Standard operating instructions for automatic water fire extinguishing installations. Organization of operation and maintenance of the fire extinguishing system Operating instructions for the automatic fire extinguishing system

I CONFIRM:
CEO
______________
________________
"___"____________ 2012

INSTRUCTIONS
ON THE OPERATION OF FIRE AUTOMATICS
____________

_________________

1. AUTOMATIC FIRE FIGHTING.

For fire extinguishing the following are provided:
-automatic installation of sprinkler water fire extinguishing with finely atomized water with installation of internal fire extinguishing valves on the supply pipelines to protect premises;
-interior fire water supply to protect office and auxiliary premises;
-equipment pumping station fire extinguishing
To protect the premises of the shopping center there is a water-filled sprinkler installation automatic fire extinguishing finely atomized water (water mist) using finely atomized water sprinklers CBS0-PHo(d)0.07-R1/2/P57.B3 "Aquamaster".
An automatic water sprinkler fire extinguishing installation consists of:
- supply pipelines;
- fire extinguishing station NS 70-65-3/100, which consists of
- pumping station module (MNS 70-65);
- module of two sprinkler control units MUU-ZS (MUU-3/100);
- module for connecting mobile fire fighting equipment.
Technical data of the fire extinguishing installation:
The “Potok-3n control device” manufactured by Bolid is used as a control device for the pumping station.
The "S2000M" remote control provides reception of signals, through addressable devices, from standard automatic addressable and manual call points, as well as technological sensors of fire extinguishing systems.
The system has an interface line, which is a two-wire communication line of the main structure with visual and audio indication of alarm and malfunction on the system devices. Possibility of programming devices for signaling the state of the fire extinguishing installation.
Additional installed modules allow for protection technical premises discrete smoke detectors, which are used for automatic control engineering systems; issuing information to light and sound annunciators, issuing sound alerts and documenting events. An indication module “S2000 BI isp.01” is installed in the duty personnel room, which allows for visual control of the operation of the automatic fire extinguishing pump station equipment.
A fire reservoir is used as a source of water supply.
To supply water to the pipelines of the sprinkler installation, booster fire pumps of the GRUNDFOS NB 50-257 type with a 30 kW electric motor (main and backup) are provided. Supply - 75 m3/h, with pressure - 81 m.
Operating principle of water fire extinguishing installation.
In standby mode, the supply pipeline (to the control units), supply and distribution pipelines are filled with water and are under pressure P = 0.5 MPa (50 m) created by the jockey pump.
Automation elements are in standby mode.
When a fire occurs in the protected premises, the temperature rises. An increase in temperature to 570C leads to the destruction of the glass flask of the sprinkler.
Opening the sprinkler leads to a drop in pressure in the supply and distribution pipelines.
The water pressure in the supply pipeline lifts the valve of the KS water-filled sprinkler valve of the "Bage" type.
When the valve of the control unit is opened, pressure alarms installed on the control unit generate a pulse to turn on the working booster pump for water supply, as well as a fire alarm (in case of failure smoke detectors earlier) and about the start of the installation.
If the working pump fails to create the design pressure Rcalc = 0.70 MPa, the backup pump is turned on and the working pump is turned off. Water flows through the open control unit through supply and distribution pipelines to the source of fire; the jockey pump is turned off.
Automatic start-up is carried out using the contacts of the Potok 3N device, which ensure the activation of the pumps of the fire extinguishing booster pumping station. Remote start of automatic smoke protection and warning people about a fire is carried out from manual fire detectors installed on evacuation routes. Manual start-up of booster pumps is carried out at the location of the equipment on the pump control cabinets.
After extinguishing the fire it is necessary;
- check the sprinklers and pipelines located in the combustion zone; if they fail, replace them;
- fill the distribution, supply and inlet pipelines with water;
- bring the opened control unit into working condition;
- bring automation elements into a state of control.
When operating the installations, it is necessary to carry out following rules:
1) repair work related to the installation and dismantling of equipment must be carried out in the absence of pressure in the unit being repaired;
2) cleaning and painting of pipelines located close to current-carrying elements is permitted only after removing the voltage from them and issuing a work permit;
3) persons involved in hydraulic tests must be in safe places or behind a specially provided screen at the time of testing;
4) hydraulic and pneumatic tests of pipelines must be carried out in accordance with the approved instructions for testing pipelines;
5) lubrication of engines while moving, tightening bolts on moving parts of mechanisms is not allowed;
6) instructions and safety posters must be posted in the premises of control units and in the fire extinguishing station;
7) carry out repair work on electrical equipment after turning off the power supply;
8) when carrying out adjustment, repair and maintenance work, it is necessary to take into account that when installing an automatic fire extinguishing system, when the voltage is removed from any control cabinet (box), a voltage of 220V, 50 Hz may be present on electrical devices, terminal blocks of this device, since the automation control circuits are interconnected , and the remaining sources are not de-energized, therefore, before carrying out the specified work, it is necessary to carefully study the power supply circuit of the installation consumers, then de-energize necessary devices;
9) when performing work with electrical equipment, dielectric mats and gloves are required;
10) when executed repair work portable lamps with a voltage not exceeding 42 V should be used;
11) all non-current-carrying parts of electrical equipment that may become energized as a result of insulation failure must be grounded (zeroed);
12) all work should be carried out only with working tools; the use of wrenches with extended handles, tool handles must be made of insulating material.
Operation of a fire extinguishing pump station.
1 To turn off fire pumps, make sure the fire is contained;
2 If the fire is extinguished or it turns out that a false alarm occurred
pump mode handles on pump control cabinets (main backup and jockey) to position “0”;
3 Call the service organization by phone ___________________;
To put the fire pumping station into standby mode, the following actions must be taken:
1 All valves must be in open position;
2 Turn off the power supply circuit breaker of the pumping station for 30 seconds;
3 Turn on the power supply circuit breaker of the pumping station;
4 Turn on all power circuit breakers in the electrical panel of the pumping station;
5 Move the pump mode handles on the pump control cabinets (main backup and jockey) to the “remote” position;
To check the operation of the pumps in manual mode (main backup and jockey), move to the “local” position. and briefly press the pump start button (green) on the control cabinet and, after making sure (1-2 seconds) that the pumps are working, briefly press the pump stop button (red) on the control cabinet.

2. AUTOMATIC FIRE ALARM AND SOUE
Automatic system fire alarm(APS) is designed to detect the early stages of fire and smoke in retail and office premises ____________, turn on the voice warning system to organize the evacuation of people and turn on active fire protection(APZ).
The number of sound alarms (sirens), their placement and power provide the necessary audibility in all places of permanent or temporary residence of people.
The warning system is automatically turned on when a fire is detected in the building by a signal from the automated fire control system or automatic fire control system.
The APS exit point is located on the first floor in the security room. The fire department is equipped with a telephone connection. Security personnel work around the clock. On floors four to seven are located office rooms.
To organize the alarm system for the office part of the building, the following equipment is used:
- analog addressable smoke fire detector Z-051, according to NPB 88-2001* at least two detectors in one room (reacts to smoke in protected premises);
- manual addressable fire detector Z-041 (installed on evacuation routes);
- fire alarm control and receiving device "Z-101" (designed for connecting and monitoring fire alarm loops, for monitoring and controlling input and output units (Z-011. Z-022);
- addressable output block "Z-011" (designed to start the fire warning system, turn off the ventilation and air conditioning systems in case of fire, start the smoke removal system).
- linear smoke detector 6500R (responses to smoke in protected premises);
- the warning system uses equipment from the JEDIA company, which has all the necessary certificates.
Fire alarm station Z-101.
The fire alarm station is designed to receive signals from detectors, addressable devices and control technological equipment.
Information about the state of the fire alarm system is displayed on the display located on the front panel, which makes it possible to display information about the state of the system in real time.
Has 2 ring loops 250 addresses each.
Has an RS-485 output for connecting remote keyboards (up to 5 pcs.).
Z-101 is a fully completed fire alarm station with a full range of necessary functions.
The stations receive and process information from peripheral devices.
Each station has 5 programmable outputs, as well as a Fire relay and a Fault relay. There is also a 24V output and an output to an external siren.
Each station has a built-in printer with the ability to filter printed events.
Log of 999 events.
Addressable analogue fire smoke detector Z-051.
The Z-051 detector is designed to work with equipment of the Z-line series. The broadcaster is connected to an addressable loop (up to 250 addresses). Designed for optoelectronic detection of combustion products. Has a built-in indicator (LED). For internal use. The detector is programmed using the Z-511 address programmer.
The operating principle is photoelectric, working on the principle of light scattering.
Manual addressable fire detector Z-041.
Module Z -041 is designed to work with equipment of the Z-line series. Manual call point is installed on escape routes, stairwells
. When you press the glass, the microswitch is activated. Restoring the detector to an operational state is carried out using a key.
Short circuit insulator Z -011
Module Z -011 is designed to work with equipment of the Z-line series. The module is connected to an addressable loop (up to 250 addresses).
Purpose:
If a short circuit occurs in the loop, the short-circuited part of the loop between the two closest short-circuit modules is disconnected.
Has a built-in indicator (LED).
The number of modules in a loop is not limited.
Has no address.
Input module Z-021
Module Z -021 is designed to work with equipment of the Z-line series.
Module Z -011 is designed to work with equipment of the Z-line series. The module is connected to an addressable loop (up to 250 addresses).
The module is connected to an addressable loop (up to 250 addresses). - Designed to receive a signal from external sources
anxiety.
- Contains an input with a 2 kOhm end-of-line resistor.
- Has a built-in indicator (LED). Programming of the module is carried out using the Z-511 address programmer.
Application:
-Start buttons.
-Flame detectors with relay outputs.
-Flow switch, etc.
Output module Z-022
Module Z -022 is designed to work with equipment of the Z-line series.
Module Z -021 is designed to work with equipment of the Z-line series.
Module Z -011 is designed to work with equipment of the Z-line series. The module is connected to an addressable loop (up to 250 addresses).
Designed to control external equipment.
Contains input feedback.
Receiving a "Fault" signal when the feedback circuit is closed without a "Fire" signal
Group of contacts for switching normally closed and normally open (N0-C-NC)
Has 2 built-in indicators (LED) Operation and Activation.
The module is programmed using the Z-511 address programmer.
Application:
Monitoring and/or control of various technological equipment
- fire-retarding valves,
- smoke exhaust hatches,
- pump boosters,
- ventilation systems, etc.

