Solenoid solenoid valve CEME solenoid valves
Solenoid valves occupy a significant part of the company's product range. This Italian company produces more than 20 series of solenoid shut-off valves designed to control the flow of transported media of various types. state of aggregation and varying degrees of aggressiveness.
Areas of application
Shut-off valves from this manufacturer can be installed in the following systems for transporting liquid and gaseous media:
- Water and steam supply lines. Moreover, for drinking water, special normally closed or open solenoid valves with DVGW type seal, and for steam - with EPDM type seal. Such fittings are suitable for an iron, a washing machine, and a vacuum cleaner operating from a household electrical outlet (220 volts).
- Oil product supply lines. Moreover, for diesel fuel or light oil requires a special FPM seal. It protects normally open or closed valves from leaks of a chemically active medium that corrodes water seals from the very first hour of operation. Therefore, diesel solenoid valves are included in a special series.
- Gas supply lines. Only for inert gases can you use almost any normally closed or open solenoid valves, for example, suitable for water (can be technical). And for flammable media - propane and so on - you need special gas fittings certified according to the CEE 90/396 standard. Standard water or steam valve won't be useful here. Moreover, for gas fuel you also need a special coil operating under a voltage of 12 volts or 24 volts. This voltage eliminates sparking.
- Coolant supply lines. In this case, you need normally open or open solenoid valves with an insert suitable for low temperature liquids or gases of any type except ammonia. Moreover, the solenoid of such a valve should work even at 50 degrees below zero. Although for air conditioner or household refrigerators You can use reinforcement with less frost resistance.
Where to buy solenoid valves?
In Russia, you can buy SEME solenoid valves only from resellers or official representative offices of this brand.
Resellers offer a limited range, without subsequent purchase support. Moreover, their product may turn out to be a Chinese counterfeit. original product from Italy. In this case, it no longer matters how much the product costs - its operation will cost the buyer much more than the initial expenses.
Official SEME dealers, such as our online store website, do not dump “to spite” competitors, but offer more significant ones than low prices, advantages.
What are the advantages of an online store website?
- Firstly, the site is the official distributor of Ceme. That's why we sell only original products.
- Secondly, you can even buy specialized types of fittings in our store. The store website offers a selection of products comparable to the official website, delivered directly from Italy.
- Thirdly, the site offers organized delivery of goods throughout Moscow and throughout Russia. In addition, delivery to order to Belarus and Kazakhstan is also possible.
Name | vendor code | Voltage | Price |
---|---|---|---|
Solenoid valve non-closed 3/8" (DN 10) | CEME8613.NBR230 | U=220B | 3,100 rub. |
Solenoid valve n/closed 1/2" (DN 15) | CEME8614.NBR230 | U=220B | 3,100 rub. |
Solenoid valve non-closed 3/4" (DN 20) | SEME8615.NBR230 | U=220B | 3,300 rub. |
Solenoid valve non-closed 1" (DN 25) | CEME8616.NBR230 | U=220B | 3,300 rub. |
Solenoid valve non-closed 1"1/4 (DN 32) | CEME8617.NBR230 | U=220B | 7,000 rub. |
Solenoid valve non-closed 1"1/2 (DN 40) | SEME8618.NBR230 | U=220B | 7,000 rub. |
Solenoid valve non-closed 2" (DN 50) | CEME8619.NBR230 | U=220B | RUB 11,650 |
Solenoid valve non-closed 2"1/2 (DN 65) | SEME8620.NBR230 | U=220B | RUB 27,440 |
Solenoid valve non-closed 3" (DN 75) | CEME8621.NBR230 | U=220B | RUB 34,800 |
Reel for non-closed valve | SEME BDF/R | U=220B | 500 rub. |
Reel for non-closed valve | SEME86 | U=24B | 500 rub. |
Normally open solenoid valves
Electromagnetic solenoid valves CEME
Solenoid electromagnetic valves SEME (Italy) are used in water supply and heat supply networks, in various industries industry, in water treatment and air conditioning systems. By design they are divided into normally open- are situated in open position in the absence of power and close when current is applied to the coil, and normally closed valves- are situated in closed position in the absence of power and open when current is applied to the coil. Electromagnetic solenoid valves CEME are installed on pipelines and open or block the flow of the working medium when supply voltage is applied to the valve coil.
