VVGNG cable marking. Wire and cable VVGNG LS technical characteristics, description, purpose Fire resistance test

Cable VVG(a), aka power wire VVG(a), also known as cable VVGng a, is a flame retardant wire that is used for the transmission and distribution of electricity, which occurs in stationary installations that have an electric current frequency of 50 Hz and a rated voltage of up to 660 or 1000 V. It is extremely widely used - it is used in any climatic conditions, at high altitudes, in water - virtually anywhere, unless, of course, it is damaged. This subtype is especially often used in places where there is an increased risk of a fire - for example, in enterprises working with flammable or explosive components.

Decoding of VVG(a) cable

The marking allows us to understand in more detail what this cable is. Here is its decoding: “VVG” means “vinyl-vinyl-naked,” which refers to the presence of two layers of polyvinyl chloride, as well as the absence of a specialized protective layer. Well, “ng”, if used in marking, means that the cable, in the event of a fire hazard, will not spread combustion. The letter “a”, very often placed in brackets, means the category of non-propagation of combustion according to. In particular, this means that even when laid in bundles, these cables do not propagate combustion, while traditional VVGs can “boast” of this only when laid individually. This letter should not be confused with the “a” that is placed before the abbreviation and means that the cable is not copper. IN in this case it's definitely copper. Often ls, frls, frlsltx, frhf are added to the marking, but in essence this is one cable.

Technical characteristics of VVGng (a)

U VVGng A a number of parameters can vary. For example, this may be the form factor of the cores (which can be round, triangular or flat), their number (from 1 to, as a rule, 5), their sections (from 1.5 mm 2 to 50 mm 2, and sometimes even more), nominal diameter (directly dependent on cross-sections), weight (from several tens of kilograms to several tons per kilometer). Allowable current can vary from 21A to several hundred, depending on both the type of cable and its location. As you can see, variations of this product There are a great variety, so before you buy a cable, you need to study in detail the description of its specific brand; it is this description that will save you time and nerves in the future. The price, again, varies depending on the complexity and size of the cable. But in comparison with other types of VVG, the cost remains at approximately the same level. But any cost is very justified, because the cable will serve you under proper operation conditions for more than thirty years, five of which, as a rule, will be under warranty.

Most types of equipment, instruments, tools and machinery in production, trade and everyday life are connected to an electrical network that has an alternating voltage of up to 1 kV. This means that in these networks the distribution and supply of electricity is carried out via a safe cable. Today, one of the most popular products for food and lighting in open and internal view This is a VVG cable. There are options for its implementation.

Types and types of VVG cable

Any cable or conductor has a special marking, by which the characteristics of the product can be determined.

Novice electricians, who encounter abbreviations for the first time, often do not understand the difference between VVGng and VVG, and also from VVGng-LS. Let's figure it out:

  1. VVG is equipped with conventional PVC insulation, which does not have fire-retardant and self-extinguishing qualities.
  2. The insulating layer of VVGng contains halogen elements, thanks to which the combustion process is neutralized.
  3. Sheath of current-carrying conductors VVGng-ls when a fire occurs, no smoke or gas is released due to the use of halogen-free polyvinyl chloride (this is a big plus for VVGng-ls).
  4. VVGngfr-ls is a similar model, but fire resistant. If this type of cable catches fire, the emission of gas and smoke is low. If you use a group gasket, then there will be no spread of combustion.
  5. Halogen-free materials are used in the production of conductor VVGng-fr-ls, which distinguish this product from other brands. Halogen-free plastic material has high level insulation and produces the amount of smoke within normal limits. Fire safety is the main feature of the VVG ngfr-ls cable type.

What is VVG?

Often in various instructions For electrical installation work, it is suggested to use non-flammable conductor VVGng. In terms of quality/price ratio it is the best option. This VVGng conductor is actually very versatile, because it is practical to use in buildings made of flammable materials and in buildings that have high humidity.

What can the marking say? First, let's look at what conductor markings exist. If you know the decoding of the letters in the given cable markings, you can easily determine its properties. Below is a list of the main characteristics by which it is quite simple to separate all conductors.

1. Material used for the production of conductive core:

  • no designation, it's copper;
  • if the letter is A, it is aluminum.

