How to calculate boiler efficiency - an overview of heat loss factors. Heat balance and boiler efficiency
Reading time: 4 min
A properly selected heating system will not only bring warmth and comfort to every home, but will also eliminate unpleasant consequences and extra costs for repairs. A hot water boiler is the basis of the heating system of a house.
Before choosing and purchasing, it is worth making a correct calculation of the efficiency of the boiler and clarifying all its parameters and factors that will affect its operation and the amount of heat generated.
What is boiler efficiency
The efficiency of steam and hot water boilers is determined by the efficiency factor - their thermal efficiency. That is, this is the volume of heat generated to produce the nominal volume hot water in relation to the nominal volume of fuel burned.
Manufacturers indicate the initial capabilities of the equipment, where the efficiency of a water heating boiler can reach 110%, but more often their value adheres to the parameters of 95-98%. During further operation, the consumer can increase these indicators with the help of technical upgrades and thermal insulation.
Independent calculation of the boiler efficiency is carried out at the installation site and depends on many factors, including a well-built smoke removal system, eliminating defects during installation, etc. All resources expended for the operation of the coolant (fuel, electricity) are compared with the volume of heat generated by it.
How to calculate efficiency
Gross efficiency The boiler is characterized by the degree of technical equipment, net efficiency is the efficiency of fuel consumption.
To identify boiler efficiency indicators, the formula is used:
Boiler efficiency = (Q1/ Q_total)x100%, where Q1 is the accumulated heat used for heating, and Q_total is the total amount of thermal energy released during fuel combustion.
The calculations do not cover many points, so their results are averaged. Any failures or deviations in the operation of equipment or external factors, affecting heat loss, will distort the result obtained from this formula.
To eliminate a larger number of distorting factors, the result is corrected to clarify the thermal efficiency. Depending on the characteristics of a particular heating system.
Boiler efficiency=100-(Q2+Q3+Q4+Q5+Q6)
Where Q2 is heat loss in the form of smoke released through the ventilation system,
Q3 – insufficient combustion of the gas mixture with incorrectly used volumes of the gas-air mixture,
Q4 – thermal heat loss due to contamination of the heat exchanger, as well as if the gas burners are dirty,
Q5 – heat loss due to external cold air (affects the performance of the boiler installation),
Q 6 – heat loss during cleaning of the combustion chamber.
The main factor influencing body efficiency is the exhaust waste combustion products; by reducing their heating within 10-12°C, the overall efficiency of a gas heating boiler can be increased by several percent.
For the same reason, condensing boilers have the highest efficiency index, i.e. the lower the temperature of the heating equipment, the higher this value. The most low rate It has minimal functionality and a simple design.
The two options used in determining the efficiency of gas heating boilers are: reporting over a specific period of time and during initial installation tests. In the latter version, the calculation result will be more accurate, thanks to the clarity in calculating heat loss.
How to increase the efficiency of a gas boiler
Create suitable conditions To increase efficiency, you can optimize processes yourself or with the involvement of a specialist. Initially, all parameters are included in the design of the electric boiler; the effectiveness of measures taken to increase the efficiency of the equipment will depend on these data.
To begin with, modernization is carried out without changing the structure of solid fuel boilers:
- Room thermostats. They control the temperature in living spaces without affecting the operation of the coolant.
- Installing a circular pump, this way you can stabilize the uniformity and speed of heating.
- Replacing a gas burner will increase the efficiency of a solid fuel boiler by 5-7%. The modulation burner will allow you to consume the gas-air mixture in correct proportions, which will eliminate incomplete combustion.
- The location of the burners near the water circuit will add several percent to the total efficiency. Such a partial modification will have a positive effect on fuel consumption and increase the thermal balance of the entire system.
Carrying out regular maintenance and cleaning of equipment will increase its efficiency. Scale in the pipes of the heating system and soot on the outer walls of the chimney, formed during operation, can take up to 5%. Plastic pipes require less maintenance, but they must be purged periodically.
A clogged chimney narrows the passage of the smoke exhaust pipe, this leads to a decrease in draft, and this is not only a loss of heat, but also a threat to the health of people in residential premises.
Also, a heat exchanger with visible signs of contamination, which are salt deposits of metals, provokes a high consumption of all types of energy spent on work, which reduces thermal conductivity and can damage the boiler. Cleaning the combustion chamber is mandatory and is carried out several times a year.