The following can be used as a control sensor that sends a signal to open or close the power circuit of the CEME valve coil:
- pressure switch;
- float switch;
- various types of level control devices;
- flow switch;
- thermostat and similar devices.
On the pipeline, solenoid valves are installed in any position (the movement of the working medium must coincide with the arrow indicated on the body). The most preferred installation option is with the coil facing up. Foreign particles must not enter the valves, nor should it be used for other purposes.
Overall and connection dimensions
Rp | D,mm | vendor code | Pmin, bar | Рmax, bar | Kv, m 3 / h | Dimensions, mm | Weight, kg | |||
---|---|---|---|---|---|---|---|---|---|---|
A | IN | WITH | D | |||||||
3/8" | 10 | 8613 | 0,3 | 10 | 1,86 | 61 | 89 | 48 | 77 | 0,54 |
1/2" | 15 | 8614 | 0,3 | 10 | 2,1 | 61 | 89 | 48 | 77 | 0,5 |
3/4" | 20 | 8615 | 0,3 | 10 | 5,7 | 87 | 101 | 69 | 84 | 0,8 |
1" | 25 | 8616 | 0,3 | 10 | 9,6 | 100 | 106 | 80 | 86 | 1,1 |
1"1/4 | 32 | 8617 | 0,3 | 10 | 22 | 131 | 122 | 112 | 95 | 2,5 |
1"1/2 | 39 | 8618 | 0,3 | 10 | 27 | 146 | 128 | 128 | 98 | 3 |
2" | 51 | 8619 | 0,3 | 10 | 35 | 174 | 145 | 146 | 108 | 4,6 |
2"1/2 | 65 | 8620 | 0,3 | 10 | 63 | 245 | 180 | 184 | 134 | 9,4 |
3" | 75 | 8621 | 0,3 | 10 | 83 | 250 | 190 | 184 | 139 | 11,23 |
In our online store in Moscow you can get acquainted with standard and specialized samples of CEME products used in fuel transportation systems, pipelines for drinking and technical quality water, steam, gas, and refrigerant supply lines. In Russia, the total number of positions for all series of CEME valves and pumps ranges into hundreds of units. In addition, the Italian company produces dozens of varieties of sensors, fuses, relays and other parts for pressure and non-pressure pipelines.
In Russia, and in particular in Moscow, almost all CEME products are certified according to the ISO 9001 standard, which imposes special requirements for the quality of assembly and product packaging. A special approach to the interests of customers is noticeable even at the selection stage construction materials for CEME products - Italian manufacturer uses bronze, stainless steel, heat-resistant and chemical-resistant seals.
Where to buy CEME in Moscow?
You can buy products from CEME in the online store MultiFlow.ru. We offer a wide selection of units and components for household appliances and industrial installations. In addition, you can buy spare parts for the entire CEME range from us. At the same time, we offer our clients prices tailored to all segments of consumers and organized delivery to order not only in Moscow and Russia, but also in neighboring countries (Kazakhstan, Belarus and other CU countries).
Solenoid valve SEME pilot action 2/2 way normally closed D25 G1 NBR~1x230V 50Hz art. 8556NN025S CEME
Art. 8556NN250SA57
Classification.
Provisions:
- 2- open – closed.
Operating principle:
Important parameters.
Characteristics:
Model: 8556NN020S D25 G1 NBR~1x230V 50Hz.
Type: normally closed.
Inlet/outlet pipes: 1”.
Flow characteristic KV:9.6 m3/h.
Weight:
Materials:
- Case: bronze.
Solenoid valve SEME pilot action 2/2 way normally closed D20 G3/4 NBR~1x230V 50Hz art. 8555NN020S CEME
Art. 8555NN200SA57
Solenoid Ceme valves(Italy) are used in water and heat supply networks, in various industries, in water treatment and air conditioning systems, in fountain installations.
Solenoid valves are installed on pipelines in almost any position (with the coil down - an undesirable option) and, depending on the design, (normally closed or normally open) they open or block the flow of the working medium when supply voltage is supplied to the valve coil.
A pressure switch, float switch, various types of level control devices, flow switch, thermostat and similar products can be used as a control sensor that sends a signal to open or close the power circuit of the valve coil.
Classification.
By the number of passages (channels connecting different circuits):
- 2 way – 2/: one input, one output.
- 3-way -3/: one inlet, one outlet and one air outlet, or three moves in various combinations.