Instructions for actions of duty personnel in the event of a fire alarm or malfunction
When receiving a “FIRE” signal (switching on of a smoothly changing tone and a red “Fire” LED indicator on the front panel of the “Z-101” device):
1. Report the incident to the fire department (PCh-12) by phone 01 or _____________; report the address of the object where it is burning (the location of the fire), what the threat is (information about the fire is displayed on the LCD display - displaying the fact of a fire alarm and detailed information about the location of the fire).
2. Report the incident to the person responsible for fire safety __________________ by phone. __________________, to the head of the DPD _________________ by phone. ________________, to CEO __________________ by phone. ______________.
3. Check that the smoke removal, fire extinguishing, and fire alarm systems are turned on. If the warning system does not work in automatic mode, you should use manual call points, as well as notify service personnel and visitors by voice via radio broadcasting for the fastest and timely evacuation of people or transfer additional functions.
4. Open all door locks at the main and emergency emergency exits from the building, the chief power engineer (electrician) must turn off the power to the floor/building.
5. Send the security guard on duty or a member of the traffic police to meet the firefighters and escort them to the fire site.
The fire alarm condition can only be reset by manual reset (by pressing the "RESET" button on the front side of the Z-101 control panel).

When receiving a “FAULT” signal on the fire alarm panel “Z-101” (an intermittent fault signal is issued to the built-in sounder and turns on the LED indicators on the front panel of the device):
1. View detailed information about the malfunction on the display (information about the malfunction is also printed on the built-in printer, namely the cause of the malfunction and the time the malfunction occurred). Try to switch the device by manual restart (by pressing the "RESET" button).
2. If normal functioning If the device is not restored, it is necessary to reversibly remove some addressable loop devices from the equipment at the facility without reprogramming the entire system. For example, this may be a situation where it is necessary to turn off a faulty detector before service personnel arrive. To do this, in standby mode, press the "menu" key and enter the password 111111. After entering the correct password, the operator menu will appear. To enter device shutdown mode, press "1". The following devices can be disabled: detectors, input and output modules, sirens. If at least one of these devices is disabled, the “Disabled” LED on the Device lights up. Shutdown information will be shown on the display.
3. Call a specialized organization to troubleshoot the problem. Tel._________________.
Mute sound (alerts):
The built-in siren is turned off manually by pressing the "Mute" key. At the same time, the “Sound Off” LED on the front panel lights up. If "Z-101" is in the sounding state or in the non-alarm monitoring state, the "Sound Off" LED on the front panel will go out.
Clearing alarm or fault information, restarting:
To clear fire alarm, supervision or fault information (main or backup power faults are indicated by LEDs, this is not shown on the display), press the "Reset" key by restarting the "Z-101". Information about disabling the device will be deleted from the display after canceling the disabling of the device (i.e., turning it on); information about the malfunction will be deleted after the malfunction is eliminated.
System testing:
On the information interface, press the "Test" (self-test) key to test on the LCD screen, the LEDs on the front panel light up and the annunciators are activated. After the self-test, the pending request state is automatically returned.
Key lock:
On the front side of the "Z-101" there is a lock with a key for locking and unlocking the keys. Turning the key to the left locks the keyboard. In this state, the operator can only mute the alert by pressing the Mute button. When the key is turned to the right, all keyboard functions are available.
Automatic and manual modes:
To switch manual/automatic modes, press the “manual/automatic” key and then enter the correct password 111111. If the Device is in automatic mode, the “automatic/manual” LED will light. When the device (Z-101) is in manual mode, the LED does not light up. The device (Z-101) in manual mode will not send any control signal automatically. In this case, control is carried out manually.
Entering a text description of the location of the addressable device (descriptor):
To enter location information in the administrator menu, press key 4 to exit to the descriptor input screen. When you enter the device address and press the "Enter" key, the display shows the available text information. To select the input mode, press the "Test" key. After selecting the input mode, enter the address (location) of the device.
More detailed information is provided in the Operating Instructions for Network Addressable Analogue Fire Alarm Panels of the Z-line Series, which is attached to this manual.

3. SMOKE EXHAUST SYSTEM
Fire safety ventilation systems are provided by:
- equipment of separate ventilation systems for premises of various functional purposes;
- installation of fire-retarding valves with standardized fire resistance limits in places where air ducts cross fire barriers (walls and ceilings);
- automatic shutdown of general ventilation in case of fire and activation of the smoke ventilation system;
- thermal insulation made of non-combustible materials.
- air ducts of smoke removal systems and transit air ducts of ventilation systems are covered fire retardant composition.
The smoke removal system is turned on automatically when the fire warning system is started and the general ventilation is turned off (if the warning system does not work automatically, it must be started from manual call points).

The instructions were compiled by ____________________

ANNEX 1.
Responsibilities of maintenance and operational personnel.
1.3.1. At the facilities, all types of maintenance and repair work, as well as installation maintenance fire automatics must be carried out by the facility’s own specialists who have undergone appropriate training, or, under a contract, by organizations that have a license from the GPN management bodies to carry out installation, adjustment and maintenance work on fire automatics installations.
1.3.2. At each facility, the following personnel must be assigned to operate and maintain fire automatic equipment in technically good condition by order of the manager:
- the person responsible for the operation of fire automatics installations;
- specialists who have been trained to perform maintenance and repair work on fire automatics installations (in the absence of an agreement with a specialized organization);
- operational (duty) personnel to monitor the condition of installations, as well as call the fire department in case of a fire.
1.3.3. Monitoring compliance with maintenance and repair regulations, timeliness and quality of work performed by a specialized organization should be entrusted to the person responsible for the operation of fire automatics installations.
1.3.4. The person responsible for the operation of fire automatics installations is obliged to ensure:
- compliance with the requirements of these rules;
- acceptance of maintenance and repair work in accordance with the schedule and calendar plan work under the contract;
- maintaining fire automatics installations in good working order and operational condition by carrying out timely maintenance and preventative maintenance;
- training of maintenance and duty personnel, as well as instructing persons working in protected premises on actions to take when the fire alarm system is activated;
- information to the relevant control bodies of the gas pumping station about all cases of failures and operation of installations;
- timely submission of complaints: to manufacturing plants - in case of delivery of incomplete, low-quality or non-compliant devices and equipment of fire automatics installations; installation organizations - upon detection of poor-quality installation or deviations during installation from the design documentation that were not agreed upon with the project developer and the state fire inspection body; service organizations - for untimely and poor-quality maintenance and repair of installations and fire automatic equipment.
1.3.5. Service staff object or representative of a specialized
organizations are required to know the structure and operating principle of the fire automatics installation at the site, know and comply with the requirements of these Rules and the operating instructions for this installation.
1.3.6. Persons who discover a malfunction of the installations are obliged to immediately report this to the personnel on duty, and the latter to the person responsible for operating the system, who is obliged to take measures to eliminate the identified malfunctions.
1.3.7. The maintenance personnel of the facility or a representative of the service organization carrying out maintenance and repair of fire automatics installations must carry out routine maintenance in a timely manner and maintain the appropriate operational documentation given in the appendices to these Rules.
1.3.8. It is prohibited to turn off the fire automatics installations during operation, as well as to introduce changes to the adopted protection scheme without adjusting the design and estimate documentation, which are not agreed upon with the territorial management body of the State Fire Facility.
1.3.9. The administration of the facilities is obliged to ensure, during the period of maintenance and preventive maintenance work, the implementation of which is associated with the shutdown of installations, the fire safety of the premises protected by the installations by compensating measures, informing the management bodies of the State Fire Department and, if necessary, private security.
1.3.10. Operational (duty) personnel must know:
- Instructions for operational (duty personnel);
- performance characteristics devices and equipment of fire automatics installations installed at the enterprise, and the principle of their operation;
- name, purpose and location of the premises protected (controlled) by the installations;
- the procedure for starting the fire automatics installation in manual mode;
- procedure for maintaining operational documentation;
- control procedure working condition installation of fire automatics on site;
- procedure for calling the fire department.