As an option to reduce chemical heat losses, a highly qualified equipment system is configured for this. It's better to refrain from self-configuration and entrust the matter to a specialist.
The fight against underburning is solved by increasing the rate at which liquefied gas enters the burner, so the combustion process occurs more actively, and the efficiency, accordingly, increases.
Although an increase in efficiency has practically no effect on the thermal efficiency of the boiler unit. Today natural gas remains the most economical, equipment using this fuel is more common and economically justified than boilers using traditional solid wood fuel or coal.
Gas boilers with the highest efficiency
The best quality boilers, which also have high efficiency rates, are of foreign origin. Energy-saving technologies that meet EU requirements are decisive in the production of such equipment.
Provides high performance modern instruments modernization, for example, like modulating burner.
Automatic and economical, it has a wide range that allows you to adapt to the individual parameters of a particular boiler and heating system. Its combustion is carried out in a constant mode.
Also, the main advantage is their maximum heat transfer. The most optimal value for heating the coolant, presented by a foreign manufacturer, is up to 70°C. Combustion products heat up to no more than 110°C.
They make a heat exchanger for boilers with the highest efficiency indicators from of stainless steel. Additionally, they are equipped with a block for extracting heat from condensate. Disadvantages that are typical at low temperature heating: the traction force develops with insufficient force and the formation of excessive condensation.
The supply of already heated gas and gas-air mixture to the burner, as well as air entering the chamber through a double-cavity pipe into the firebox, ensures a reduction in the total heat input for closed-type boilers by 1-2%.
Good option modernization of the boiler unit consists of installing exhaust gas recirculation. With this option, combustion products enter the burner device after passing through a chimney channel with strong kinks, while being enriched with oxygen from the external environment. Maximum efficiency is achieved at a temperature at which condensation forms (dew point).
Condensing boilers, operating under heating conditions at low temperatures characterized by relatively low gas consumption. This determines their thermal efficiency, especially when connected to gas cylinder units. This also makes such a boiler economical.
List of condensing boilers from well-known and distinguished European manufacturers with best quality assembly and high level Efficiency:
- Baxi.
- Buderus.
- De Dietrich.
- Vaillant.
- Viessmann.
As stated by their manufacturers in the accompanying documentation, the efficiency of these boiler units, when connected to low-temperature systems, corresponds to 107-110%.
Heating equipment that runs on solid fuel is represented today by a whole group of devices. Every solid fuel boiler produced today by domestic and foreign manufacturing companies is a completely new, high-tech heating device. Thanks to the introduction of technical innovations and automatic control devices into the design of heating devices, it was possible to significantly increase efficiency and optimize the operation of solid fuel boilers.
Heating devices of this type use a traditional principle of operation, similar to the variant that is well known to us stove heating. The main action is due to the process of generating thermal energy released during the combustion of coal, coke, firewood and other fuel resources in the boiler furnace, followed by heat transfer to the coolant.
Like other devices that provide energy generation, transmission, boiler equipment has its own efficiency factor. Let us consider in more detail what the efficiency of units operating on solid fuel is. We will try to find answers to questions related to these parameters.
What is the efficiency of heating devices
For any heating unit whose task is to heat the interior space of residential buildings and structures for various purposes, operating efficiency was, is and remains an important component. The parameter that determines the efficiency of solid fuel boilers is the efficiency factor. Efficiency shows the ratio of the expended thermal energy produced by the boiler during the combustion process solid fuel to useful heat, which is supplied to the entire heating system.
This ratio is expressed as a percentage. The better the boiler works, the higher the interest. Among modern solid fuel boilers there are models with high efficiency, high-tech, efficient and economical units.
For reference: As a rough example, one should evaluate the thermal effect obtained by sitting near a fire. Emitted when burning wood thermal energy capable of heating limited space and objects around the fire. Most of the heat from a burning fire (up to 50-60%) goes into the atmosphere, providing no benefit other than aesthetic content, while neighboring objects and air receive a limited amount of kilocalories. The efficiency of a fire is minimal.
The efficiency of heating equipment strongly depends on what type of fuel is used and what design features devices.
For example: when burning coal, wood or pellets, different amounts of thermal energy are released. Efficiency largely depends on the technology of fuel combustion in the combustion chamber and the type of heating system. In other words, each type of heating device (traditional solid fuel boilers, units long burning, pellet boilers and devices operating by pyrolysis), has its own technological design features that affect the efficiency parameters.