Provisions:
- 2- open – closed.
- Adjustable position, some models.
Working conditions. This parameter indicates whether the valve is in the OPEN (with the passage of the working medium) or CLOSED (without passing the working medium) state most of the time.
- N.C. Normally Closed: The valve is closed when there is no supply voltage at the coil terminals.
- N.O. Normally open: On the contrary, under the conditions mentioned above, the valve is open.
Operating principle:
Depending on the value of the minimum cut-off pressure (equal to zero or greater than zero), valves are either direct-acting or servo-actuated.
- Direct action: the fluid passage is opened or closed by a sealing piece mounted directly on a plunger with an electromagnet controlled by a coil. The operating pressure directly depends on the hole diameter and the power of the coil; with minimal operating pressure equals zero.
- With servo drive: there are control and main holes, the electromagnetic device opens and closes only the control hole, so the maximum and minimum operating pressure does not depend on the power of the coil, but only on design features sealing device of the main hole (diaphragm, piston, etc.). For this type of valve, the main characteristic is the minimum operating pressure, which is always non-zero and greater than zero.
Important parameters.
Maximum Operating Pressure Differential (M.O.P.D.), the maximum pressure difference between the inlet and outlet of a valve at which the solenoid can safely operate. If the outlet pressure is unknown, the value of M.R.P.D. the inlet pressure is assumed.
The minimum operating differential pressure is the pressure required to open/close the valve and hold it in the open (closed) position.
Characteristics:
Model: 8555NN020S D20 G3/4 NBR~1x230V 50Hz.
Operating principle: with servo drive.
Number of moves: 2-way.
Type: normally closed.
Working medium: air, water, light oils.
Mounting position: any; the position in which the coil is at the bottom is not recommended.
Minimum operating pressure drop: 0.25 bar.
Maximum operating pressure difference (M.O.P.D.): 10 bar.
Temperature environment: 80°C; in devices direct current at temperatures above 40°C, performance characteristics(M.R.P.D.) may decrease.
Maximum operating temperature: 90°C
Inlet/outlet pipes: 3/4”.
Flow characteristic KV: 5.7 m3/h.
Coil supply voltage: ~1x230V 50Hz.
Weight:
Materials:
- Case: bronze.
- Seal: NBR, optional EPDM-FPM.
- Guide rod: stainless steel(has a metal seal with the valve body for high temperature operation).
- Internal details: stainless steel.
Solenoid valve SEME normally closed D15 G1/2 NBR~1x230V 50Hz pilot action 2/2 way art. 8554NN012S CEME
Art. 8554NN120SA57
Ceme solenoid valves (Italy) are used in water and heat supply networks, in various industries, in water treatment and air conditioning systems, in fountain installations.
Solenoid valves are installed on pipelines in almost any position (coil down - an undesirable option) and, depending on the design, (normally closed or normally open) they open or block the flow of the working medium when supply voltage is supplied to the valve coil.
A pressure switch, float switch, various types of level control devices, flow switch, thermostat and similar products can be used as a control sensor that sends a signal to open or close the power circuit of the valve coil.
Classification.
By the number of passages (channels connecting different circuits):
- 2 way – 2/: one input, one output.
- 3-way -3/: one inlet, one outlet and one air outlet, or three moves in various combinations.
Provisions:
- 2- open – closed.
- Adjustable position, some models.
Working conditions. This parameter indicates whether the valve is in the OPEN (with the passage of the working medium) or CLOSED (without passing the working medium) state most of the time.
- N.C. Normally Closed: The valve is closed when there is no supply voltage at the coil terminals.
- N.O. Normally open: On the contrary, under the conditions mentioned above, the valve is open.
Operating principle:
Depending on the value of the minimum cut-off pressure (equal to zero or greater than zero), valves are either direct-acting or servo-actuated.
- Direct acting: the fluid passage is opened or closed by a sealing part mounted directly on a plunger with an electromagnet controlled by a coil. The operating pressure directly depends on the hole diameter and the power of the coil; in this case, the minimum operating pressure is zero.
- With servo drive: there are control and main holes, the electromagnetic device opens and closes only the control hole, so the maximum and minimum operating pressures do not depend on the power of the coil, but only on the design features of the sealing device of the main hole (diaphragm, piston, etc.) . For this type of valve, the main characteristic is the minimum operating pressure, which is always non-zero and greater than zero.
