Tour tor s40 10 connection to electricity. Circulation pumps
Type
Circulation pump with glandless rotor, with threaded or flange connection
Application
water heating systems, industrial circulation plants, air conditioning systems and closed cooling circuits
Designation
Product Features/Benefits
- Used in heating systems and cooling/air conditioning systems from -20 °C to +130 °C (TOP-S 25/13, TOP-S 80/15 and TOP-S 80/20 from -20 °C to +110 °C )
- Pump housing with cataphoresis coating (KTL) to protect against corrosion due to condensation.
- Manual power adjustment with
3 speed levels - The pump is easy to install thanks to the PN 6/PN 10 combination flange (for DN 40 - DN 65)
Specifications
- Permissible temperature range from -20 °C to +130 °C,
short-term (2 hours) up to +140 °C (TOP-S 25/13, 80/15, 80/20 and pumps with Wilo safety module: -20 °C to +110 °C) - Network connection:
- 1~230 V, 50 Hz (depending on type)
- 3~230 V, 50 Hz (optional with switching plug)
- 3~400 V, 50 Hz
- IP protection class X4D
- Threaded or flanged connection (depending on type) Rp 1 to DN 100
- Max. operating pressure standard version: 6/10 bar or 6 bar (special version: 10 bar or 16 bar)
Equipment/functions
Operating modes
- Switching speed stages
Manual control
- Adjustment of speed steps: 3 speed steps (2 speed steps for single-phase pumps with P 2 ? 350 W)
Automatic control
- Complete motor protection with integrated electronic system shutdown (standard equipment only for three-phase pumps with P 2 ? 180 W and single-phase pumps P 2 ? 350 W, as an option for all types with Wilo?C protective module)
External control
- Control input "Off" by priority" (optional for all types with Wilo?C safety module)
Alarm and indication
- Separate/combined fault signaling (volt-free normally open contact) (optional for all types with Wilo?C safety module)
- Integrated fault signaling (volt-free break contact) (standard equipment only for 3 pumps with P 2 ≤ 180 W and 1 pump with P 2 ≤ 350 W, optional for all types with Wilo-C safety module)
- Separate operating signaling (potential-free normally open contact) (optional for all types with Wilo?C safety module)
- Protective winding contact (ZKO, potential-free break contact) only for single-phase pumps with P 2 = 180 W)
- Light indication of fault (standard equipment only for three-phase pumps with P 2 ? 180 W and for single-phase pumps with P 2 ? 350 W, optional for all types with Wilo-C safety module)
- Direction of rotation indicator lamp (only for three-phase pumps)
Twin pump control (double pump or two single pumps)
- Main/standby operating mode (automatic pump switching based on fault signal/timer): optional for all pump types with Wilo-C safety module
Equipment
- For pumps with flange connection: Flange versions
- Standard version for pumps DN 40 - DN 65: combination flange PN 6/10 (flange PN 16 according to EN 1092-2) for counter flanges PN 6 and PN 16,
- Standard version for pumps DN 80/DN 100: PN 6 flange (calculated PN 16 according to EN 1092-2) for PN 6 counterflange,
- Special version for pumps DN 40 - DN 100: PN 16 flange (according to EN 1092-2) for PN 16 counterflange,
- Cable connection is possible on both sides (only for single-phase and three-phase pumps with P 2 ? 180 W)
- Serial equipment of pumps used in heating systems with thermal insulation.
Materials
- Pump body: Gray cast iron
- Working wheel: Synthetic material
- Shaft: Stainless steel
- Bearings: metalgraphite
Scope of delivery
- Pump
- Thermal insulation
- With seals for threaded connection
- Washers for flange screws (for nominal connection diameters DN 40 × DN 65)
- Installation and operating instructions
Options
- Special version for operating pressure PN 16 (at extra cost)
- Version for special voltages on request.