Operating conditions and quality of ventilation also affect the efficiency of boilers. Poor ventilation causes a lack of air necessary for the high intensity of the combustion process of the fuel mass. Not only the level of comfort during interior spaces, but also the efficiency of heating equipment, the performance of the entire heating system.
The accompanying documentation for the heating boiler must contain the equipment efficiency declared by the manufacturer. Compliance of real indicators with the declared information is achieved through correct installation device, strapping and subsequent operation.
Operating rules for boiler devices, compliance with which affects the efficiency value
Any kind heating unit has its own parameters for the optimal load, which should be as useful as possible from a technological and economic point of view. The operation process of solid fuel boilers is designed in such a way that most of the time the equipment operates in optimal mode. This operation can be ensured by following the rules of operation of heating equipment operating on solid fuel. IN in this case You must adhere to and follow the following points:
- it is necessary to observe acceptable modes of blowing and exhaust operation;
- constant control over the intensity of combustion and completeness of fuel combustion;
- control the amount of entrainment and failure;
- assessment of the condition of surfaces heated during fuel combustion;
- regular boiler cleaning.
The listed points are the necessary minimum which must be adhered to during operation of boiler equipment in heating season. Compliance with simple and clear rules will allow you to obtain the efficiency of an autonomous boiler declared in the characteristics.
We can say that every little thing, every element of the design of a heating device affects the value of the efficiency factor. A properly designed chimney and ventilation system ensure optimal air flow into the combustion chamber, which significantly affects the quality of combustion of the fuel product. Ventilation performance is assessed by the excess air coefficient. An excessive increase in the volume of incoming air leads to excessive fuel consumption. Heat leaves more intensely through the pipe along with combustion products. When the coefficient decreases, the operation of boilers deteriorates significantly, and there is a high probability of oxygen-limited zones appearing in the furnace. In this situation, soot begins to form and accumulate in large quantities in the firebox.
The intensity and quality of combustion in solid fuel boilers require constant monitoring. The combustion chamber must be loaded evenly, avoiding focal fires.
On a note: coal or firewood is evenly distributed over the grates or grate. Combustion should occur over the entire surface of the layer. Evenly distributed fuel dries quickly and burns over the entire surface, ensuring complete burnout of the solid components of the fuel mass to volatile combustion products. If you have correctly placed fuel in the firebox, the flame when the boilers are operating will be bright yellow, straw-colored.
During combustion, it is important to prevent failure of the fuel resource, otherwise you will have to face significant mechanical losses (underburning) of fuel. If you do not control the position of the fuel in the firebox, large fragments of coal or firewood falling into the ash box can lead to unauthorized combustion of the remaining fuel mass products.
Soot and resin accumulated on the surface of the heat exchanger reduce the degree of heating of the heat exchanger. As a result of all the listed violations of operating conditions, the useful volume of thermal energy required for normal operation heating systems. As a result, we can talk about a sharp decrease in the efficiency of heating boilers.
Factors on which boiler efficiency depends
Boilers with a high efficiency value today are represented by the following heating equipment:
- units running on coal and other solid fossil fuels;
- pellet boilers;
- pyrolysis type devices.
The efficiency of heating devices that fire anthracite, coal and peat briquettes is on average 70-80%. Pellet devices have a significantly higher efficiency – up to 85%. Loaded with pellets, heating boilers of this type are highly efficient, producing a huge amount of thermal energy during fuel combustion.
On a note: one load is enough to operate the device at optimal modes for up to 12-14 hours.
The absolute leader among solid fuel heating equipment is the pyrolysis boiler. These appliances use firewood or waste wood. The efficiency of such equipment today is 85% or more. The units also apply to high efficiency devices long burning, but subject to the necessary conditions - fuel moisture should not exceed 20%.
An important factor for the efficiency value is the type of material from which it is made. heating device. Today on the market there are models of solid fuel boilers made of steel and cast iron.
For reference: The first includes steel products. To reduce the market value of the unit, manufacturing companies use basic structural elements made of steel. For example, the heat exchanger is made of high-strength, heat-resistant black steel with a thickness of 2-5 mm. The heating tubular elements used to heat the main circuit are manufactured in the same way.