APPENDIX 2.
Operation log
Fire automatic systems
(Form)
1.Name and departmental affiliation (form of ownership) of the facility equipped with a fire automatic system
(type of system, starting method)
Address_________________________________________________________________
Date of installation of the system, name of the installation organization
______________________________________________________________________
Fire automatic system type
______________________________________________________________________
Name of the organization (service) serving the system
______________________________________________________________________
Telephone_______________________________________________________________
2. Characteristics of the fire automatic system
______________________________________________________________________
______________________________________________________________________
______________________________________________________________________
______________________________________________________________________
______________________________________________________________________
(name of technical equipment, release date, start date of operation, next inspection period)
3. Fundamental wiring diagram fire automatic systems.
4. Results of hydraulic and electrical tests.
Date Test results Conclusion Signature

5. Acceptance and delivery of duty and technical condition of the system:
Date of acceptance and delivery State of the systems during the period of duty Name of the protected objects and type of systems from which the signals were received Last names, signature of the person who passed and took over the duty

6. Accounting for failures and malfunctions of fire automatic systems
No. Date and time of receipt of message Name
controlled
premises Character
malfunction Name and position of the person who accepted it Date and time the malfunction was eliminated Note

7.Accounting Maintenance and scheduled preventive maintenance of fire automatic systems.
No. Date Type of system Controlled object Nature of work performed List of work performed Position, surname and signature of the person who carried out the maintenance Note

8.Checking the knowledge of personnel servicing fire automatic systems

Full name, position, work experience of the person being inspected Date of inspection Knowledge assessment Signature of the inspector Signature of the person being inspected

9.Accounting for the activation (shutdown) of fire automatic systems and information from fire suppression authorities

p/n Name of the controlled object Type and type of fire automatic system Date of activation (off) Reason for operation (off) Damage from fire Amount of saved valuables Reason for operation Date of GPN information

10.Instruction of technical and operational personnel on safety precautions when working with fire automatic systems.

p/n Last name of the person being instructed Position held by the person being instructed Date of the briefing Signature of the person being instructed Signature of the person who conducted the briefing

APPENDIX 3.
Message
about the activation (failure) of the fire automatic system (sent to the territorial office of the State Fire Service)
1.Name of the enterprise and its address
______________________________________________________________________
______________________________________________________________________
(type of ownership)
2.Date of activation or shutdown_____________________________________________
3. Characteristics of the controlled premises___________________________
______________________________________________________________________
4. Reason for activation or shutdown __________________________________________
______________________________________________________________________
______________________________________________________________________
5.Type of control panel or fire extinguishing system
______________________________________________________________________
______________________________________________________________________
6. Number of triggered sprinklers and detectors
______________________________________________________________________
7. Efficiency in detecting or extinguishing a fire of system fire automatic equipment__________________________________________________________________________
______________________________________________________________________
(worked on time, late, etc.)
8. Estimated fire damage
______________________________________________________________________

9. Material assets saved due to the presence and timely operation of the fire automatic system_____________________________________________
(amount, thousand rubles)
10.If the system fails, indicate the reasons for the failure
______________________________________________________________________

______________________________________________________________________________((surname, signature official)

"_________"_________________________ 20_____

APPENDIX 4.
Work regulations
for the maintenance of fire extinguishing systems, fire and
security and fire alarm system.
Regulations
maintenance of water fire extinguishing systems
List of works Frequency of maintenance by the enterprise operation service Frequency of maintenance by specialized organizations under contract option 1 Frequency of maintenance by specialized organizations under contract option 2
Visual inspection components system (technological part - pipelines, sprinklers, check valves, dosing devices, shut-off valves, pressure gauges, pneumatic tank, pumps, etc.; electrical part - electrical control cabinets, electric motors, etc.), on no damage, corrosion, dirt, leaks; strength of fastenings, presence of seals, etc. Daily Monthly Quarterly
Monitoring pressure, water level, operating position of shut-off valves, etc. Daily Monthly Quarterly
Monitoring the main and backup power sources and checking the automatic switching of power from the working input to the backup input and back The same The same The same
Checking the operability of the system components (technological part, electrical part and signaling part) The same Same Same
Preventative work Monthly Quarterly Quarterly
Checking system functionality in
manual (local, remote) and automatic modes Same Same Same
Flushing of pipelines and changing water in the system and tanks Annually Annually Annually

Measuring the insulation resistance of electrical circuits Once every 3 years Once every 3 years Once every 3 years
Hydraulic and pneumatic testing of pipelines for tightness and strength Once every 3.5 years Once every 3.5 years Once every 3.5 years
Technical examination of system components operating under pressure In accordance with the standards of Gosgortekhnadzor In accordance with the standards of Gosgortekhnadzor In accordance with the standards of Gosgortekhnadzor

Regulations
maintenance of fire alarm systems
External inspection of the system components (control panel, detectors, sirens, alarm loop) for the absence of mechanical damage, corrosion, dirt, fastening strength, etc. Daily Monthly Quarterly
Monitoring the operating position of switches and switches, the serviceability of the light indication, the presence of seals on the receiver - control device Same Same Same
Monitoring the main and backup power sources and checking the automatic switching of power from the working input to
reserve Weekly Same Same
Checking the functionality of the system components (control panel, detectors, sirens,
measurement of alarm loop parameters, etc.) Same Same Same
Preventive maintenance Same Same Same
Checking system functionality Same Same Same
Metrological verification of instrumentation Annually Annually
Measurement of protective and working grounding resistance Annually Annually Annually

Regulations
maintenance of smoke protection systems
List of works Frequency of maintenance by the facility operation service Frequency of maintenance by specialized organizations under contract option 1 Frequency of maintenance by specialized organizations under contract option 2
External inspection of the system components (electrical part of the remote control panel, electrical panel of the floor valve of the local control panel, actuators, fans, pumps, etc.;
signaling part - receiving and control devices, alarm loop, detectors, sirens, etc.) for absence of damage. Corrosion, dirt, strength of fastenings, presence of seals, etc. Daily Monthly Quarterly
Monitoring the operating position of switches and switches, light indication, etc. Same Same Same
Monitoring of the main and backup power sources and automatic switching of power from the working input to
backup and back Weekly Same Same
Checking the functionality of the system components (electrical parts,
signaling part) Same Same Same
Checking system functionality in manual (local, remote) and automatic modes Same Same Same
Metrological verification of instrumentation Annually Annually
Measurements of resistance of protective and working grounding The same The same The same
Measuring the insulation resistance of electrical circuits 1 time every 3 years 1 time every 3 years 1 time every 3 years

Download the operating instructions for fire alarm systems

RUSSIAN JOINT STOCK COMPANY
ENERGY AND ELECTRIFICATION "UES OF RUSSIA"

DEPARTMENT OF SCIENCE AND TECHNOLOGY

STANDARD INSTRUCTIONS
ON THE OPERATION OF AUTOMATIC WATER FIRE-FIGHTING UNITS

RD 34.49.501-95

ORGRES SERVICE OF EXCELLENCE

MOSCOW 1996

DEVELOPED Joint-stock company "Company for adjustment and improvement of technology
and operation of power plants and networks "ORGRES".

AGREED with the Department of the General Inspectorate for the Operation of Power Plants
and networks of RAO UES of Russia December 28, 1995

IN REPLACE TI 34-00-046-85.

VALIDITY installed since 01/01/97

In this Standard instructions basic requirements for operation are given technological equipment water fire extinguishing installations used at energy enterprises, and also sets out the procedure for flushing and pressure testing of pipelines of fire extinguishing installations. The volume and priority of monitoring the condition of process equipment, the timing of the inspection of all equipment of fire extinguishing installations are indicated, and basic recommendations for troubleshooting are given.

Responsibility for the operation of fire extinguishing installations is established, the necessary working documentation and requirements for personnel training are provided.

The basic safety requirements for the operation of fire extinguishing installations are indicated.

Forms for acts of flushing and pressure testing of pipelines and conducting fire tests are given.

With the publication of this Standard Instruction, the “Standard Operating Instructions” becomes invalid automatic installations fire extinguishing: TI 34-00-046-85" (M.: SPO Soyuztekhenergo, 1985).

1. INTRODUCTION

1.1. The standard instructions establish requirements for the operation of technological equipment of water fire extinguishing installations and are mandatory for managers of energy enterprises, shop managers and persons appointed responsible for the operation of fire extinguishing installations.

1.2. Technical requirements for the operation of technological equipment of foam fire extinguishing installations are set out in the “Instructions for the operation of fire extinguishing installations using air-mechanical foam” (M.: SPO ORGRES, 1997).

1.3. When operating the fire alarm of an automatic fire extinguishing installation (AUP), one should be guided by the “Standard Instructions for the Operation of Automatic Fire Alarm Installations at Energy Enterprises” (Moscow: SPO ORGRES, 1996).

The following abbreviations are adopted in this Standard Instruction.

UVP – water fire extinguishing installation,

AUP – automatic fire extinguishing installation,

AUVP - automatic water fire extinguishing installation,

PPS – fire alarm panel,

PUEZ – control panel for electric valves,

PUPN – fire pump control panel,

PI – fire detector,

PN – fire pump,

OK - check valve,

DV – water deluge,

DVM – modernized water drencher,

OPDR – foam-drencher sprinkler.

2. GENERAL INSTRUCTIONS

2.1. Based on this Standard Instruction, the organization that set up the AUP process equipment, together with the energy enterprise where this equipment is installed, must develop local instructions for the operation of the process equipment
and AUP devices. If the adjustment was carried out by an energy enterprise, then the instructions are developed by the personnel of this enterprise. Local instructions must be developed at least one month in advance
before the AUP is accepted into operation.

2.2. The local instructions must take into account the requirements of this Standard Instruction
and the requirements of factory passports and operating instructions for equipment, instruments and apparatus included in the AUVP. Reducing the requirements set out in these documents is not permitted.

2.3. Local instructions must be revised at least once every three years and each time after the reconstruction of the AUP or in the event of a change in operating conditions.

2.4. Acceptance of the AUP for operation must be carried out by representatives of:

energy enterprises (chairman);

design, installation and commissioning organizations;

state fire supervision.

The commission's work program and acceptance certificate must be approved by the chief technical
head of the enterprise.

