance allows the use of conventional circulation pumps with a head of 6÷8 m and a drive power of up to 210 W for autonomous systems GSW and heating with a power of up to 100 kW. This device prevents the formation of condensation inside the boiler furnace during startup and operation of the boiler in hot water supply systems.
DEAERATION EXPANSION TANK
DRB is designed to remove gases and compensate for thermal expansion of the coolant. A decrease in carbon dioxide content leads to the formation of CaCO3 from carbonates protective film on metal pipes heating systems, heating devices, fire tube part of boilers. At permanent job heating systems in expansion tank thermal deaeration occurs, which increases durability steel pipelines, heating devices, boiler equipment.