The thicker the steel used in the structure, the higher the heat transfer characteristics of the equipment. The efficiency increases accordingly.
In steel devices, an increase in efficiency is achieved through the installation of special internal partitions in the form of pipes - main flow stages and smoke dissipators. Measures are forced and partial, allowing to slightly increase the efficiency of the main device. Among the models of steel solid fuel boilers, you can rarely find devices with an efficiency above 75%. The service life of such products is 10-15 years.
In order to increase the efficiency of steel heating boilers, foreign companies use a bottom combustion process in their models, with 2 or 3 traction flows. The design of the products provides for the installation of tubular heating elements to improve heat transfer. Such equipment has an efficiency of 75-80%, and can last longer, 1.5 times.
Unlike steel units, cast iron solid fuel units are more efficient.
The design of cast iron units uses heat exchangers made of a special grade of cast iron alloy, which has high heat transfer. Such boilers are most often used for open heating systems heating. The products are additionally equipped with grate bars, thanks to which intensive extraction of thermal energy is carried out directly from the burning fuel placed on the grate bar.
The efficiency of such heating devices is 80%. The long service life of cast iron boilers should be taken into account. The service life of such equipment is 30-40 years.
How to increase the efficiency of heating equipment operating on solid fuels
Today, many consumers, having at their disposal a solid fuel boiler, try to find the most convenient and practical way how to increase the efficiency of heating equipment. The technological parameters of heating devices laid down by the manufacturer lose their nominal values over time, therefore, to increase the efficiency of boiler equipment, efforts are being made to various ways and funds.
Let's consider one of the most effective options, installing an additional heat exchanger. The task of the new equipment is to remove thermal energy from volatile combustion products.
In the video you can see how to make your own economizer (heat exchanger)
To do this, we first need to know what the temperature of the smoke at the outlet is. You can change it using a multimeter, which is placed directly in the middle of the chimney. Data on how much additional heat can be obtained from evaporating combustion products is necessary to calculate the area of the additional heat exchanger. We do the following:
- we send a certain amount of firewood into the firebox;
- We measure how long it takes for a certain amount of firewood to burn.
For example: firewood, in the amount of 14.2 kg. burn for 3.5 hours. The smoke temperature at the boiler outlet is 460 0 C.
In 1 hour we burned: 14.2/3.5 = 4.05 kg. firewood
To calculate the amount of smoke, we use the generally accepted value of 1 kg. firewood = 5.7 kg. flue gases. Next, we multiply the amount of wood burned in one hour by the amount of smoke produced by burning 1 kg. firewood As a result: 4.05 x 5.7 = 23.08 kg. volatile combustion products. This figure will become the starting point for subsequent calculations of the amount of thermal energy that can be additionally used to heat the second heat exchanger.
Knowing the value of the heat capacity of volatile hot gases as 1.1 kJ/kg, we make further power calculations heat flow, if we want to reduce the smoke temperature from 460 0 C to 160 degrees.
Q = 23.08 x 1.1 (460-160) = 8124 kJ thermal energy.
As a result, we obtain the exact value of the additional power provided by volatile combustion products: q = 8124/3600 = 2.25 kW, a large figure that can have a significant impact on increasing the efficiency of heating equipment. Knowing how much energy is wasted, the desire to equip the boiler with an additional heat exchanger is completely justified. Due to the influx of additional thermal energy for heating the coolant, not only the efficiency of the entire heating system increases, but also the efficiency of the heating unit itself increases.
conclusions
Despite the abundance of models of modern heating equipment, solid fuel boilers continue to be one of the most effective and affordable types of heating equipment. Compared to electric boilers, which have an efficiency of up to 90%, solid fuel units have a high economic effect. The increase in efficiency on new models has allowed this type of boiler equipment to come closer to electric and gas boilers.
Modern solid fuel devices are capable of not only operating for a long time using affordable natural fuel resources, but also have high performance characteristics.
Boiler efficiency gross characterizes the efficiency of using the heat entering the boiler and does not take into account costs electrical energy to drive blower fans, smoke exhausters, feed pumps and other equipment. When running on gas
h br k = 100 × Q 1 / Q c n. (11.1)
Energy consumption for the boiler installation’s own needs is taken into account by the boiler efficiency net
h n k = h br k – q t – q e, (11.2)
Where q t, q e– relative costs for own needs of heat and electricity, respectively. Heat consumption for own needs includes heat loss with blowing, for blowing screens, spraying fuel oil, etc.