Important parameters.
Maximum Operating Pressure Differential (M.O.P.D.), the maximum pressure difference between the inlet and outlet of a valve at which the solenoid can safely operate. If the outlet pressure is unknown, the value of M.R.P.D. the inlet pressure is assumed.
The minimum operating differential pressure is the pressure required to open/close the valve and hold it in the open (closed) position.
Characteristics:
Model: 8554NN012S 15 G1/2 NBR~1x230V 50Hz.
Operating principle: with servo drive.
Number of moves: 2-way.
Type: normally closed.
Working medium: air, water, light oils.
Mounting position: any; the position in which the coil is at the bottom is not recommended.
Minimum operating pressure drop: 0.25 bar.
Maximum operating pressure difference (M.O.P.D.): 10 bar.
Ambient temperature: 80°C; In DC applications at temperatures above 40°C, performance characteristics (M.R.P.D.) may be reduced.
Maximum operating temperature: 90°C
Inlet/outlet pipes: 1/2”.
Flow characteristic KV: 2.1 m3/h.
Coil supply voltage: ~1x230V 50Hz.
Weight: 0.400 kg
Materials:
- Case: bronze.
- Seal: NBR, optional EPDM-FPM.
- Guide rod: stainless steel (has a metal seal with the valve body for high temperature operation).
- Internal parts: stainless steel.
Solenoid valve D25 G1" NBR~1x230V 50Hz 2/2 way normally closed art. 8416NN025S C57 CEME
Art. 8416NN250SC57
Ceme solenoid valves (Italy) are used in water and heat supply networks, in various industries, in water treatment and air conditioning systems, in fountain installations.
Solenoid valves are installed on pipelines in almost any position (coil down - an undesirable option) and, depending on the design, (normally closed or normally open) they open or block the flow of the working medium when supply voltage is supplied to the valve coil.
A pressure switch, float switch, various types of level control devices, flow switch, thermostat and similar products can be used as a control sensor that sends a signal to open or close the power circuit of the valve coil.
Classification.
By the number of passages (channels connecting different circuits):
- 2 way – 2/: one input, one output.
- 3-way -3/: one inlet, one outlet and one air outlet, or three moves in various combinations.
Provisions:
- 2- open – closed.
- Adjustable position, some models.
Working conditions. This parameter indicates whether the valve is in the OPEN (with the passage of the working medium) or CLOSED (without passing the working medium) state most of the time.
- N.C. Normally Closed: The valve is closed when there is no supply voltage at the coil terminals.
- N.O. Normally open: On the contrary, under the conditions mentioned above, the valve is open.
Operating principle:
Depending on the value of the minimum cut-off pressure (equal to zero or greater than zero), valves are either direct-acting or servo-actuated.
- Direct acting: the fluid passage is opened or closed by a sealing part mounted directly on a plunger with an electromagnet controlled by a coil. The operating pressure directly depends on the hole diameter and the power of the coil; in this case, the minimum operating pressure is zero.
- With servo drive: there are control and main holes, the electromagnetic device opens and closes only the control hole, so the maximum and minimum operating pressures do not depend on the power of the coil, but only on the design features of the sealing device of the main hole (diaphragm, piston, etc.) . For this type of valve, the main characteristic is the minimum operating pressure, which is always non-zero and greater than zero.
Important parameters.
Maximum Operating Pressure Differential (M.O.P.D.), the maximum pressure difference between the inlet and outlet of a valve at which the solenoid can safely operate. If the outlet pressure is unknown, the value of M.R.P.D. the inlet pressure is assumed.
The minimum operating differential pressure is the pressure required to open/close the valve and hold it in the open (closed) position.
Characteristics:
Model: 8416NN025S C57 D25 G1 NBR~1x230V 50Hz
Operating principle: with servo drive.
Number of moves: 2-way.
Type: normally closed.
Working medium: air, water, light oils.
Ambient temperature: 80°C; In DC applications at temperatures above 40°C, performance characteristics (M.R.P.D.) may be reduced.
Maximum operating temperature: 90°C
Inlet/outlet pipes: 1”.
Flow characteristic KV: 7.50 m3/h.
Coil supply voltage: ~1x230V 50Hz.
Weight:
Materials:
- Case: bronze.
- Seal: NBR, optional EPDM-FPM.
- Guide rod: stainless steel (has a metal seal with the valve body for high temperature operation).