3. SAFETY PRECAUTIONS

3.1. When operating technological equipment of water fire extinguishing installations
personnel of energy enterprises must comply with the relevant safety requirements specified in the PTE, PTB, as well as in factory passports and operating instructions for a particular
equipment.

3.2. During maintenance and repair of AUP, when visiting a premises protected by AUP, automatic control of a specific distribution pipeline in this direction must be switched to manual (remote) before the last person leaves the premises.

3.3. Pressure testing of pipelines with water should only be carried out according to an approved program,
which should include measures to ensure the protection of personnel from possible rupture of pipelines. It is necessary to ensure complete removal of air from the pipelines. Combining crimping work with other work in the same room is prohibited. If pressure testing is carried out by contractors, then the work is performed according to the work permit. The performance of these works by operational or maintenance personnel of the energy enterprise is documented in written order.

3.4. Before starting work, personnel involved in pressure testing must undergo workplace safety training.

3.5. There should be no unauthorized persons in the room during pressure testing. Pressure testing must be carried out under the supervision of a responsible person.

3.6. Repair work on process equipment must be carried out after removing the pressure from this equipment and preparing the necessary organizational and technical measures established by the current safety regulations.

4. PREPARATION FOR WORK AND CHECKING
TECHNICAL CONDITION OF THE FIRE FIGHTING INSTALLATION

4.1. The water fire extinguishing installation consists of:

source of water supply (reservoir, pond, city water supply, etc.);

fire pumps (designed to collect and supply water to pressure pipelines);

suction pipelines (connecting the water source with fire pumps);

pressure pipelines (from the pump to the control unit);

distribution pipelines (laid within the protected premises);

control units installed at the end of pressure pipelines;

irrigators.

In addition to the above, based on design decisions, the following may be included in the fire extinguishing installation diagram:

a water tank for filling fire pumps;

a pneumatic tank to maintain constant pressure in the network of the fire extinguishing installation;

compressor for replenishing the pneumatic tank with air;

drain valves;

check valves;

dosing washers;

pressure switch;

pressure gauges;

vacuum gauges;

level gauges for measuring the level in tanks and pneumatic tanks;

other signaling, control and automation devices.

A schematic diagram of a water fire extinguishing installation is shown in the figure.

4.2. After graduation installation work suction, pressure and distribution pipelines must be flushed and hydraulically tested. The results of washing and pressing must be documented in reports (Appendices 1 and 2).

If possible, the effectiveness of the fire extinguishing installation should be checked by organizing extinguishing an artificial fire (Appendix 3).

Schematic diagram of a water fire extinguishing installation:

1 – water storage tank; 2 – fire pump (PF) with electric drive; 3 – pressure pipeline;
4 – suction pipeline; 5 – distribution pipeline; 6 – fire detector (PI);
7 – control unit; 8 – pressure gauge; 9 – check valve (OK)

Notese. Backup fire pump with fittings not shown.

4.3. When flushing pipelines, water should be supplied from their ends towards the control units (in order to prevent clogging of pipes with smaller diameter) at a speed 15–20% higher than the speed of water in a fire (determined by calculations or recommendations of design organizations). Washing should continue until sustainable emergence clean water.

If it is impossible to flush certain sections of pipelines, it is permissible to purge them
dry, clean, compressed air or inert gas.

4.4. Hydraulic testing of pipelines must be carried out under a pressure equal to 1.25 working pressure (P), but not less than P+0.3 MPa, for 10 minutes.

To disconnect the tested section from the rest of the network, it is necessary to install blind flanges or plugs. It is not allowed to use existing control units, repair valves, etc. for this purpose.

After 10 minutes of testing, the pressure should be gradually reduced to working pressure and a thorough inspection of all welded joints and adjacent areas should be carried out.

The pipeline network is considered to have passed the hydraulic test if no signs of rupture, leaks or drops are found in the welded joints and on the base metal, visible residual
deformations.

Pressure should be measured with two pressure gauges.

4.5. Flushing and hydraulic testing of pipelines must be carried out in conditions
preventing them from freezing.

It is prohibited to fill open trenches with pipelines that have been exposed to severe frosts, or to fill such trenches with frozen soil.

4.6. Automatic water fire extinguishing installations must operate in automatic start mode. For the period of personnel presence in cable structures (bypass, repair work
etc.) the start-up of installations should be switched to manual (remote) start-up (clause 3.2).

5. MAINTENANCE OF FIRE FIGHTING INSTALLATIONS

5.1. Organizational events

5.1.1. Persons responsible for operation, carrying out capital and current repairs technological equipment of the fire extinguishing installation are appointed by the head of the energy enterprise, who also approves schedules for technical supervision and repair of equipment.

5.1.2. The person responsible for the constant readiness of the process equipment of a fire extinguishing installation must have a good knowledge of the design principle and operating procedure of this equipment,
and also have the following documentation:

project with changes made during installation and commissioning of the fire extinguishing installation;

factory passports and operating instructions for equipment and devices;

this Standard Instruction and local operating instructions for technological equipment;

acts and protocols for conducting installation and commissioning work, as well as testing the operation of technological equipment;

schedules for maintenance and repair of process equipment;

“Logbook of maintenance and repair of fire extinguishing installations.”

5.1.3. Any deviations from the scheme adopted by the project, replacement of equipment, additional
the installation of sprinklers or their replacement with sprinklers with a larger nozzle diameter must be previously agreed upon with the design institute - the author of the project.

5.1.4. To monitor the technical condition of the process equipment of the fire extinguishing installation, a “Logbook of maintenance and repair of the fire extinguishing installation” must be kept, in which the date and time of the inspection, who carried out the inspection, detected malfunctions, their nature and the time of their elimination, the time of forced shutdown and startup must be recorded. fire extinguishing installations, testing of the operation of the entire installation or individual equipment. Approximate form journal is given in Appendix 4.

At least once a quarter, the chief technical manager of the enterprise must familiarize himself with the contents of the magazine against receipt.

5.1.5. To check the readiness and effectiveness of the AUVP, a complete audit of the technological equipment of this installation must be carried out once every three years.

During the inspection, in addition to the main work, pressure testing of the pressure pipeline is carried out and in two or three directions, washing (or purging) and pressure testing of distribution pipelines (clauses 4.2–4.5) located in the most aggressive environment (dampness, gas contamination, dust) are carried out.

If deficiencies are discovered, it is necessary to develop measures to ensure complete
eliminating them in a short time.

5.1.6. Automatic fire extinguishing installation in accordance with the approved schedule
by the head of the relevant workshop, but at least once every three years they must be tested (tested) according to a specially developed program with their actual putting into operation, provided that this
will not entail the shutdown of technological equipment or the entire production process. During testing on the first and last sprinklers, the water pressure and irrigation intensity should be checked.

Testing should be carried out for 1.5–2 minutes with the inclusion of working drainage devices.

Based on the test results, a report or protocol must be drawn up, and the fact of testing must be registered in the “Logbook of maintenance and repair of the fire extinguishing installation.”

5.1.7. Checking the operation of the AUVP or individual species equipment should be carried out during repair, maintenance of the protected premises and technological installation.

5.1.8. For storing spare equipment, equipment parts, and accessories,
tools, materials, instruments necessary for monitoring and organizing repair work of the AUVP, a special room must be allocated.

5.1.9. Technical capabilities AUVP should be included in the operational fire extinguishing plan
at this power plant. During fire drills, it is necessary to expand the circle of personnel who know the purpose and structure of the fire control system, as well as the procedure for putting it into operation.

5.1.10. Personnel servicing AUVP compressors and pneumatic tanks must be trained and certified in accordance with the requirements of the Gosgortekhnadzor rules.

5.1.11. The person responsible for the operation of the process equipment of a fire extinguishing installation must organize training with the personnel allocated to control the operation and maintenance of this equipment.

5.1.12. In the premises of the AUVP pumping station, the following must be posted: instructions on the procedure for putting pumps into operation and opening shut-off valves, as well as circuit and technological diagrams.

5.2. Technical requirements for AUVP

5.2.1. Entrances to the building (room) of the pumping station and fire extinguishing installation, as well as approaches to pumps, pneumatic tanks, compressors, control units, pressure gauges and other equipment of the fire extinguishing installation, must always be free.

5.2.2. In an operating fire extinguishing installation, they must be sealed in working order.
position:

hatches of tanks and containers for storing water supplies;

control units, valves and manual taps;

pressure switch;

drain taps.

5.2.3. After the fire extinguishing system has been activated, its functionality must be fully restored within 24 hours.

5. MAINTENANCE OF FIRE FIGHTING INSTALLATIONS

5.1. Organizational events

5.1.1. Persons responsible for the operation, overhaul and current repairs of process equipment of a fire extinguishing installation are appointed by the head of the energy enterprise, who also approves schedules for technical supervision and repair of equipment.

5.1.2. The person responsible for the constant readiness of the process equipment of a fire extinguishing installation must have a good knowledge of the design principle and operating procedure of this equipment, and also have the following documentation:

  • project with changes made during installation and commissioning of the fire extinguishing installation;
  • factory passports and operating instructions for equipment and devices;
  • this Standard Instruction and local operating instructions for process equipment;
  • acts and protocols for conducting installation and commissioning work, as well as testing the operation of technological equipment;
  • schedules for maintenance and repair of process equipment;
  • "Logbook of maintenance and repair of fire extinguishing installations."
  • 5.1.3. Any deviations from the scheme adopted by the project, replacement of equipment, additional installation of sprinklers or their replacement with sprinklers with a larger nozzle diameter must be previously agreed upon with the design institute - the author of the project.