2. Material from which the insulation is made for conductors:

  • if the letter is B, then polyvinyl chloride was used;
  • if the letters are Pv, then polyethylene was used;
  • if the letter is P, then polymer insulation was used.

3. Cable armor:

  • if the letter is B, then armored;
  • if the letter is G, then there is no armor, bare cable.

4. Shell (outer insulation):

  • if the letter is P, then the shell is made of polymer;
  • if the letters Шп, then there is a protective hose made of polyethylene;
  • if the letters are Shv, then the hose is protective;
  • if the letter is B, then the insulation is made of polyvinyl chloride.

5. Fire safety:

  • if there is a marking ng-frhf, then when the conductor is carried out in a group, it does not spread combustion, and during combustion and smoldering no corrosive substances are formed in the form of gas;
  • if there is a marking ngfr-ls, then when the conductor is carried out in a group, combustion does not spread, the formation of smoke and gas is reduced;
  • if there is a marking ng-hf, then when the conductor is carried out in groups, it does not spread combustion, and during combustion and smoldering no corrosive substances are formed in the form of gas;
  • if there is an ng-ls marking, then the gas and smoke emission is reduced; when the ng-ls conductor is carried out in a group, combustion does not spread;
  • if there is an NG marking, then when the conductor is carried out in a group, it will not spread fire;
  • If there is no marking, then when laying a single conductor, fire will not spread.

If you follow the above, you can decipher the abbreviation VVGng: the first letter B means that the insulation of the conductors was made of polyvinyl chloride, the second letter B indicates that the insulation of the outer shell was also made of polyvinyl chloride, the third letter G indicates that there is a special layer of protection, there is no armor.

In the professional language of electricians, the abbreviation VVG means approximately: the letter V is vinyl, the letter B is vinyl, the letter G is bare. And the letters ng indicate that if you use a group laying of this conductor, it will not support combustion. This important indicator for cases when it is necessary to lay conductor in places where there is a high probability of fire. After all, the main thing is safety. The marking does not contain the letter A, which means that the conductor has conductive conductors made of copper.

This conductor happens made in two modern modifications: with the ending ng-ls - this means that during combustion there is a reduced release of smoke and gas (this is what ng-ls is good for); with the ending ng-hf - this means that during the combustion of the cable there is no release of corrosive substances in the form of gas. These modifications have improvements - this is fr (in other words, fire resistance, which differs from ng-ls).

Often with the usual VVG you can find cables that have the letter “P” at the end of the marking. Judging by the technical data, they are no different, but the slight difference lies in the structure - it is flat. This means that decoding the cable VVG p sounds like this: the letter V is vinyl, the letter B is vinyl, the letter G is bare, the letter P is flat.

Cable routing options

Open VVG cable laying

If you follow technical parameters of this cable, its open installation is only permitted on surfaces and structures made of flame-resistant or non-flammable materials, for example plaster, concrete, brick, plastered surface, etc.

VVG cable laying open method allowed to be used under suspended structures such as cables, etc. These structures must provide sufficiently reliable installation. When laying the cable, any possibility of mechanical action on it should be excluded.

If there is a risk of damage mechanically cable product, the necessary additional protection should be installed. Additional protection should be used when laying cable products in an open manner on combustible wood surfaces. In this case, installation should be carried out using a cable channel, corrugated hose, metal hose, pipe and other types of protection.

Laying the VVG cable in a hidden way

This cable installation option remains the most popular for residential premises. The cable is laid under the plaster, in voids, in grooves, etc.

With this installation option, mechanical damage is practically eliminated, so the use of additional protection is not expected, with the exception of wall voids in wooden houses.

Hidden installation of cables in pipes or other non-flammable materials is allowed here. Available regulations that concern hidden electrical wiring. They define correct execution hidden way cable installation.

Laying VVG cable in the ground

It is known that It is not allowed to lay a cable of this brand underground without using special protection methods. All this is due to the fact that the protection that will save the cable from any mechanical influences, there is no.

Installation of VVG conductor underground is possible only in special sealed boxes and only along overpasses and cable structures.