The main ones are heat losses due to blowing
q t = G pr × (h c.v – h p.v) / (B × Q c n) .
Relative electricity consumption for own needs
q el = 100 × (N p.n /h p.n + N d.v /h d.v + N d.s /h d.s)/(B × Q c n) ,
where N p.n, N d.v, N d.s – electrical energy consumption for driving feed pumps, blower fans and smoke exhausters, respectively; h p.n, h d.v, h d.s - efficiency of feed pumps, blower fans and smoke exhausters, respectively.
11.3. Methodology for performing laboratory work
and processing of results
Balance tests in laboratory work are carried out for the stationary operating mode of the boiler when performing the following mandatory conditions:
The duration of operation of the boiler installation from lighting to the start of testing is at least 36 hours,
The duration of withstanding the test load immediately before the test is 3 hours,
Permissible load fluctuations during the break between two adjacent experiments should not exceed ±10%.
Parameter values are measured using standard instruments installed on the boiler panel. All measurements must be carried out simultaneously at least 3 times with an interval of 15-20 minutes. If the results of two experiments of the same name differ by no more than ±5%, then their arithmetic mean is taken as the measurement result. If the relative discrepancy is greater, the measurement result in the third, control experiment is used.
The results of measurements and calculations are recorded in a protocol, the form of which is given in table. 26.
Table 26
Determination of heat loss from a boiler
Parameter name | Designation | Unit | measured | |||
№1 | №2 | №3 | Experimental results | |||
Average | Flue gas volume | V g | ||||
m 3 /m 3 | Average volumetric heat capacity of flue gases | C g¢ | ||||
kJ/ (m 3 K) | Flue gas temperature | J | ||||
°C | Heat loss with flue gases | Q 2 | ||||
MJ/m 3 | Volume of 3-atomic gases | V g | ||||
VRO 2 | Theoretical nitrogen volume | V g | ||||
V° N 2 | Excess oxygen in flue gases | --- | ||||
a y | Theoretical air volume | V g | ||||
V° in | Dry gas volume | V g | ||||
V сг | Volume of carbon monoxide in flue gases | % | ||||
CO | Heat of combustion CO | Q 2 | ||||
Q CO | Volume of hydrogen in flue gases | % | ||||
H 2 | Heat of combustion H 2 | Q 2 | ||||
QH 2 | Volume of methane in flue gases | % | ||||
CH 4 | Heat of combustion CH 4 | Q 2 | ||||
Q CH 4 | Heat loss from chemical incomplete combustion | Q 2 | ||||
Q 3 | % | |||||
q 5 | Heat loss from external cooling | Q 2 |
Q 5
End of table. 26
Table 27
Parameter name | Designation | Unit | measured | |||
№1 | №2 | №3 | Experimental results | |||
Boiler efficiency gross and net | Electrical consumption energy to drive feed pumps | |||||
N p.n. | Electrical consumption energy for driving blower fans | |||||
N d.in | Electrical consumption energy for driving smoke exhausters | |||||
N d.s | Efficiency of feed pumps | |||||
h Mon | Efficiency of blower fans | |||||
h door | Efficiency of smoke exhausters | |||||
h dm | Relative electric consumption energy for own needs | |||||
q el | Net boiler efficiency | % |
h net k
Analysis of laboratory results
The value of h br k obtained as a result of the work using the method of direct and reverse balances must be compared with the certified value of 92.1%.
Analyzing the effect on the boiler efficiency of the amount of heat loss with flue gases Q 2, it should be noted that an increase in efficiency can be achieved by reducing the temperature of the flue gases and reducing the excess air in the boiler. At the same time, a decrease in gas temperature to the dew point temperature will lead to condensation of water vapor and low-temperature corrosion of heating surfaces. A decrease in the excess air coefficient in the furnace can lead to underburning of fuel and an increase in Q 3 losses. Therefore, the temperature and excess air must not be lower than certain values.
Then it is necessary to analyze the effect on the efficiency of the boiler's operation of its load, with an increase in which losses with flue gases increase and losses Q 3 and Q 5 decrease.
The laboratory report should make a conclusion about the level of efficiency of the boiler.