    5.1.4. To monitor the technical condition of the process equipment of the fire extinguishing installation, a “Logbook of maintenance and repair of the fire extinguishing installation” must be kept, which must record the date and time of the inspection, who carried out the inspection, detected malfunctions, their nature and the time of their elimination, the time of forced shutdown and startup fire extinguishing installations, testing of the operation of the entire installation or individual equipment. An approximate form of the journal is given in Appendix 4.

    At least once a quarter, the chief technical manager of the enterprise must familiarize himself with the contents of the magazine against receipt.

    5.1.5. To check the readiness and effectiveness of the AUVP, a complete audit of the technological equipment of this installation must be carried out once every three years.

    During the inspection, in addition to the main work, pressure testing of the pressure pipeline is carried out and in two or three directions, washing (or purging) and pressure testing of distribution pipelines (clauses 4.2-4.5) located in the most aggressive environment (dampness, gas contamination, dust) are carried out.

    If deficiencies are discovered, it is necessary to develop measures to ensure their complete elimination in a short time.

    5.1.6. Automatic fire extinguishing installations in accordance with the schedule approved by the head of the relevant workshop, but at least once every three years, must be tested (tested) according to a specially developed program with their actual commissioning, provided that this does not entail a shutdown of the process equipment or the entire production process. During testing on the first and last sprinklers, the water pressure and irrigation intensity should be checked.

    Testing should be carried out for 1.5-2 minutes with the inclusion of working drainage devices.

    Based on the testing results, a report or protocol must be drawn up, and the fact of testing must be registered in the “Logbook of maintenance and repair of the fire extinguishing installation.”

    5.1.7. The operation of the AUVP or individual types of equipment should be checked during repairs, maintenance of the protected premises and technological installation.

    5.1.8. A special room must be allocated for storing spare equipment, equipment parts, as well as devices, tools, materials, instruments necessary for monitoring and organizing repair work of the AUVP.

    5.1.9. The technical capabilities of the AUVP should be included in the operational plan for extinguishing a fire at a given energy enterprise. During fire drills, it is necessary to expand the circle of personnel who know the purpose and structure of the fire control system, as well as the procedure for putting it into operation.

    5.1.10. Personnel servicing AUVP compressors and pneumatic tanks must be trained and certified in accordance with the requirements of the Gosgortekhnadzor rules.

    5.1.11. The person responsible for the operation of the process equipment of a fire extinguishing installation must organize training with the personnel allocated to control the operation and maintenance of this equipment.

    5.1.12. In the premises of the AUVP pumping station, the following must be posted: instructions on the procedure for putting pumps into operation and opening shut-off valves, as well as circuit and technological diagrams.

    5.2. Technical requirements for AUVP

    5.2.1. Entrances to the building (room) of the pumping station and fire extinguishing installation, as well as approaches to pumps, pneumatic tanks, compressors, control units, pressure gauges and other equipment of the fire extinguishing installation, must always be free.

    5.2.2. In an operating fire extinguishing installation, the following must be sealed in the operating position:

  • hatches of tanks and containers for storing water supplies;
  • control units, valves and manual taps;
  • pressure switch;
  • drain taps.
  • 5.2.3. After the fire extinguishing system has been activated, its functionality must be fully restored within 24 hours.

    5.3. Water storage tanks

    5.3.1. The water level in the tank must be checked daily and recorded in the “Logbook for maintenance and repair of the fire extinguishing installation.”

    If the water level decreases due to evaporation, it is necessary to add water, if there are leaks, determine the location of damage to the tank and eliminate the leaks.

    5.3.2. The proper operation of the automatic level gauge in the tank must be checked at least once every three months at positive temperatures, monthly at negative temperatures, and immediately in case of doubt about the proper operation of the level gauge.

    5.3.3. Tanks must be closed to access by unauthorized persons and sealed; the integrity of the seal is checked during the inspection of the equipment, but at least once a quarter.

    5.3.4. The water in the tank should not contain mechanical impurities that could clog pipelines, dosing washers and sprinklers.

    5.3.5. To prevent water from rotting and blooming, it is recommended to disinfect it with bleach at the rate of 100 g of lime per 1 m of water.

    5.3.6. The water in the tank must be replaced annually in the fall. When replacing water, the bottom and inner walls of the tank are cleaned of dirt and build-up, and damaged paint is restored or completely renewed.

    5.3.7. Before the onset of frost in buried tanks, the gap between the lower and upper hatch covers must be filled with insulating material.

    5.4. Suction line

    5.4.1. Once a quarter the condition of the inputs, shut-off valves, measuring instruments and a water intake well.

    5.4.2. Before the onset of frost, the fittings in the water intake well must be inspected, repaired if necessary, and the well insulated.

    5.5. Pumping station

    5.5.1. Before testing the pumps, it is necessary to check: the tightness of the seals; lubricant level in bearing baths; correct tightening of foundation bolts, pump cover nuts and bearings; connections of the pipeline on the suction side and the pumps themselves.

    5.5.2. Once a month, pumps and other equipment of the pumping station must be inspected and cleaned of dust and dirt.

    5.5.3. Each fire pump must be turned on at least twice a month to create the required pressure, which is recorded in the operational log.

    5.5.4. At least once a month, the reliability of transferring all fire pumps to the main and backup power supply should be checked and the results recorded in the operational log.

    5.5.5. If there is a special tank for filling pumps with water, the latter must be inspected and painted annually.

    5.5.6: Once every three years, pumps and motors in accordance with clause 5.1.5. of this Standard Instruction must undergo an audit, during which all existing deficiencies are eliminated.

    Repair and replacement of worn parts, checking of seals are carried out as necessary.

    5.5.7. The pumping station premises must be kept clean. When not on duty, it must be locked. One of the spare keys must be stored on the control panel, as indicated on the door.

    5.6. Pressure and distribution pipelines

    5.6.1. Once a quarter you need to check:

  • absence of leaks and deflections of pipelines;
  • the presence of a constant slope (at least 0.01 for pipes with a diameter of up to 50 mm and 0.005 for pipes with a diameter of 50 mm or more);
  • condition of pipeline fastenings;
  • no contact with electrical wires and cables;
  • condition of painting, absence of dirt and dust.
  • Detected deficiencies that may affect the reliability of the installation must be corrected immediately.

    5.6.2. The pressure pipeline must be in constant readiness for action, i.e. filled with water and under operating pressure.

    5.7. Control units and shut-off valves

    5.7.1. For AUVP transformers and cable structures in shut-off and start-up devices, steel fittings should be used: electrified gate valves with automatic start, grade 30s 941nzh; 30s 986nzh; 30s 996nzh with a working pressure of 1.6 MPa, repair valves with manual drive brand 30s 41nzh with a working pressure of 1.6 MPa.

    5.7.2. The condition of control units and shut-off valves, the presence of seals, and pressure values ​​before and after control units must be monitored at least once a month.

    5.7.3. An inspection must be carried out once every six months electrical diagram activation of the control unit with its automatic activation from the fire detector when the valve is closed.

    5.7.4. The installation site of the control unit must be well lit, the inscriptions on the pipelines or special stencils (node ​​number, protected area, type of sprinklers and their quantity) must be made with indelible bright paint and be clearly visible.

    5.7.5. All damage to valves, valves and check valves that may affect the reliability of the fire extinguishing installation must be repaired immediately.

    5.8. Sprinklers

    5.8.1. OPDR-15 sprinklers with a working water pressure in front of the sprinklers in the range of 0.2-0.6 MPa are used as water sprinklers for automatic fire extinguishing of transformers; For automatic fire extinguishing of cable structures, DV and DVM sprinklers with a working pressure of 0.2-0.4 MPa are used.

    5.8.2. When inspecting the equipment distribution devices, but at least once a month, sprinklers must be inspected and cleaned of dust and dirt. If a malfunction or corrosion is detected, measures must be taken to eliminate it.

    5.8.3. When carrying out repair work, sprinklers must be protected from plaster and paint (for example, with polyethylene or paper caps, etc.). Traces of paint and mortar found after repair must be removed.

    5.8.5. To replace faulty or damaged sprinklers, a reserve of 10-15% of the total number of installed sprinklers should be created.

    5.9. Air tank and compressor

    5.9.1. Putting the pneumatic tank into operation must be done in the following sequence:

  • fill the pneumatic tank with water to approximately 50% of its volume (check the level using the water gauge glass);
  • turn on the compressor or open the valve on the compressed air pipeline;
  • raise the pressure in the pneumatic tank to operating pressure (controlled by a pressure gauge), after which the pneumatic tank is connected to the pressure pipeline, creating working pressure in it.
  • 5.9.2. Every day you should carry out an external inspection of the air tank, check the water level and air pressure in the air tank. When the air pressure decreases by 0.05 MPa (relative to the working one), it is pumped up.

    Once a week the compressor is tested at idle.

    5.9.3. Maintenance of the air tank and compressor, carried out once a year, includes:

  • emptying, inspecting and cleaning the air tank;
  • removal and testing on a bench safety valve(if faulty, replace with a new one);
  • painting the surface of the air tank (indicate the date of repair on the surface);
  • detailed inspection of the compressor (replace worn parts and fittings);
  • fulfillment of all others technical requirements provided by the manufacturer's data sheets and operating instructions for the pneumatic tank and compressor.
  • 5.9.4. Disconnecting the pneumatic tank from the fire extinguishing installation circuit is prohibited.

    5.9.5. The pneumatic tank is inspected special commission with the participation of representatives of Gosgortekhnadzor, local bodies of the State Fire Supervision and this energy enterprise.