- Internal parts: stainless steel.
Solenoid valve D20 G3/4" NBR~1x230V 50Hz 2/2 way normally closed art. 8415NN020S C57 CEME
Art. 8415NN200SC57
Ceme solenoid valves (Italy) are used in water and heat supply networks, in various industries, in water treatment and air conditioning systems, in fountain installations.
Solenoid valves are installed on pipelines in almost any position (coil down - an undesirable option) and, depending on the design, (normally closed or normally open) they open or block the flow of the working medium when supply voltage is supplied to the valve coil.
A pressure switch, float switch, various types of level control devices, flow switch, thermostat and similar products can be used as a control sensor that sends a signal to open or close the power circuit of the valve coil.
Classification.
By the number of passages (channels connecting different circuits):
- 2 way – 2/: one input, one output.
- 3-way -3/: one inlet, one outlet and one air outlet, or three moves in various combinations.
Provisions:
- 2- open – closed.
- Adjustable position, some models.
Working conditions. This parameter indicates whether the valve is in the OPEN (with the passage of the working medium) or CLOSED (without passing the working medium) state most of the time.
- N.C. Normally Closed: The valve is closed when there is no supply voltage at the coil terminals.
- N.O. Normally open: On the contrary, under the conditions mentioned above, the valve is open.
Operating principle:
Depending on the value of the minimum cut-off pressure (equal to zero or greater than zero), valves are either direct-acting or servo-actuated.
- Direct acting: the fluid passage is opened or closed by a sealing part mounted directly on a plunger with an electromagnet controlled by a coil. The operating pressure directly depends on the hole diameter and the power of the coil; in this case, the minimum operating pressure is zero.
- With servo drive: there are control and main holes, the electromagnetic device opens and closes only the control hole, so the maximum and minimum operating pressures do not depend on the power of the coil, but only on the design features of the sealing device of the main hole (diaphragm, piston, etc.) . For this type of valve, the main characteristic is the minimum operating pressure, which is always non-zero and greater than zero.
Important parameters.
Maximum Operating Pressure Differential (M.O.P.D.), the maximum pressure difference between the inlet and outlet of a valve at which the solenoid can safely operate. If the outlet pressure is unknown, the value of M.R.P.D. the inlet pressure is assumed.
The minimum operating differential pressure is the pressure required to open/close the valve and hold it in the open (closed) position.
Characteristics:
Model: CEME8415NN020S D20 G3/4 NBR~1x230V 50Hz.
Operating principle: with servo drive.
Number of moves: 2-way.
Type: normally closed.
Working medium: air, water, light oils.
Mounting position: It is recommended to mount the valve with coil in a vertical position. Models 8417, 8418, 8419 must be mounted in a horizontal position with the coil in a vertical position.
Minimum operating pressure drop: 0 bar.
Maximum operating pressure difference (M.O.P.D.): 4 bar.
Ambient temperature: 80°C; In DC applications at temperatures above 40°C, performance characteristics (M.R.P.D.) may be reduced.
Maximum operating temperature: 130°C
Inlet/outlet pipes: 3/4”.
Flow characteristic KV: 5.5 m3/h.
Coil supply voltage: ~1x230V 50Hz.
Weight:
Materials:
- Case: bronze.
- Seal: NBR, optional EPDM-FPM.
- Guide rod: stainless steel (has a metal seal with the valve body for high temperature operation).
- Internal parts: stainless steel.
We use solenoid valves to close or open the water. I never talked about these valves, because I thought that everything was already clear to everyone. But some time ago I was faced with the fact that this valve needed to be serviced and, taking this opportunity, I decided to make a short post about them.
What is the difference between a solenoid valve and a faucet with an electric drive and where is it better to install it? And in general, why are they needed? And they are needed in order to sharply (quickly) open or close the flow of water or other liquid. Some valves can only work with water, some can work with air and water. The fact that the valve works quickly is both good and bad. This is good where you need to dose something at low pressures: watering plants, an area, clean water after a filter. But it’s bad where the water flow speed is high and due to its sudden opening/closing, severe water hammer can occur.
That is, the place for such a valve is after the pressure reducers on the outgoing water lines. But there is no need to install it as the main inlet valve so that it shuts off all the water in the apartment when the leakage protection is activated. Because the valve is less reliable than a faucet with an electric drive and will also cause water hammer. An electric faucet will close slowly and will remove all sorts of debris and rust. But the same small weed can interfere with the operation of the valve, and this will be bad.