- Control questions
- Based on what indicators of boiler operation can a conclusion be made about the efficiency of its operation?
- What is the heat balance of a boiler? By what methods can it be compiled?
- What heat losses increase during boiler operation?
- How can you increase q 2?
- What parameters have a significant impact on the boiler efficiency?
Keywords: boiler heat balance, boiler gross and net efficiency, corrosion of heating surfaces, excess air coefficient, boiler load, heat loss, exhaust gases, chemical incomplete combustion of fuel, boiler operating efficiency.
CONCLUSION
In the process of performing a laboratory workshop on the course of boiler plants and steam generators, students become familiar with methods for determining the calorific value of liquid fuel, humidity, volatile yield and ash content of solid fuel, the design of the DE-10-14GM steam boiler and experimentally investigate the thermal processes occurring in it.
Future specialists study methods for testing boiler equipment and gain the necessary practical skills needed in determining the thermal characteristics of the furnace, drawing up the heat balance of the boiler, measuring its efficiency, as well as drawing up the salt balance of the boiler and determining the amount of optimal blowdown.
Bibliography
1. Khlebnikov V.A. Boiler plant equipment testing:
Laboratory workshop. - Yoshkar-Ola: MarSTU, 2005.
2. Sidelkovsky L.N., Yurenev V.N. Boiler installations of industrial enterprises: Textbook for universities. – M.: Energoatomizdat, 1988.
3. Trembovlya V.I., Finger E.D., Avdeeva A.A. Thermal testing of boiler installations. - M.: Energoatomizdat, 1991.
4. Aleksandrov A.A., Grigoriev B.A. Tables of thermophysical properties of water and water vapor: Handbook. Rec. State standard reference data service. GSSSD R-776-98. – M.: Publishing house MPEI, 1999.
5. Lipov Yu.M., Tretyakov Yu.M. Boiler installations and steam generators. – Moscow-Izhevsk: Research Center “Regular and Chaotic Dynamics”, 2005.
6. Lipov Yu.M., Samoilov Yu.F., Tretyakov Yu.M., Smirnov O.K. Testing of equipment in the boiler department of the MPEI CHPP. Laboratory workshop: Tutorial on the course “Boiler installations and steam generators”. – M.: Publishing house MPEI, 2000.
7. Roddatis K.F., Poltaretsky A.N. Handbook of low-capacity boiler installations/Ed. K.F. Roddatis. – M.: Energoatomizdat, 1989.
8. Yankelevich V.I. Adjustment of gas-oil industrial boiler houses. – M.: Energoatomizdat, 1988.
9. Laboratory work in the courses “Heat-generating processes and installations”, “Boiler installations of industrial enterprises” / Comp. L.M. Lyubimova, L.N. Sidelkovsky, D.L. Slavin, B.A. Sokolov and others / Ed. L.N. Sidelkovsky. – M.: Publishing house MPEI, 1998.
10. Thermal calculation of boiler units (Normative method)/Ed. N.V. Kuznetsova. – M.: Energia, 1973.
11. SNiP 2.04.14-88. Boiler installations/Gosstroy of Russia. – M.: CITP Gosstroy of Russia, 1988.
Educational edition
KHLEBNIKOV Valery Alekseevich
BOILER UNITS
AND STEAM GENERATORS
Laboratory workshop
Editor A.S. Emelyanova
Computer set V.V.Khlebnikov
Computer layout V.V.Khlebnikov
Signed for publication on 02/16/08. Format 60x84/16.
Offset paper. Offset printing.
Conditional p.l. 4.4. Uch.ed.l. 3.5. Circulation 80 copies.
Order No. 3793. S – 32
Mari State Technical University
424000 Yoshkar-Ola, pl. Lenina, 3
Editorial and Publishing Center
Mari State technical university
424006 Yoshkar-Ola, st. Panfilova, 17
In 2020, it is planned to produce 1720-1820 million Gcal.
A milligram equivalent is the amount of a substance in milligrams that is numerically equal to the ratio of its molecular weight to the valency in a given compound.