Accessories
- Threaded connections for threaded connection
- Compensators
- For 3~400 V pumps:
- Switching plug 3~230 V, 50 Hz (not TOP-S 80/15, TOP-S 80/20)
- Wilo C protection module, 3~400 V
- For 1~230 V pumps:
- Wilo shut-off device SK 602N/SK 622N for complete motor protection
- Wilo C protection module, 1~230 V
Glandless circulation pump with threaded or flanged connection
Application:
water heating systems, industrial circulation plants, air conditioning systems and closed cooling circuits
Product Features/Benefits:
Used in heating and cooling/air conditioning systems from -20 °C to +130 °C
(TOP-S 80/15 and TOP-S 80/20 from -20 °C to +110 °C)
- Pump housing with cataphoresis coating (KTL) to protect against corrosion due to condensation formation
- Manual power adjustment with 3 speed levels
- Easy installation thanks to the PN 6/PN 10 combination flange (for DN 40 - DN 65)
Specifications:
Permissible temperature range from -20 °C to +130 °C,
short-term (2 hours) up to +140 °C (TOP-S 25/13, 80/15, 80/20 and pumps with Wilo safety module: -20 °C to +110 °C)
- Network connection:
- 1~230 V, 50 Hz (depending on type)
- 3~230 V, 50 Hz (optional with switching plug)
- 3~400 V, 50 Hz
- IP protection class X4D
- Threaded or flanged connection (depending on type) Rp 1 to DN 100
- Max. operating pressure standard version: 6/10 bar or 6 bar (special version: 10 bar or 16 bar)
Equipment/functions
Operating modes:
Switching speed stages
Manual control:
Setting of speed steps: 3 speed steps (2 speed steps for single-phase pumps with P2 ? 350 W)
Automatic control:
Complete motor protection with integrated electronic shutdown system (standard equipment only for three-phase pumps with P2 ? 180 W and single-phase pumps P2 ? 350 W, optional for all types with Wilo?C protection module)
External control:
Control input "Off" by priority" (optional for all types with Wilo?C safety module)
Alarm and indication:
Separate/combined fault signaling (volt-free normally open contact) (optional for all types with Wilo?C safety module)
- Integrated fault signaling (volt-free normally open contact) (standard equipment only for 3 pumps with P2 ≥ 180 W and 1 pump with P2 ≥ 350 W, optional for all types with Wilo-C safety module)
- Separate operating signaling (potential-free normally open contact) (optional for all types with Wilo?C safety module)
- Protective winding contact (ZKO, potential-free break contact) only for single-phase pumps with P2 = 180 W)
- Light indication of fault (standard equipment only for three-phase pumps with P2 ? 180 W and for single-phase pumps with P2 ? 350 W, as an option for all types with Wilo-C safety module)
- Indicator lamp for direction of rotation (only for three-phase pumps)
Twin pump control (double pump or two single pumps):
Main/standby operating mode (automatic pump switching based on fault signal/timer): optional for all pump types with Wilo-C safety module
Equipment:
For pumps with flange connection: Flange versions
- Standard version for pumps DN 40 - DN 65: combination flange PN 6/10 (flange PN 16 according to EN 1092-2) for counter flanges PN 6 and PN 16,
- Standard version for pumps DN 80/DN 100: PN 6 flange (calculated PN 16 according to EN 1092-2) for PN 6 counterflange,
- Special version for pumps DN 40 - DN 100: PN 16 flange (according to EN 1092-2) for PN 16 counterflange,
- Cable connection is possible on both sides (only for single-phase and three-phase pumps with P2?180 W)
- Serial equipment of pumps used in heating systems with thermal insulation.
Materials:
Pump body: Gray cast iron
- Impeller: Synthetic material
- Shaft: Stainless steel
- Bearings: metalgraphite
Scope of delivery:
Pump
- Thermal insulation
- With seals for threaded connections
- Washers for flange screws (for nominal connection diameters DN 40 × DN 65)
- Installation and operating instructions
Options:
Special version for operating pressure PN 16 (at extra cost)
- Version for special voltages on request.