    _________
    Note. The compressor must only be started manually. In this case, it is necessary to monitor the level in the air tank, since when the compressor is automatically turned on, it is possible that water can be squeezed out of the air tank and even from the network by air.

    5.10. Pressure gauges

    5.10.1. The correct operation of pressure gauges installed on pneumatic tanks should be checked once a month; those installed on pipelines should be checked once every six months.

    5.10.2. A complete check at the fire extinguishing installation of all pressure gauges with their sealing or branding must be carried out annually in accordance with the current regulations.

    RUSSIAN JOINT STOCK COMPANY SOCIETYENERGY
    AND
    ELECTRIFICATION « UESRUSSIA»

    DEPARTMENTSCIENCEANDTECHNIQUES

    TYPICALINSTRUCTIONS
    BY
    OPERATIONAUTOMATIC
    INSTALLATIONS
    WATERFIRE FIGHTING

    RD 34.49.501-95

    ORGRES

    Moscow 1996

    DevelopedJoint-stock company “Company for adjustment, improvement of technology and operation of power plants and networks “ORGRES”.

    PerformersYES. ZAZAMLOV, A.N. IVANOV, A.S. KOZLOV, V.M. OLD PEOPLE

    Agreedwith the Department of the General Inspectorate for the Operation of Power Plants and Networks of RAO UES of Russia on December 28, 1995.

    Chief N.F. Gorev

    ApprovedDepartment of Science and Technology of RAO UES of Russia December 29, 1995

    Chief A.P. BERSENEV

    STANDARD INSTRUCTIONS FOR OPERATING AUTOMATIC WATER FIRE FIGHTING UNITS

    RD 34.49.501-95

    Expiration date set

    from 01/01/97

    This Standard Instruction contains the basic requirements for the operation of technological equipment of water fire extinguishing installations used at energy enterprises, and also sets out the procedure for flushing and pressure testing of pipelines of fire extinguishing installations. The volume and priority of monitoring the condition of process equipment, the timing of the inspection of all equipment of fire extinguishing installations are indicated, and basic recommendations for troubleshooting are given.

    Responsibility for the operation of fire extinguishing installations is established, the necessary working documentation and requirements for personnel training are provided.

    The basic safety requirements for the operation of fire extinguishing installations are indicated.

    Forms for acts of flushing and pressure testing of pipelines and conducting fire tests are given.

    With the release of this Standard Instruction, the “Standard Instructions for the Operation of Automatic Fire Extinguishing Installations: TI 34-00-046-85” (Moscow: SPO Soyuztekhenergo, 1985) becomes invalid.

    1. INTRODUCTION

    1.1 . The standard instructions establish requirements for the operation of technological equipment of water fire extinguishing installations and are mandatory for managers of energy enterprises, shop managers and persons appointed responsible for the operation of fire extinguishing installations.

    1.2 . Technical requirements for the operation of technological equipment of foam fire extinguishing installations are set out in the “Instructions for the operation of fire extinguishing installations using air-mechanical foam” (M.: SPO ORGRES, 1997).

    1.3 . When operating an automatic fire alarmfire extinguishing installations (AUP) should be guided by the “Standard Instructions for the Operation of Automatic Fire Alarm Installations at Energy Enterprises” (Moscow: SPO ORGRES, 1996).

    The following abbreviations are adopted in this Standard Instruction.

    UVP - water fire extinguishing installation,

    AUP - automatic fire extinguishing installation,

    AUVP - automatic water fire extinguishing installation,

    PPS - fire alarm panel,

    PUEZ - control panel for electric valves,

    PUPN - fire pump control panel,

    PI - fire detector,

    PN - fire pump,

    OK - check valve,

    DV - water deluge,

    DVM - modernized water drencher,

    OPDR - foam-drencher sprinkler.

    2. GENERAL INSTRUCTIONS

    2.1 . Based on this Standard Instruction, the organization that carried out the adjustment of the process equipment of the automatic control system, together with the energy enterprise where this equipment is installed, must develop local instructions for the operation of the technological equipment and devices of the automatic control system. If the adjustment was carried out by an energy enterprise, then the instructions are developed by the personnel of this enterprise. Local instructions must be developed at least one month before the AUP is accepted into operation.

    2.2 . The local instructions must take into account the requirements of this Standard Instruction and the requirements of factory passports and operating instructions for equipment, instruments and apparatus included in the AUVP. Reducing the requirements set out in these documents is not permitted.

    2.3 . Local instructions must be revised at least once every three years and each time after the reconstruction of the AUP or in the event of a change in operating conditions.

    2.4 . Acceptance of the AUP for operation must be carried out by representatives of:

    energy enterprises (chairman);

    design, installation and commissioning organizations;

    state fire supervision.

    The commission's work program and acceptance certificate must be approved by the chief technical manager of the enterprise.

    3. SAFETY PRECAUTIONS

    3.1 . When operating technological equipment of water fire extinguishing installations, personnel of energy enterprises must comply with the relevant safety requirements specified in PTE, PTB, as well as in factory passports and operating instructions for specific equipment.

    3.2 . During maintenance and repair of the automatic control system, when visiting a room protected by the automatic control system, the automatic control of a specific distribution pipeline in this direction must be switched to manual (remote) until the last person leaves the room.

    3.3 . Pressure testing of pipelines with water should be carried out only according to an approved program, which should include measures to ensure the protection of personnel from possible rupture of pipelines. It is necessary to ensure complete removal of air from the pipelines. Combining crimping work with other work in the same room is prohibited. If pressure testing is carried out by contractors, then the work is performed according to the work permit. The performance of these works by operational or maintenance personnel of the energy enterprise is documented in written order.

    3.4 . Before starting work, personnel involved in pressure testing must undergo workplace safety training.

    3.5 . There should be no unauthorized persons in the room during pressure testing. Pressure testing must be carried out under the supervision of a responsible person.

    3.6 . Repair work on process equipment must be carried out after removing the pressure from this equipment and preparing the necessary organizational and technical measures established by the current safety regulations.

    4. PREPARATION FOR OPERATION AND CHECKING THE TECHNICAL CONDITION OF THE FIRE FIGHTING INSTALLATION

    4.1 . The water fire extinguishing installation consists of:

    source of water supply (reservoir, pond, city water supply, etc.);

    fire pumps (designed to collect and supply water to pressure pipelines);

    suction pipelines (connecting the water source with fire pumps);

    pressure pipelines (from the pump to the control unit);

    distribution pipelines (laid within the protected premises);

    control units installed at the end of pressure pipelines;

    irrigators.

    In addition to the above, based on design decisions, the following may be included in the fire extinguishing installation diagram:

    a water tank for filling fire pumps;

    a pneumatic tank to maintain constant pressure in the network of the fire extinguishing installation;

    compressor for replenishing the pneumatic tank with air;

    drain valves;

    check valves;

    dosing washers;

    pressure switch;

    pressure gauges;

    vacuum gauges;

    level gauges for measuring the level in tanks and pneumatic tanks;

    other signaling, control and automation devices.

    A schematic diagram of a water fire extinguishing installation is shown in the figure.

    4.2 . After completion of installation work, suction, pressure and distribution pipelines must be washed and subjected to hydraulic tests. The results of washing and pressure testing must be documented in reports (appendices And ).

    If possible, you should check the effectiveness of the fire extinguishing installation by organizing extinguishing an artificial fire (Appendix).

    4.3 . When flushing pipelines, water should be supplied from themends towards the control units (in order to prevent clogging of pipes with a smaller diameter) at a speed of 15 - 20% greater than the speed of water in a fire (determined by calculations or recommendations of design organizations). Flushing should be continued until clean water appears steadily.

    If it is impossible to flush certain sections of pipelines, it is allowed to blow them with dry, clean, compressed air or inert gas.


    Schematic diagram of a water fire extinguishing installation:

    1 - water storage tank; 2 - fire pump (PN) with electric drive; 3 - pressure pipeline; 4 - suction pipeline; 5 - distribution pipeline; 6 - fire detector (PI); 7 - control unit; 8 - pressure gauge; 9 - check valve (OK)

    Note.The backup fire pump with fittings is not shown.

    4.4 . Hydraulic testing of pipelines must be carried out under a pressure equal to 1.25 working pressure (P), but not less than P + 0.3 MPa, for 10 minutes.

    To disconnect the tested section from the rest of the network, it is necessary to install blind flanges or plugs. It is not allowed to use existing control units, repair valves, etc. for this purpose.

    After 10 minutes of testing, the pressure should be gradually reduced to working pressure and a thorough inspection of all welded joints and adjacent areas should be carried out.

    The pipeline network is considered to have passed the hydraulic test if there are no signs of rupture, leaks, drops in welded joints or on the base metal, or visible residual deformations.

    Pressure should be measured with two pressure gauges.

    4.5 . Flushing and hydraulic testing of pipelines must be carried out under conditions that prevent them from freezing.

    It is prohibited to fill open trenches with pipelines that have been exposed to severe frosts, or to fill such trenches with frozen soil.

    4.6 . Automatic water fire extinguishing installations must operate in automatic start mode. During the period of personnel presence in cable structures (bypass, repair work, etc.), the start-up of installations must be switched to manual (remote) activation (clause ).

    5. MAINTENANCE OF FIRE FIGHTING INSTALLATIONS

    5.1 . Organizational events

    5.1.1 . Persons responsible for the operation, overhaul and current repairs of process equipment of a fire extinguishing installation are appointed by the head of the energy enterprise, who also approves schedules for technical supervision and repair of equipment.