The heat released during fuel combustion cannot be fully used to produce steam or hot water; some of the heat is inevitably lost, dissipating in the environment. The heat balance of a boiler unit is a specific formulation of the law of conservation of energy, which asserts the equality of the amount of heat introduced into the boiler unit and the heat expended on the production of steam or hot water, taking into account losses. In accordance with the “Standard Method”, all values included in the heat balance are calculated per 1 kg of burned fuel. The incoming part of the heat balance is called available heat :
Where Q- - lower heating value of fuel, kJ/kg; c T t T - physical heat of fuel (with t - heat capacity of fuel, / t - fuel temperature), kJ/kg; Q B - heat of air entering the furnace when heated outside the unit, kJ/kg; Q n - heat introduced into the boiler unit with steam used for atomizing fuel oil, external blowing of heating surfaces or supply under the grate during layer combustion, kJ/kg.
When using gaseous fuel, the calculation is performed relative to 1 m 3 of dry gas under normal conditions.
Physical heat of the fuel plays a significant role only when preheating the fuel outside the boiler unit. For example, fuel oil is heated before being supplied to the burners, since it has a high viscosity at low temperatures.
Air heat, kJ/ (kg fuel):
where a t is the coefficient of excess air in the furnace; V 0 H - in theory required amount air, n.m 3 /kg; from to - isobaric heat capacity of air, kJ/(n.m 3 K); / x in - cold air temperature, °C; t B - air temperature at the entrance to the furnace, °C.
Heat introduced with steam, kJDkgfuel):
Where G n - specific consumption blown steam (approximately 0.3 kg of steam per 1 kg of fuel oil is consumed to atomize fuel oil); / n = 2750 kJ/kg - the approximate value of the enthalpy of water vapor at the temperature of the combustion products leaving the boiler unit (about 130 °C).
In approximate calculations, 0 r is taken ~Q? due to the smallness of the other components of equation (22.2).
The consumption part of the heat balance consists of useful heat (production of steam or hot water) and the amount of losses, kJDkgfuel):
where 0 2 - heat loss with gases leaving the boiler unit;
- 03 - heat loss from chemical incomplete combustion of fuel;
- 0 4 - heat loss from mechanical incomplete combustion of fuel;
- 0 5 - heat loss through the lining in environment; 0 6 - losses with physical heat of the slag removed from the boiler unit.
The heat balance equation is written as
As a percentage of available heat, equation (22.6) can be written:
The usefully used heat in a steam boiler with continuous blowing of the upper drum is determined by the equation, kJDkgfuel):
Where D- boiler steam output, kg/s; Dnp- flow rate of purge water kg/s; IN - fuel consumption, kg/s; / p, / p w, / k w - enthalpy of steam, feed and boiler water at pressure in the boiler, respectively, kJ/kg.
Heat loss with flue gases, kJ/(kg fuel):
Where s g And from to- isobaric heat capacity of combustion products and air, kJ/(n.m 3 K); g - flue gas temperature, °C; ax is the coefficient of excess air at the gas outlet from the boiler unit; K 0 G and V 0- theoretical volume of combustion products and theoretically required amount of air, n.m 3 / (kgfuel).
A vacuum is maintained in the gas ducts of the boiler unit; the volumes of gases as they move along the gas path of the boiler increase due to air suction through leaks in the boiler lining. Therefore, the actual coefficient of excess air at the outlet of the boiler unit ax is greater than the coefficient of excess air in the furnace a. It is determined by summing the coefficient of excess air in the firebox and air suction in all flues. In the practice of operating boiler plants, it is necessary to strive to reduce air suction in gas ducts as one of the most effective means combating heat loss.
Thus, the amount of loss Q 2 determined by the temperature of the exhaust gases and the value of the excess air coefficient ax. IN modern boilers the temperature of the gases behind the boiler does not fall below 110 °C. A further decrease in temperature leads to condensation of water vapor contained in gases and the formation of sulfuric acid during combustion of sulfur-containing fuel, which accelerates corrosion metal surfaces gas path. The minimum losses with flue gases are q 2 ~ 6-7%.
Losses from chemical and mechanical incomplete combustion are characteristics of combustion devices (see clause 21.1). Their value depends on the type of fuel and combustion method, as well as on the perfection of the organization of the combustion process. Losses from chemical incomplete combustion in modern furnaces amount to q 3 = 0.5-5%, from mechanical - q 4 = 0-13,5%.
Heat loss to the environment q 5 depend on the boiler power. The higher the power, the lower the relative amount of loss q 5 . So, with the steam output of the boiler unit D= 1 kg/s losses are 2.8%, with D= 10 kg/s q 5 ~ 1%.