Cables of the “NG” design, which do not propagate combustion when laid in a bundle with a standardized volume of flammable mass of cables in accordance with GOST 12176-89, section 3 (IEC 332-3-96), were developed in 1984-1986. Non-propagation of combustion, depending on the design of the cables, was ensured by using special protective thermal barriers or screens in cable structures, by limiting the volume of combustible materials, by using polymer and other materials with low specific heat of combustion and polymer compositions with high oxygen index values. At the same time, when burning, cables of the “NG” design emit a large number of


smoke containing corrosive and toxic products. In this regard, a set of works was carried out to create polyvinyl chloride compositions with reduced fire hazard , on the basis of which a new series of flame retardant cables with low smoke and gas emissions “NG-LS” was developed and mastered. Index"LS" (low smoke)


- compliance with the requirements for smoke generation during combustion of IEC 61034, parts 1 and 2. Distinctive feature cables of the “NG-LS” design is that their insulation, filling and sheath are made of special polymer compositions of reduced fire danger created on the basis of polyvinyl chloride. Cables of the "NG-LS" design differ from cables with the "NG" index in that, in addition to flame retardation, they are characterized by reduced hydrogen chloride emission and low smoke generating ability during combustion and smoldering. Therefore, the use of cables with the index “NG” in subways Western Europe


To solve problems associated with the release of HCl and smoke, a class of cable materials was created that do not contain halogens, that is, do not emit corrosive gases and have significantly higher low level smoke emissions - so-called compositions. Cables using these materials are designated with the index “NG-LS HF”. Index “HF” (halogen free) - compliance with the requirements for the corrosive activity of smoke and gas emission products during combustion GOST R IEC 60754, part 2.


Polymer shell METALANGA corresponds to index "NG-LS HF" normal fire safety.

The combination of a polymer shell with a metal hose ensures fire safety in the most unfavorable conditions. Cable VVG ng ls - this is a subtype of VVG cable, just like its “bigger” brother, intended for transmission and distribution electric current

in conditions where, at a frequency of up to 50 Hz, a rated voltage of 0.66, 1 or 6 kV is used in certain stationary installations. However, there are differences. In particular, this cable is most suitable for use in areas where the risk of fire is particularly high. Its marking tells us this.

Decoding of the VVG ng ls cable

Its decoding is straightforward and, in fact, contains a description of the key technical characteristics of the product. “VVG” stands for “vinyl-vinyl-naked,” which indicates that two layers of polyvinyl chloride are used and then there is no protective layer. The letters “ng” indicate that the cable is flame retardant. Well, “ls” means “Low Smoke”, that is, in Russian, low smoke level. The absence of the letter “A” means that the cable in question is copper. By the way, don’t be surprised if you come across the less familiar abbreviation frls - it’s the same thing. Simply “fr” means “Fire Resistance”, that is, resistant to fire, and this is essentially the same as “ng”. Due to its properties, the use of VVG ng ls is becoming available in more places, especially in relatively hazardous industries.

Fire resistance test. Comparison with NUM cable
Flammability testing of cables with and without the “NG” index.
1. plot: We burn the cable NUM and VVGng-LS under equal conditions;

At its core, this cable is not much different from - however, there are two differences. For example, round cables (and the core form factor can be round, flat or triangular) use halogen-free filler, as well as unvulcanized rubber, which has a very good degree of fire safety. Also, a special insulation coating is used for the cable sheath, which has anti-flammability properties, unlike.

Otherwise, the number of cores can vary from one to six, their cross-sections can reach 240 mm 2, the diameter also changes in proportion to the cross-sectional area, the permissible current, depending on the type and number of wires, can vary from 21A to 704A, and the weight varies from approximately 40 kg/km to several tons for the same one kilometer. If you decide to buy such a cable, carefully read its description in the store - after all, you may come across a product that does not have the characteristics that you need. The price varies greatly depending on the characteristics, and the cost can increase hundreds of times if the number of cores and their total area. The traditional service life of such a product is more than thirty years, of which five are usually under warranty.

Temperature range when using VVGng: from -30°С to +50°С

Relative humidity should be up to 98% at +35 degrees Celsius.

Minimum bending radius when laying

  • single-core cables - 10 outer diameters,
  • multi-core cables - 7.5 outer diameters.