    5.1.2 . The person responsible for the constant readiness of the process equipment of a fire extinguishing installation must have a good knowledge of the design principle and operating procedure of this equipment, and also have the following documentation:

    project with changes made during installation and commissioning of the fire extinguishing installation;

    factory passports and operating instructions for equipment and devices;

    this Standard Instruction and local operating instructions for process equipment;

    acts and protocols for conducting installation and commissioning work, as well as testing the operation of technological equipment;

    schedules for maintenance and repair of process equipment;

    “Logbook of maintenance and repair of fire extinguishing installations.”

    5.1.3 . Any deviations from the scheme adopted by the project, replacement of equipment, additional installation of sprinklers or their replacement with sprinklers with a larger nozzle diameter must be previously agreed upon with the design institute - the author of the project.

    5.1.4 . To monitor the technical condition of the process equipment of the fire extinguishing installation, a “Logbook of maintenance and repair of the fire extinguishing installation” must be kept, in which the date and time of the inspection, who carried out the inspection, detected malfunctions, their nature and the time of their elimination, the time of forced shutdown and startup must be recorded. fire extinguishing installations, testing of the operation of the entire installation or individual equipment. An approximate form of the journal is given in the appendix .

    At least once a quarter, the chief technical manager of the enterprise must familiarize himself with the contents of the magazine against receipt.

    5.1.5 . To check the readiness and effectiveness of the AUVP, a complete audit of the technological equipment of this installation must be carried out once every three years.

    During the inspection, in addition to the main work, pressure testing of the pressure pipeline is carried out and in two or three directions, washing (or purging) and pressure testing of distribution pipelines (points -) located in the most aggressive environment (dampness, gas contamination, dust) are carried out.

    If deficiencies are discovered, it is necessary to develop measures to ensure their complete elimination in a short time.

    5.1.6 . Automatic fire extinguishing installations in accordance with the schedule approved by the head of the relevant workshop, but at least once every three years, must be tested (tested) according to a specially developed program with their actual commissioning, provided that this does not entail a shutdown of the process equipment or the entire production process. During testing on the first and last sprinklers, the water pressure and irrigation intensity should be checked.

    Testing should be carried out for 1.5 - 2 minutes with the inclusion of serviceable drainage devices.

    Based on the test results, a report or protocol must be drawn up, and the fact of testing must be registered in the “Logbook of maintenance and repair of the fire extinguishing installation.”

    5.1.7 . The operation of the AUVP or individual types of equipment should be checked during repairs, maintenance of the protected premises and technological installation.

    5.1.8 . A special room must be allocated for storing spare equipment, equipment parts, as well as devices, tools, materials, instruments necessary for monitoring and organizing repair work of the AUVP.

    5.1.9 . The technical capabilities of the AUVP should be included in the operational plan for extinguishing a fire at a given energy enterprise. During fire drills, it is necessary to expand the circle of personnel who know the purpose and structure of the fire control system, as well as the procedure for putting it into operation.

    5.1.10 . Personnel servicing AUVP compressors and pneumatic tanks must be trained and certified in accordance with the requirements of the Gosgortekhnadzor rules.

    5.1.11 . The person responsible for the operation of the process equipment of a fire extinguishing installation must organize training with the personnel allocated to control the operation and maintenance of this equipment.

    5.1.12 . In the premises of the AUVP pumping station, the following must be posted: instructions on the procedure for putting pumps into operation and open shut-off valves, as well as schematic and technological diagrams.

    5.2 . Technical requirements for AUVP

    5.2.1 . Entrances to the building (room) of the pumping station and fire extinguishing installation, as well as approaches to pumps, pneumatic tanks, compressors, control units, pressure gauges and other equipment of the fire extinguishing installation, must always be free.

    5.2.2 . In an operating fire extinguishing installation, the following must be sealed in the operating position:

    hatches of tanks and containers for storing water supplies;

    control units, valves and manual taps;

    pressure switch;

    drain taps.

    5.2.3 . After the fire extinguishing system has been activated, its functionality must be fully restored no later than 24 hours later.

    5.3 . Water storage tanks

    5.3.1 . The water level in the tank must be checked daily and recorded in the “Logbook for maintenance and repair of the fire extinguishing installation.”

    If the water level decreases due to evaporation, it is necessary to add water, if there are leaks, determine the location of damage to the tank and eliminate the leaks.

    5.3.2 . The proper operation of the automatic level gauge in the tank must be checked at least once every three months at positive temperatures, monthly at negative temperatures, and immediately in case of doubt about the proper operation of the level gauge.

    5.3.3 . Tanks must be closed to access by unauthorized persons and sealed; the integrity of the seal is checked during the inspection of the equipment, but at least once a quarter.

    5.3.4 . The water in the tank should not contain mechanical impurities that could clog pipelines, dosing washers and sprinklers.

    5.3.5 . To prevent decay and blooming of water, it is recommended to disinfect it with bleach at the rate of 100 g of lime per 1 m 3 of water.

    5.3.6 . The water in the tank must be replaced annually in the fall.her time. When replacing water, the bottom and inner walls of the tank are cleaned of dirt and build-up, and damaged paint is restored or completely renewed.

    5.3.7 . Before the onset of frost in buried tanks, the gap between the lower and upper hatch covers must be filled with insulating material.

    5.4 . Suction line

    5.4.1 . Once a quarter, the condition of the inputs, shut-off valves, measuring instruments and water intake well is checked.

    5.4.2 . Before the onset of frost, the fittings in the water intake well must be inspected, repaired if necessary, and the well insulated.

    5.5 . Pumping station

    5.5.1 . Before testing the pumps, it is necessary to check: the tightness of the seals; lubricant level in bearing baths; correct tightening of foundation bolts, pump cover nuts and bearings; connections of the pipeline on the suction side and the pumps themselves.

    5.5.2 . Once a month, pumps and other equipment of the pumping station must be inspected and cleaned of dust and dirt.

    5.5.3 . Each fire pump must be turned on at least twice a month to create the required pressure, which is recorded in the operational log.

    5.5.4 . At least once a month, the reliability of transferring all fire pumps to the main and backup power supply should be checked and the results recorded in the operational log.

    5.5.5 . If there is a special tank for filling pumps with water, the latter must be inspected and painted annually.

    5.5.6 . Once every three years, pumps and motors in accordance with paragraph. . of this Standard Instruction must undergo an audit, during which all existing deficiencies are eliminated.

    Repair and replacement of worn parts, checking of seals are carried out as necessary.

    5.5.7 . The pumping station premises must be kept clean. When not on duty, it must be locked. One of the spare keys must be stored on the control panel, as indicated on the door.

    5.6 . Pressure and distribution pipelines

    5.6.1 . Once a quarter you need to check:

    absence of leaks and deflections of pipelines;

    the presence of a constant slope (at least 0.01 for pipes with a diameter of up to 50 mm and 0.005 for pipes with a diameter of 50 mm or more);

    condition of pipeline fastenings;

    no contact with electrical wires and cables;

    condition of painting, absence of dirt and dust.

    Detected deficiencies that may affect the reliability of the installation must be corrected immediately.

    5.6.2 . The pressure pipeline must be in constant readiness for action, i.e. filled with water and under operating pressure.

    5.7 . Control units and shut-off valves

    5.7.1 . For AUVP transformers and cable structures in shut-off and start-up devices, steel fittings should be used: electrified gate valves with automatic start-up, brand 30s 941nzh; 30s 986nzh; 30s 996nzh with a working pressure of 1.6 MPa, repair valves with manual drive brand 30s 41nzh with a working pressure of 1.6 MPa.

    5.7.2 . The condition of control units and shut-off valves, the presence of seals, and pressure values ​​before and after control units must be monitored at least once a month.

    5.7.3 . Once every six months, the electrical circuit of the control unit should be checked with its automatic activation from the fire detector when the valve is closed.

    5.7.4 . The installation site of the control unit must be well lit, the inscriptions on the pipelines or special stencils (node ​​number, protected area, type of sprinklers and their quantity) must be made with indelible bright paint and be clearly visible.

    5.7.5 . All damage to valves, valves and check valves that may affect the reliability of the fire extinguishing installation must be repaired immediately.

    5.8 . Sprinklers

    5.8.1 . OPDR-15 sprinklers with a working water pressure in front of the sprinklers in the range of 0.2 - 0.6 MPa are used as water sprinklers for automatic fire extinguishing of transformers; For automatic fire extinguishing of cable structures, DV, DVM sprinklers with a working pressure of 0.2 - 0.4 MPa are used.

    5.8.2 . When inspecting switchgear equipment, but at least once a month, sprinklers must be inspected and cleaned of dust and dirt. If a malfunction or corrosion is detected, measures must be taken to eliminate it.

    5.8.3 . When carrying out repair work, sprinklers must be protected from plaster and paint (for example, with polyethylene or paper caps, etc.). Traces of paint and mortar found after repair must be removed.

    5.8.4 . It is prohibited to install plugs or plugs in place of faulty sprinklers.

    5.8.5 . To replace faulty or damaged sprinklers, a reserve of 10 - 15% of the total number of installed sprinklers should be created.

    5.9 . Air tank and compressor

    5.9.1 . Putting the pneumatic tank into operation must be done in the following sequence:

    fill the pneumatic tank with water to approximately 50% of its volume (check the level using the water gauge glass);

    turn on the compressor or open the valve on the compressed air pipeline;

    raise the pressure in the pneumatic tank to the operating pressure (controlled by a pressure gauge), after which the pneumatic tank is connected to the pressure pipeline, creating a working pressure in it.

    5.9.2 . Every day you should carry out an external inspection of the air tank, check the water level and air pressure in the air tank. When the air pressure decreases by 0.05 MPa (relative to the working one), it is pumped up.