Accessories:
Threaded connections for threaded connection
- Compensators
- For pumps 3~400 V:
- Switching plug 3~230 V, 50 Hz (not TOP-S 80/15, TOP-S 80/20)
- Wilo C protection module, 3~400 V
- For pumps 1~230 V:
- Wilo SK 602N/SK 622N shut-off device for complete motor protection
- Wilo C protection module, 1~230 V
Circulating WILO pump TOP-S 40/10 DM PN6/10 is used for circulating water or a water-glycol mixture in heating or air conditioning systems. Also used in underfloor heating systems. It is a reliable and proven pumping equipment. Installed directly on the pipeline, designed for long-term uninterrupted operation.
Designation
- TOP-S - standard pump
- 40 - nominal inner diameter
- 10 - nominal pressure (feed height), m
- DM - three-phase pump, 3~230/400 V, 50 Hz
Features of the circulation pump WILO TOP-S 40/10 DM PN6/10
- The “wet” rotor ensures virtually silent operation.
- Three operating modes corresponding to different degrees of power. You can choose the optimal frequency, thereby optimizing energy costs.
- Cataphoretic coating for protection against corrosion and condensation.
- Supplied with thermal insulation.
- Wide range of temperatures of the pumped liquid - from -20 to +130 C.
Specifications
Head, m | 10 |
Consumption, m3/hour | 21 |
Rated power, W | 350 |
Power, W | 365 / 465 / 585 |
Current, A 230 / 400 | 0,65 / 0,82 / 1,17 / 1,12 / 1,43 / 2,02 |
Electrical connection | 3~230/400 V, 50 Hz |
Electrical protection class | IP44 |
System pressure (max.), bar | 10 |
Pressure in front of the pump at t | |
+ 50 °C | 0.05 m. |
+ 95 °C | 5 m. |
+ 110 °C | 11 m. |
+ 130 °C | 24 m |
Pump installation | horizontal / vertical |
Pumped medium | clean |
Temperature of the pumped liquid | from -20 to + 110 °C |
Short term | from -20 to + 140 °C |
Pipeline connection | flanged |
Inner diameter flange, mm | 40 |
Temperature environment | up to 40°С |
Mounting length, mm | 250 |
Weight, kg | 12.5 |
Equipment and functions
Flow and pressure characteristics
Design and operational features
- “Wet rotor” - the rotor is located directly in the pumped liquid, which lubricates the pump bearings.
- Materials used
- body - Gray cast iron
- shaft - Stainless steel (X46Cr13)
- Working wheel- Synthetic material (PPE)
- bearings - Metalgraphite - Has built-in overheat protection
- After emergency shutdown the pump automatically turns on after cooling
- It is possible to pump water and a water-glycol mixture (max. 1:1; with a glycol content of more than 20%, the performance characteristics must be checked).
Contents of delivery
- Pump
- Thermal insulation
- With seals for threaded connections
- Washers for flange screws (for nominal connection diameters DN 40/DN 65)
- Installation and operating instructions
Accessories (not included in the basic package)
Threaded connections for threaded connection
- Compensators
- For pumps 3~400 V:
- Switching plug 3~230 V, 50 Hz (not TOP-S 80/15, TOP-S 80/20)
- Wilo C protection module, 3~400 V
- For pumps 1~230 V:
- Wilo SK 602N/SK 622N shut-off device for complete motor protection
- Wilo C protection module, 1~230 V
This circulation pump is used as part of medium and large heating and air conditioning systems. It is reliable and proven equipment.
How to buy a circulation pump WILO TOP-S 40/10 DM PN6/10
You can buy the WILO TOP-S 40/10 DM PN6/10 pump by making a purchase directly on the online store website, or by calling the phone in the Contacts section. Our manager will contact you and arrange delivery or reserve the goods for pickup.
If you need drainage pump in Moscow or the Moscow region, delivery within the city and the nearest Moscow region is at your service. For buyers from other regions of Russia - delivery by any transport company or postal service as agreed.
Payment for goods is carried out in the following ways:
1.Payment in cash.
When picking up from the store, or when receiving the goods to the courier.
2.Bank transfer - payment according to the invoice issued for payment as for legal, and for physical persons
When placing an order, select the payment method: "Bank transfer".
After confirming the order, our specialist will contact you and after agreeing on all organizational issues, you will be sent an invoice e-mail which you can pay at any bank or via an Internet client.