Long-term permissible heating temperature of cable cores during operation: +70°C

Limit temperature of current-carrying conductors of cables under the condition of non-ignition of the cable during short-circuit: + 400°C

Number of cores, cross-section, mm2 VVGng-LS Number of cores, cross-section, mm2 VVGng-LS
diameter, mm weight, kg diameter, mm weight, kg
0.66 kV 1 kV 0.66 kV 1 kV 0.66 kV 1 kV 0.66 kV 1 kV
1x1.55.9 6.3 43 48
1x2.56.2 6.6 54 60 3x2.5+1x1.510.0 11.0 190 215
1x46.9 7.5 75 86 3x4+1x2.511.8 12.8 262 302
1x67.4 8.0 98 109 3x6+1x412.9 14.4 359 409
1x107.7 8.0 149 155 3x10+1x615.3 16.3 539 579
1x169.3 9.7 221 227 3x16+1x1018.7 19.2 826 858
1x2510.8 11.0 322 327 3x25+1x1622.7 23.2 1376 1408
1x3511.8 12.0 415 421 3x35+1x1622.6 23.1 1692 1723
1x5013.3 13.5 556 563 3x50+1x2524.7 25.1 2252 2288
1x7015.8 806 3x70+1x3528.1 28.5 2708
1x9517.8 1083 3x95+1x50 30.8 3621
1x12019.5 1370 3x120+1x70 34.8 4576
1x15021.4 1658 3x150+1x70 37.9 5423
1x18523.80 2020 3x185+1x95 41.8 6835
1x24026.60 2665 3x240+1x120 45.9 8787
2x1.57.6 8.4 93 113 4x1.5 52.0 147 169
2x2.58.2 9.7 124 156 4x2.59.3 10.0 196 220
2x410.2 11.4 189 223 4x410.2 11.1 284 327
2x611.3 12.4 245 282 4x611.8 13.1 377 424
2x1013.6 14.0 383 398 4x1013.0 14.4 592 610
2x1616.1 16.5 538 553 4x1615.9 16.5 887 910
2x2519.4 19.8 905 928 4x2519.5 20.0 1431 1472
2x3521.2 21.6 1180 1205 4x3522.7 23.2 1878 1912
2x5025.0 25.4 1569 1600 4x5025.5 25.9 2493 2528
2x7024.3 1694 4x7029.1 29.5 3056
2x95 27.0 2220 4x95 31.2 4102
2x120 29.3 2723 4x120 35.5 5081
2x150 31.8 3336 4x150 38.9 6183
2x185 35.0 4015 4x185 42.6 7701
2x240 39.0 5190 4x240 46.7 10069
3x1.58.0 9.4 114 143 5x1.5 52.7 180 202
3x2.59.3 10.2 164 182 5x2.511.9 12.0 235 263
3x410.8 12.0 233 270 5x412.8 14.4 344 394
3x611.8 13.1 310 350 5x614.1 15.7 463 519
3x1014.4 14.9 480 496 5x1017.4 17.9 720 756
3x1616.5 17.4 681 721 5x1620.9 21.4 1078 1103
3x2520.4 20.9 1167 1193 5x2525.3 25.8 1695 1735
3x3522.6 23.1 1519 1548 5x3527.9 28.4 2153 2204
3x5026.4 26.8 1991 2046 5x5032.2 32.7 2900 2962
3x70 28.3 2354 5x70 36.5 3858
3x95 31.6 3131 5x95 39.3 5101
3x120 34.6 3864 5x120 43.9 6304
3x150 38.0 4774 5x150 47.7 7815
3x185 41.5 5850 5x185 53.3 9569
3x240 47.0 7596 5x240 59.0 12406

Power cables with plastic insulation, flame retardant, low smoke and gas emissions for voltages up to 1 kV (ng-LS) TU 16.K71-310-2001

Application area
For transmission and distribution electrical energy in stationary installations at alternating voltages of 0.66 and 1 kV and constant voltages up to 1 kV. Cables are manufactured for general industrial use and nuclear power plants for supply to the domestic market and for export. For use in NPP systems of classes 2, 3 and 4 according to classification OPB-88/97 (PNAEG-01-011-97). Climatic version of cable UHL-T, placement category 5 according to GOST 15150-69.
The cables are recommended for use in the construction of residential buildings, public buildings, facilities nuclear energy, metro. The cables correspond to the best foreign analogues.