Heat loss with physical heat of slag q b are small and are usually taken into account when drawing up an accurate heat balance, %:
Where a shl = 1 - a un; a un - share of ash in flue gases; with went and? shl - heat capacity and temperature of the slag; A g - ash content of the operating state of the fuel.
Efficiency factor (Efficiency) of the boiler unit is the ratio of the useful heat of combustion of 1 kg of fuel to produce steam in steam boilers or hot water in hot water boilers to the available heat.
Boiler efficiency, %:
The efficiency of boiler units depends significantly on the type of fuel, combustion method, flue gas temperature and power. Steam boilers operating on liquid or gaseous fuel have an efficiency of 90-92%. When burning solid fuel in layers, the efficiency is 70-85%. It should be noted that the efficiency of boiler units significantly depends on the quality of operation, especially on the organization of the combustion process. Operating a boiler unit with steam pressure and output less than nominal reduces efficiency. During the operation of boilers, thermal technical tests must be periodically carried out in order to determine losses and the actual efficiency of the boiler, which allows making the necessary adjustments to its operating mode.
Fuel consumption for a steam boiler (kg/s - for solid and liquid fuel; n.m 3 /s - gaseous)
Where D- steam output of the boiler unit, kg/s; / p, / p w, / k w - enthalpy of steam, feed and boiler water, respectively, kJ/kg; Q p - available heat, kJ/(kg fuel) - for solid and liquid fuels, kJ/(N.m 3) - for gaseous fuel (often taken in calculations Q p ~ Q- due to their slight differences); P - value continuous blowing, % of steam production; g| ka - efficiency of the cola unit, fraction.
Fuel consumption for hot water boiler (kg/s; n.m 3 /s):
where C in - water consumption, kg/s; /, / 2 - initial and final enthalpies of water in the boiler, kJ/kg.
The efficiency factor of a heating boiler is the ratio of the useful heat consumed to produce steam (or hot water) to the available heat of the heating boiler. Not all the useful heat generated by the boiler unit is sent to consumers; part of the heat is spent on its own needs. Taking this into account, the efficiency of a heating boiler is distinguished by the generated heat (gross efficiency) and by the released heat (net efficiency).
The difference between the generated and released heat is used to determine the consumption for auxiliary needs. Not only heat is consumed for its own needs, but also electrical energy (for example, to drive a smoke exhauster, fan, feed pumps, fuel supply mechanisms), i.e. consumption for own needs includes the consumption of all types of energy spent on the production of steam or hot water.
As a result, the gross efficiency of a heating boiler characterizes the degree of its technical perfection, and the net efficiency characterizes its commercial profitability. For a boiler unit, gross efficiency, %:
according to the direct balance equation:
η br = 100 Q floor / Q r r
where Q floor is the amount of useful heat, MJ/kg; Q р р — available heat, MJ/kg;
according to the reverse balance equation:
η br = 100 - (q u.g + q h.n + q n.o)
where q u.g, q h.n, q n.o - relative heat losses with exhaust gases, from chemical incomplete combustion of fuel, from external cooling.
Then the net efficiency of the heating boiler according to the reverse balance equation:
η net = η br - q s.n
where q s.n is energy consumption for own needs, %.
Determination of efficiency according to the direct balance equation, they are carried out mainly when reporting for a separate period (decade, month), and according to the reverse balance equation - when testing a heating boiler. Calculating the efficiency of a heating boiler using reverse balance is much more accurate, since the errors in measuring heat losses are smaller than in determining fuel consumption.
Dependence of boiler efficiency η k on its load (D/D nom) 100
q u.g, q h.n, q n.o - heat losses with exhaust gases, from chemical and mechanical incomplete combustion, from external cooling and total losses.
Thus, to improve the efficiency of a heating boiler, it is not enough to strive to reduce heat losses; It is also necessary to completely reduce the consumption of thermal and electrical energy for own needs, which amount on average to 3...5% of the heat available in the boiler unit.
The change in efficiency of a heating boiler depends on its load. To construct this dependence (Fig.), you need to subtract from 100% sequentially all losses of the boiler unit, which depend on the load, i.e. q u.g, q x.n, q n.o. As can be seen from the figure, the efficiency of a heating boiler at a certain load has a maximum value. Operating the boiler at this load is most economical.