1.Pickup.
Pickup times and times:
PVZ m. Sokol: you can pick up your order the next day after ordering from 10 to 18 on weekdays. The order is stored at the point of issue for 3 working days.
Pickup cost:free when ordering over RUB 1,000. (for orders less than 1,000 rubles, the cost of pickup is 80 rubles.)
Attention! Only pre-reserved items are available at the order pick-up point!
The employee at the delivery point does not give any advice on goods!
Directions to the pick-up point are located on the page CONTACTS
2. Delivery in Moscow within the Moscow Ring Road
The following items are delivered free of charge:
Kerosene heaters trademark"Sengoku"
Cost of delivery:
If your order weighs more than 20 kg, the manager will calculate and inform you of the additional delivery cost!
Delivery time:
Delivery is carried out on weekdays from 10:00 to 20:00.
Behind 30-90 minutes the courier calls you and agrees exact time arrival.
Exact delivery address (city, street, house number, apartment or office number, intercom code)
The contact person
Contact phone numbers
3. Delivery beyond the Moscow Ring Road and further within the Moscow region
Cost of delivery:
If the product card does not indicate WEIGHT, you can check it with the manager.
If your order weighs more than 20 kg, the manager will calculate and inform you of the additional delivery cost!
Delivery time:
Delivery is carried out within 1-3 working days from 10:00 to 20:00 without reference to half a day.
Behind 1-2 hours before delivery, the courier calls you and agrees on the exact time of arrival.
What is important to indicate when ordering:
Exact delivery address ( city, region, locality, street, house number, apartment or office number, intercom code)
The contact person
Contact phone numbers
4. Delivery to regions of the Russian Federation
We can send you goods from any of the companies listed below.
SDEK - www.cdek.ru
First Expedition Company (PEC) - www.pecom.ru
The estimated cost of delivery of goods can be found on the websites of these companies or contact our specialist.
What is important to indicate when ordering:
Passport series and number, date of issue
Full Name
Receipt city
If none of the above methods suits you, we will send the goods to your address in another way - as agreed with you.
The coolant in the heating system must constantly circulate. Its movement is ensured by circulation pump, which is indispensable in heating systems with forced circulation. But in addition to the movement of coolant in the system, the circulation pump can perform an energy-saving function, which is especially important in old systems made of large-diameter pipes.
How does this happen? If you buy a circulation pump and install it in the heating system, the coolant will move faster and return to the boiler without having time to give up all its heat. Accordingly, significantly less energy will be required for reheating, which can ultimately result in savings of 20-30%.
Circulation pump prices and types
There are two types of circulation pumps: wet and dry rotor. In wet pumps, the rotor is separated from the electric motor. O-rings, and the function of lubricating and cooling the engine is performed by the coolant. Its advantages are:
- noiselessness;
- compactness;
- efficiency,
- as well as long-term uninterrupted operation and ease of repair and operation. The disadvantages of “wet” type pumps include low efficiency, which limits their use in domestic heating systems.
In “dry” type pumps, the rotor does not come into contact with the coolant. They are much more powerful than “wet” ones (if the efficiency of “wet” ones is about 50%, then the efficiency of “dry” ones is 80%), which determines their use in industry. “Dry” pumps create noise and are demanding on the cleanliness of the coolant.
When choosing a circulation pump, price plays an important, but still secondary role. In the first place are the features of the heating system of a particular building and the pressure characteristics of the pump itself, which should provide required amount heat to maintain the required microclimate. The calculation is usually made by heating engineers who take into account the average outside temperature, wall, roof and floor material, characteristics ventilation system and other characteristics. The result of the calculation is the indicator of the volumetric coolant supply to heating system.
An important factor when choosing a pump is also its flow rate, or the dependence of the power of the heat source on the difference in water temperatures in the supply and return pipelines. Regarding manufacturers pumping equipment, then pumps from European manufacturers GRUNDPOS and Wilo have excellent characteristics, as well good quality Korean KITURAMI are famous. Among Russian companies the undoubted leaders are Gilex and Espa, which provide comparative quality at a lower price.