Rated voltage

from -50°С to +50°С

Maximum permissible heating temperature of cable cores in emergency mode
(or overload mode)

7.5 dia. cable

Service life not less

Fire resistance of cables

at least 90 minutes

Cables are made 1, 2, 3, 4, 5-core (A)

(A) VVGng-LS

  1. Copper or aluminum, single-wire or multi-wire, round or sector compacted conductor
  2. Extruded PVC insulation with reduced fire hazard
  3. Outer sheath made of PVC plastic compound of reduced fire hazard

(A) VBBShvng-LS

  1. Cores - single-wire or multi-wire copper (VBBShvng-LS) or aluminum (AVBbShvng-LS) conductor
  2. Insulation - PVC plastic compound of reduced fire hazard
  3. Inner sheath made of PVC with reduced fire hazard
  4. Armor made of two galvanized steel strips
  5. Outer shell - PVC plastic compound of reduced fire hazard
Brand Design terms of Use
VVGng5LS
AVVGng5LS
Veins– single-wire or multi-wire copper (VVGngQLS) or aluminum (AVVGngQLS) conductor;
Insulation
Outer shell

Installed in fire hazardous areas provided there is no danger
mechanical damage.

VVG5Png5LS
AVVG5Png5LS
Veins– single-wire copper (VVGQPngQLS) or aluminum (AVVGQPngQLS) conductor;
Insulation– PVC plastic compound of reduced fire hazard. Insulated cores are laid parallel in one plane;
Outer shell– PVC plastic compound of reduced fire hazard.
VBBShvng5LS
AVBBShvng5LS
Veins– single-wire or multi-wire copper (VBBShvngQLS) or aluminum (AVBbShvngQLS) conductor;
Insulation– PVC plastic compound of reduced fire hazard;
Inner shell made of PVC of reduced fire hazard;
Armor made of two galvanized steel strips;
Outer shell– PVC plastic compound of reduced fire hazard.
They are laid in cable structures and premises, including in fire hazardous areas in the absence of tensile forces during operation.

Outside diameter, mm

Estimated weight, kg/km

WITH ALUMINUM CONDUCTORS


AVBbShvng LS-0.66

OKP code 35 2222

Number and nominal cross-section of cores, mm 2

Outer diameter, mm

Estimated weight, kg/km


AVVG-Png LS-0.66

OKP code 35 2222 4600

Number and nominal cross-section of cores, mm 2

Outer diameter, mm

Estimated weight, kg/km

Power cable with insulation and sheath made of polyvinyl chloride compositions of reduced fire hazard
AVVGng LS-0.66

OKP code 35 2222

3 x 4+1 x 2.5 (solid)

3 x 6+1 x 2.5 (solid)

3 x 6+1 x 4 (olzh)

3 x 10+1 x 4 (olzh)

3 x 10+1 x 6 (olzh)

3 x 16+1 x 6 (olzh)

3 x 16+1 x 10 (ozh)

3 x 25+1 x 10 (ozh)

Number and nominal cross-section of cores, mm 2

Outer diameter, mm

Estimated weight, kg/km

AVBbShv ng-LSH
OKP code 35 3771

3 x 6+1 x 4 (olzh)

3 x 10+1 x 6 (olzh)

3 x 16+1 x 10 (ozh)

3 x 25+1 x 16 (olzh)

3 x 35+1 x 16 (olzh)

3 x 25+1 x 16 (olzh)

3 x 35+1 x 16 (olzh)

3 x 50+1 x 25 (olzh)

3 x 120 (cold)*

3 x 120+1 x 35

3 x 150+1 x 50

3 x 185+1 x 50

Number and nominal cross-section of cores, mm 2

Outer diameter, mm

Estimated weight, kg/km

Power cable with insulation and sheath made of polyvinyl chloride compositions
AVVG-Png-LSH

OKP code 35 3771 7200

Number and nominal cross-section of cores, mm 2

Outer diameter, mm

Estimated weight, kg/km


AVVGng-LSH

OKP code 35 3771

3 x 4+1x2.5 (cool)

3 x 6+1x2.5 (cool)

3 x 6+1 x 4 (olzh)

3 x 10+1 x 4 (olzh)

3 x 10+1 x 6 (olzh)

3 x 16+1 x 6 (olzh)

3 x 16+1 x 10 (ozh)

3 x 25+1 x 10 (ozh)

3 x 25+1 x 16 (olzh)

3 x 35+1 x 16 (olzh)

3 x 120+1 x 70

3 x 150+1 x 70

3 x 185+1 x 95

3 x 240+1 x 120

* With round cores.