    Once a week the compressor is tested at idle.

    5.9.3 . Maintenance of the air tank and compressor, carried out once a year, includes:

    Emptying, inspecting and cleaning the air tank:

    removing and testing the safety valve on a bench (if faulty, replace it with a new one);

    painting the surface of the air tank (indicate the date of repair on the surface);

    detailed inspection of the compressor (replace worn parts and fittings);

    fulfillment of all other technical requirements stipulated by the factory passports and operating instructions for the pneumatic tank and compressor.

    5.9.4 . Disconnecting the pneumatic tank from the fire extinguishing installation circuit is prohibited.

    5.9.5 . The inspection of the pneumatic tank is carried out by a special commission with the participation of representatives of Gosgortekhnadzor, local bodies of the State Fire Supervision and the given energy enterprise.

    Note.The compressor must only be started manually. In this case, it is necessary to monitor the level in the air tank, since when the compressor is automatically turned on, it is possible that water can be squeezed out of the air tank and even from the network by air.

    5.10 . Pressure gauges

    5.10.1 . The correct operation of pressure gauges installed on pneumatic tanks should be checked once a month; those installed on pipelines should be checked once every six months.

    5.10.2 . A complete check at the fire extinguishing installation of all pressure gauges with their sealing or branding must be carried out annually in accordance with the current regulations.

    6. ORGANIZATION AND REQUIREMENTS FOR REPAIR WORK

    6.1 . When repairing process equipment of a fire extinguishing installation, one should, first of all, be guided by the requirements of the passport, the plant’s instructions for operating specific equipment, the requirements of the relevant standards and technical conditions, as well as the requirements of this Standard Instruction.

    6.2 . When replacing a section of pipeline at a bend, the minimum radius of the internal bend curve steel pipes must be atbending them in a cold state with at least four outer diameters, in a hot state - at least three.

    There should be no folds, cracks or other defects on the curved part of the pipe. Ovality in places of bending is allowed no more than 10% (determined by the ratio of the difference between the largest and smallest outer diameters of the bent pipe to the outer diameter of the pipe before the bend).

    6.3 . The difference in thickness and displacement of the edges of joined pipes and pipeline parts should not exceed 10% of the wall thickness and should not exceed 3 mm.

    6.4 . Before welding, the edges of the pipe ends to be welded and the surfaces adjacent to them must be cleaned of rust and dirt to a width of at least 20 mm.

    6.5 . Welding of each joint must be performed without interruption until the entire joint is completely welded.

    6.6 . The welded pipe joint must be rejected if the following defects are detected:

    cracks extending to the surface of the weld or base metal in the welding zone;

    sagging or undercuts in the transition zone from the base metal to the deposited metal;

    burns;

    unevenness of the weld seam in width and height, as well as its deviations from the axis.

    6.7 . In particularly damp rooms with a chemically active environment, pipeline fastening structures must be made of steel profiles with a thickness of at least 4 mm. Piping and fastening structures must be covered protective varnish or paint.

    6.8 . Pipeline connections during open installation must be located outside walls, partitions, ceilings and other building structures of buildings.

    6.9 . The fastening of pipelines to the building structures must be carried out using normalized supports and hangers. Welding pipelines directly to metal structures buildings and structures, as well as elements of technological equipment is not allowed.

    6.10 . Welding of supports and hangers to building structures must be carried out without weakening their mechanical strength.

    6.11 . Sagging and bending of pipelines is not allowed.

    6.12 . Each turn of a pipeline longer than 0.5 m musthave a mount. The distance from hangers to welded and threaded joints of pipes must be at least 100 mm.

    6.13 . Newly installed sprinklers must be cleaned of preservative grease and checked hydraulic pressure 1.25 MPa (12.5 kgf/cm2) for 1 min.

    The average service life of sprinklers is determined to be at least 10 years.

    6.14 . The performance of sprinklers DV, DVM and OPDR-15 is given in table. .

    Table 1

    Sprinkler type

    Outlet diameter, mm

    Sprinkler capacity, l/s, at pressure MPa

    DV-10 and DVM-10

    OPDR-15

    7. CHARACTERISTIC MALFUNCTIONS AND METHODS OF THEIR ELIMINATION

    7.1 . Possible faults in the operation of a water fire extinguishing installation and recommendations for eliminating them are given in Table. .

    table 2

    Nature of the malfunction, external signs

    Probable Causes

    Water does not come out of the sprinklers, the pressure gauge shows normal pressure

    The valve is closed

    Open the valve

    Check valve stuck

    Open check valve

    The pipeline is clogged

    Clean the pipeline

    Sprinklers are clogged

    Clear the blockage

    Water does not come out of the sprinklers, the pressure gauge does not show pressure

    The fire pump did not start working

    Turn on the fire pump

    The valve on the pipeline on the suction side of the fire pump is closed

    Open the valve

    There is an air leak on the suction side of the fire pump

    Troubleshoot connection problems

    Wrong direction of rotor rotation

    Switch motor phases

    A valve in the other direction is accidentally opened

    Close the valve in the other direction

    Water leakage through welded seams, in places where control units and sprinklers are connected

    Poor quality welding

    Check the quality of welds

    The gasket is worn out

    Replace gasket

    Loose bolts

    Tighten the bolts

    No pressure gauge reading

    There is no pressure in the pipeline

    Restore pressure in the pipeline

    The inlet is clogged

    Remove the pressure gauge and clean the hole

    Sparking pressure gauge contacts

    Contamination of pressure gauge contacts

    Remove the pressure gauge glass and clean the contacts

    Annex 1

    ACT
    WASHING PIPELINES OF FIRE FIGHTING INSTALLATIONS

    G . _______________ “____”_________ 19__

    Object name ________________ ____________________________________

    (power plant, substation)

    We, the undersigned __________________________________________________

    in the face ___________________________________________________________________

    (representative from the customer, full name, position)

    _________________________________________________________________________

    And _______________________________________________________________________

    (representative from the installation organization, full name, position)

    _________________________________________________________________________

    have drawn up this act that the pipelines ___________________________________

    _________________________________________________________________________

    (installation name, section number)

    Operating instructions for fire extinguishing systems, fire extinguishing systems, fire extinguishing systems, fire extinguishing systems based on the Corundum 1I Control Panel

    I approve

    ______________________________________________________

    INSTRUCTIONS

    for the operation of fire extinguishing systems, fire alarms and warning people about fire at the address: ___________________________________________________________

    Control Panel "Corundum 1I"

    1. 1. A common part.
    2. 2. The fire alarm system is designed to detect and notify about the occurrence of a fire.

    2.1. The system must be in standby mode 24/7.

    3. Responsibilities of the shift supervisor to maintain the PS installation in working condition.

    3.1. The shift supervisor is obliged to conduct an external inspection of all protected premises for damage to installed equipment and devices.

    3.2. Monitor all malfunctions and system activations, report them to the head of the unit and the security officer on duty at the checkpoint.

    4. Operation of the system during a fire.

    Actions of the shift supervisor when the control panel "Corundum 1 I" is triggered

    On the front panel of the device there are light indicators (LEDs red and yellow color) indicators state of alarm loops from 1 to 4 are not glowing LEDs correspond to the on state of the alarm loops, power indicator " NET» backup power indicator « RESERVE" red from states 1 to 4 " FIRE» train.

    Control buttons: " NET» switching on 220 V power supply and backup power supply direct current 24 V, toggle switches for disabling alarm loops from 1 to 4 button " CONTROL" to check the device in the " mode SELF-CONTROL", button " SOUND" to turn off the sound signal, buttons, button " RESET» to restore the state of the loops after triggering. Toggle switches for turning off (turning on loops) and toggle switches for turning off (turning on) ASPT systems are covered with a protective casing.

    When the devices are working properly and the fire alarm loops are working properly, LEDs 1 to 4 on the linear units and on the instrument panel are off, the LED lights up green, the reserve LED is on.

    In the event of a malfunction in a loop (or several loops), the yellow LED “ FAULT» on the corresponding linear unit and on the instrument panel. The device produces a characteristic intermittent fault signal on the device remote control.

    IN in this case disable the button SOUND", open protective cover linear units, turn off the toggle switch of the corresponding loop and press the button " RESET» to restore the “standby” state of the device, make a record of the time of the malfunction and record the number of the faulty loop in the operational log, report to management and call representatives of the organization performing maintenance of the alarm system.

    If the device is triggered by fire detectors in the “ FIRE", the red LED lights up " FIRE» the corresponding loop(s) sounds a characteristic continuous sound signal on the device, the remote sounder in the corridor turns on. In this case, turn off the sound signal of the device (the button on the panel " SOUND") check the premises of the corresponding plume for no signs of combustion, if the event is confirmed " FIRE» Call the fire brigade by phone. 01 and, to the extent possible, take measures to extinguish the fire using available fire extinguishing means.

    At the same time, report to the head of the unit and call the checkpoint, inform the security officer on duty about the fire.

    When false alarm: open the protective casing of the linear units, turn off the toggle switch of the corresponding loop, press the button " RESET» to restore the “standby” state of the device, make a record of the time of the malfunction and record the number of the faulty loop in the operational log, report to the head of the department and call representatives of the organization performing maintenance of the alarm system.

    If the main power source of the device is turned off, backup power The device remains on, which will be indicated by the red LED “ RESERVE" After restoring the main power to the device, call a service representative to check and recharge, if necessary, the battery.

    About the serviceability of the backup power supply and battery. batteries are signaled by LEDs " NET" red and " ACC. BAT." green on backup source nutrition.

    Responsible person for fire automatics