Just such a case happened to me and, using it, I decided to see what was inside the solenoid valve. It turned out to be very easy to disassemble and maintain.
The most popular and easily purchased valves among people are CEME valves. They are usually sold by the store http://forwater.ru/shop/125/180/, where everyone buys them. These valves can be normally closed (this means that until current is applied, the valve is closed) and normally open (when current is applied, the valve will close). We will be interested in normally closed valves, because we want our entire system not to consume electricity until we need to open the water, and when it fails, everything closes so that water does not flow anywhere in vain.
In early models of these valves, the solenoid coil was not designed to big time work. After about an hour of operation, if water did not flow through the valve and did not cool it, the coil would become very hot and I was afraid to forget to turn off the light in the toilet (we are talking about an apartment in Moscow, where I did this). Now (I bought the valve a year ago) this glitch has been corrected and the coil almost does not heat up at all. Most likely, the manufacturer increased the number of turns of wire in the coil to reduce the current. This guess is confirmed by the fact that the new coil is one and a half times larger in size than the old one. Once I went to the country and forgot to turn off the light in the toilet for two days. The valve did not die and did not even get hot!
Where do I use these valves:
- In a hygienic shower. Here the valve’s task is to block the weak flow of water to the shower head. This is what they do when hygienic shower assembled without a special mixer built into the wall, which is usually used to regulate the flow of water. Without a valve, the shower head will always be under water pressure, which is bad for it. And people came up with the idea of installing a valve parallel to the toilet lighting. Therefore, when we turn off the light in the toilet, the valve cuts off the pressure from the shower head.
- In the water supply to washing machine. In Moscow, it stands in the corner of the corridor, and previously water was supplied to it using a long flexible line. Since it was scary that someday this line would burst, the water was turned off to it with a tap. When I redid the plumbing, I replaced the liner with a pipe, and instead of a faucet I installed a valve. Next to the washing machine we have a very convenient unit: a socket and a switch. I wanted to do the laundry - I turned on the machine and immediately turned it off. I washed it and turned it off.
- In dosing clean water after the filter. This is my mega cheat! If you want, I’ll go to Moscow someday, take some photos and tell you about the automation of my bathroom. The idea is as follows: I’m tired of forgetting that the kettle fills slowly from under the flow-through water filter. Sometimes you go away to answer a couple of lines in ICQ - and the water is already on the countertop and on the floor.
So I installed such a valve at the filter outlet and made a time relay with two buttons. Press one - and just enough water is poured to fill the kettle (selected according to time). Press the second one at any moment and the water closes. Convenient as hell!
So one time I had a glitch with this system. The water suddenly stopped closing by itself and began to drip in, and then flow in a thin stream. I thought and thought and decided to disassemble the valve of this unit. First, I removed the assembly itself (valve, John Guest fitting - this is the name for fittings for thin tubes through which pure water flows, and the control valve) and unscrewed the coil from the valve.
And then he took the key and disassembled the valve. This valve operates on a difference in water pressure. I didn’t fully understand how it works, but I got the gist of it. A small, puny electromagnet drives a piston, which opens or closes small holes in the membrane.
If the hole is closed by a piston, then water passes through other holes and presses on the membrane from above, pressing it tightly and closing the path to exit. And if the piston is opened, then water flows to the valve outlet, its pressure is compared with the pressure under the membrane and there it does not prevent water from flowing to the valve outlet. That is, with the help of a small frail hole we control a lot of pressure.
The valve opens very easily - you only need to unscrew four screws. Under the top cover there is a small spring, which creates initial pressure on the membrane and the membrane itself.
In my case, the damage to the valve was a small fragment of a cheap filter cartridge. Its body split into several pieces, and a fragment traveled through a thin tube to the valve and prevented the membrane from tightly closing the valve outlet:
I was afraid that the membrane had burst, that the valve had already broken and that they would have to be replaced. In fact, these valves are good (if used correctly) and after I washed the membrane and cleaned it, everything worked and continues to work. I have had these valves in service since the moment I started using my plumbing - since 2012.
Here's a little review. That is, there is no need to use these valves to shut off large volumes of water entering the apartment; they can be used to control water flows at end points according to the “open-close” scheme.