Number and nominal cross-section of cores, mm 2

Outer diameter, mm

Estimated weight, kg/km

WITH COPPER CONDUCTORS

Power cable with insulation and sheath made of polyvinyl chloride compositions of reduced fire hazard with a protective cover type BbShv with a PVC hose of reduced fire hazard
VBBShvng-LS-0.66

OKP code 35 2122

Number and nominal cross-section of cores, mm 2

Outer diameter, mm

Estimated weight, kg/km

Power cable with insulation and sheath made of polyvinyl chloride compositions of reduced fire hazard in a flat design
VVG-Png-LS-0.66

Number and nominal cross-section of cores, mm 2

Outer diameter, mm

Estimated weight, kg/km

Power cable with insulation and sheath made of polyvinyl chloride compositions of reduced fire hazard
VVGng-LS-0.66

OKP code 35 2122

3 x 1.5+1 x 1 (solid)

3 x 1.5+1 x 1.5 (solid)

3 x 2.5+1 x 1.5 (solid)

3 x 4+1 x 2.5 (solid)

3 x 6+1 x 2.5 (solid)

3 x 6+1 x 4 (olzh)

3 x 10+1 x 4 (olzh)

3 x 10+1 x 6 (olzh)

3 x 16+1 x 6 (olzh)

3 x 16+1 x 10 (ozh)

3 x 25+1 x 10 (ozh)

3 x 25+1 x 16 (olzh)

3 x 35+1 x 16 (olzh)

Number and nominal cross-section of cores, mm 2

Outer diameter, mm

Estimated weight, kg/km

Power cable with insulation and sheath made of polyvinyl chloride compositions of reduced fire hazard with a protective cover type BbShv with a PVC hose of reduced fire hazard
VBBShv ng-LSH

OKP code 35 3371

Number and nominal cross-section of cores, mm 2

Outer diameter, mm

Estimated weight, kg/km

Power cable with insulation and sheath made of polyvinyl chloride compositions of reduced fire hazard in a flat design
VVG-Png-LSH

OKP code 35 3371 3500

Number and nominal cross-section of cores, mm 2

Outer diameter, mm

Estimated weight, kg/km

Power cable with insulation and sheath made of polyvinyl chloride compositions of reduced fire hazard
VVGng-LS-1

OKP code 35 3371

3 x 1.5+1 x 1 (solid)

3 x 1.5+1 x 1.5 (solid)

3 x 2.5+1 x 1.5 (solid)

3 x 4+1 x 2.5 (solid)

3 x 6+1 x 2.5 (solid)

3 x 6+1 x 4 (olzh)

3 x 10+1 x 4 (olzh)

3 x 10+1 x 6 (olzh)

3 x 16+1 x 6 (olzh)

3 x 16+1 x 10 (ozh)

3 x 16+1 x 6 (olzh)

3 x 25+1 x 10 (ozh)

3 x 25+1 x 16 (olzh)

3 x 35+1 x 16 (olzh)

3 x 50+1 x 16*

3 x 120+1 x 35

3 x 120+1 x 70

3 x 150+1 x 50

3 x 150+1 x 70

3 x 185+1 x 50

3 x 185+1 x 95

3 x 240+1 x 70

3 x 240+1 x 120

Power cables, with PVC insulation, flame retardant, with low smoke and gas emission for voltage 6 kV TU 16.K10-016-2003

Application area
For transmission and distribution of electrical energy in stationary installations at alternating voltage up to 6 kV. Cables are manufactured for general industrial use and nuclear power plants for supply to the domestic market and for export. For use in NPP systems of classes 2,3 and 4 according to classification OPB-88/97 (PNAEG-01-011-97). Type of climatic version of the cable - B, placement category 5 according to GOST 15150-69.
terms of Use
VVGng-LS, AVVGng-LS, for installation in fire hazardous areas, provided there is no danger of mechanical damage. VBVng-LS, AVBVng-LS - for installation in cable structures and premises, incl. in fire hazardous areas in the absence of tensile forces during operation.

Main technical and operational characteristics

Rated voltage

Temperature environment during cable operation

from -30°С to +50°С

Relative air humidity (at temperatures up to +35°C)

Minimum cable laying temperature without preheating

Limit long-term permissible operating temperature of the cores

Maximum permissible heating temperature of cable cores in emergency mode (or overload mode)

Maximum temperature of the cores under the conditions of non-ignition of the cable during a short circuit

Life time

Warranty life of the cable

Number and nominal cross-section of cores, mm 2

Estimated weight, kg/km

Power cable with insulation and sheath made of polyvinyl chloride plastic compound of reduced fire hazard, armored
AVBVng-LS-6, VBVng-LS-6

OKP code 353773, 353373

Number and nominal cross-section of cores, mm 2

Cable outer diameter (geometric dimensions), mm

Estimated weight, kg/km

Power cable with insulation and sheath made of polyvinyl chloride plastic compound of reduced fire hazard
AVVGng-LS-6, VVGng-LS-6

OKP code 353773, 353373

Power cable with flame retardant polyvinyl chloride insulation for alternating voltage up to 0.66 kV with a frequency of 50 Hz NYMng-LS TU 3521-039-05755714-2007

Application area
The cable is intended for the transmission and distribution of electrical energy in stationary installations for alternating voltage up to 0.66 kV with a frequency of 50 Hz. Climatic version of the cable is UHL, T, placement categories 1-5 according to GOST 15150-69. Fire safety class according to NBP 248-97- PRGP1.
terms of Use
The cable is intended for installation of electrical wiring and cable lines in industrial, residential and public buildings and structures, as well as in cable structures to ensure safe operation electrical equipment of protection class 1 electrical safety along with cables of the VVGng type. The cable can be used for laying power and lighting networks in explosive zones of classes V-1b, V-1g, V-IIa, as well as for lighting networks in explosive zones of class B-Ia.

Main technical and operational characteristics

Rated voltage

Ambient temperature during cable operation

from -30°С to +50°С

Relative air humidity (at temperatures up to +35°C)

Minimum cable laying temperature without preheating

Limit long-term permissible operating temperature of the cores

Minimum permissible bending radius when laying

4 dia. cable

Life time

Warranty life of the cable

Number and nominal cross-section of cores, mm 2

Outer diameter, mm

Estimated weight, kg/km

NYMng-LS
OKP code 352122

Core colors

Number of cores

NYMng-LS-J
with grounding conductor

NYMng-LS-O
with zero core

Blue, brown

Green-yellow, blue, brown

Blue, black, brown

Green-yellow, blue, black, brown

Blue, black, brown, black or brown

Green-yellow, blue, black,
brown, black or brown

Blue, black, brown, black or brown, black or brown

Information provided by Sevkabel-Holding OJSC specifically for the site

If you have not found information on the products you are interested in, contact the forum and you will certainly receive an answer to your question. Or use the form to contact the portal administration.

For reference: The “Directory” section on the website is intended for informational purposes only. The directory was compiled by sampling data from open sources, as well as thanks to information coming from manufacturers cable products. The section is constantly updated with new data and improved for ease of use.

List of used literature:

Electrical cables, wires and cords.
Directory. 5th edition, revised and expanded. Authors: N.I. Belorussov, A.E. Sahakyan, A.I. Yakovleva. Edited by N.I. Belorussov.
(M.: Energoatomizdat, 1987, 1988)

“Optical cables. Manufacturing plants. General information. Structures, equipment, technical documentation, certificates"
Authors: Larin Yuri Timofeevich, Ilyin Anatoly Aleksandrovich, Nesterko Victoria Aleksandrovna
Year of publication 2007. Publishing house "Prestige" LLC.

Directory "Cables, wires and cords".
Publishing house VNIIKP in seven volumes, 2002.

Cables, wires and materials for the cable industry: Technical reference book.
Comp. and editing: Kuzenev V.Yu., Krekhova O.V.
M.: Publishing house "Oil and Gas", 1999

Cable products. Directory

Installation and repair of cable lines. Electrician's Handbook
Edited by A.D. Smirnova, B.A. Sokolova, A.N. Trifonova
2nd edition, revised and expanded, Moscow, Energoatomizdat, 1990